Default Boiler Air Lock Diagnosis Help

I have to tell everyone that this is actually for my own boiler and not for a client.

I am having a problem with the boiler in my apartment that keeps air locking. The problem has been ongoing for about 4 years now and is getting worse. Recently 4 spirovents were installed on the baseboards, a expansion tank was installed, and a pressure regulator valve was installed. The system holds pressure and there isn't any signs of water damage in the building that would indicate leaks in the system. Circulator pump is working normally too.

We figure that the make-up water probably has a lot of air in it, but the spirovents should be taking care of this at the baseboards and at the air scoop a the top of the boiler. Anyone have any other ideas why the system would keep air locking? If you need more specifics, I can provide you with what I know about it.

The boiler is somewhere between 13 and 20 years old. The water that is drained to clear the air locks is always very dark rusty water. There is also stains around the vents in the spirovents that were just recently installed about a month ago from the rusty water or air bleeding out.

Thanks
Reply With Quote
  #2  
Old 11/2/08, 10:35 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boiler Air Lock Diagnosis Help

You have a leak that you have not found yet. Simple as that.

If you have a fast-fill on the pressure regulator, flip it up to jack up the pressure to something approaching twice normal operating pressure (with boiler not firing), but below the 35 that the TPR will blow off at and find your leaks.
Reply With Quote
  #3  
Old 11/2/08, 10:51 PM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is online now
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,321
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Boiler Air Lock Diagnosis Help

That's what I keep telling the landlord Marc. Problem is that I am on the third floor and the plumbing lines are behind closed walls that come from the basement. The two tenants below me have not reported any leaks or water stains and the maintnenance staff can't seem to find anying.
Reply With Quote
  #4  
Old 11/2/08, 11:59 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Boiler Air Lock Diagnosis Help

Tell me more, where is the boiler located what kind of seal is on the circulating pump is the make up water automatic or manual is there a sight glass on the boiler indicating water level. Where is the highest section of lines for this system and does it have a bleeder installed at that point or are they just at the baseboard heater. Does the circulating pump have gauges on the return and discharge sides of the pump and what are the pressures especially on the return side.

I Don't think air would be introduced within the make up water itself.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #5  
Old 11/3/08, 12:09 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boiler Air Lock Diagnosis Help

There normally wouldn't be a sight glass on a hot water system. They're best reserved for steam.
Reply With Quote
  #6  
Old 11/3/08, 12:30 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Boiler Air Lock Diagnosis Help

Quote:
Originally Posted by Marc D. Shunk View Post
There normally wouldn't be a sight glass on a hot water system. They're best reserved for steam.
They are good anywhere they are installed Keeps the blind from leading the blind they would normally be installed at the expansion tank



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #7  
Old 11/3/08, 12:40 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boiler Air Lock Diagnosis Help

Quote:
Originally Posted by cbottger View Post
They are good anywhere they are installed Keeps the blind from leading the blind they would normally be installed at the expansion tank
Uh-huh.

One tends to suspect a dried out circulator suction side flange gasket when air is a persistent problem.
Reply With Quote
  #8  
Old 11/3/08, 1:12 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Boiler Air Lock Diagnosis Help

Quote:
Originally Posted by Marc D. Shunk View Post
Uh-huh.

One tends to suspect a dried out circulator suction side flange gasket when air is a persistent problem.
Uh-Huh or even the pump shaft seal a possibility



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #9  
Old 11/3/08, 7:10 AM
Gary Oleski Gary Oleski is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Bridgeport, CT
Posts: 503
Default Re: Boiler Air Lock Diagnosis Help

Quote:
Originally Posted by Marc D. Shunk View Post
Uh-huh.

One tends to suspect a dried out circulator suction side flange gasket when air is a persistent problem.
I agree with Marc.



Gary Oleski Home Inspections
Home Inspections Connecticut
Connecticut . 06610
NACHI04012833
CT#HOI.341
C M I
Reply With Quote
  #10  
Old 11/3/08, 5:39 PM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is online now
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,321
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Boiler Air Lock Diagnosis Help

OK...We think we finally found the problem with the system I was talking about. Sometimes it is the strangest things that can contribute to a major problem. He is what we found today...

First off...the aquastat on the boiler was turned up to 230 degrees by one of the maintenance guys that apparently never turned it back down. The system was boiling the water and the disolved gases in the water were coming out of solution creating air blockages.

Secondly...the air bleed valves were closed all the way and the air could not escape when it built up.

Thirdly...the pressure regulator for the system was not set properly and did not allow the system to fill back up to a pressure that would drive it to the third floor.

And the big problem...when the maintenance staff would come out to bleed the system of air...he would practically flush the entire system and add all new water. The new makeup water has a lot more disolved gases in it and after several heating cycles would start to come out of solution and create another air blockage.

Problem should be solved now that the maintenance staff has been educated on how to bleed the air from a system.

Once the maintenance guys finally explained what they were doing, it made perfect sense to all of the experts involved in trying to diagnose this 4 year problem. Amazing!!!
Reply With Quote
  #11  
Old 11/3/08, 8:30 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boiler Air Lock Diagnosis Help

And the big problem...when the maintenance staff would come out to bleed the system of air...he would practically flush the entire system and add all new water. The new makeup water has a lot more disolved gases in it and after several heating cycles would start to come out of solution and create another air blockage.

not to mention the extra corrosion being created by the new water (O2)....

Anatol
Reply With Quote
  #12  
Old 11/4/08, 11:03 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boiler Air Lock Diagnosis Help

Quote:
Originally Posted by sgilligan1 View Post
Problem should be solved now that the maintenance staff has been educated on how to bleed the air from a system.

Once the maintenance guys finally explained what they were doing, it made perfect sense to all of the experts involved in trying to diagnose this 4 year problem. Amazing!!!
When I was running an IAQ/TAB company, I was very surprised at the lack of training for maintenance staff on HVAC systems.

One of the worst is when we were contracted to do a TAB contract on 3 smaller military buildings. About 1/2 way through our projected timeline, we halted work and got permission to write an interim report outlining problems that would not allow us to balance these system: about 1/2 the equipment couldn't be properly balanced due to:
-Seized dampers/disconnected control arms
-disconnected pneumatic tubing/no pressures
-of course, dirty and displaced filters
-extremely poor duct design with some of the first take-offs being within 2-3 feet of the air handler fan discharge
- in one case the fan motor was turning but the fan blower wheel was stuck

If that was representative of how the military generally ran, I'm glad that we weren't at war then. Hopefully things have improved because we have Canadian forces in Afghanistan now. We wouldn't want them to be dying because of "equipment problems"!
Reply With Quote
  #13  
Old 11/4/08, 9:08 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 212
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boiler Air Lock Diagnosis Help

Have you seen that you have a fix. Question. Is the circulator pumping towards the boiler or away from the boiler? Pumping away is the preferred method. Piping the expansion tank and the water feed between the circulator and the boiler will keep the same pressure throughout the system the same. Pumping towards the boiler will result in a pressure drop bewteen the circulator and the radiators or baseboard. Dropping the pressure will allow air bubbles to exapand in the water.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Boiler Shutdown dkoniuk HVAC 2 8/6/07 10:34 AM
Boiler Control Recall ldapkus HVAC 0 1/25/07 5:50 PM
Boiler Recall bwiley HVAC 5 12/20/06 7:20 AM
Peerless gas boiler 53bako Plumbing 6 11/29/06 7:50 AM
Romex on a Boiler? mgifford Electrical 7 1/10/06 5:27 PM


All times are GMT -4. The time now is 11:48 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts