Default Boiler Explosion

The title is a little misleading. The boiler didn't explode, but there was a gas explosion while trying to light it. I got called out at 3:00 a.m. night before last in the small town where I live. A gentleman who had a bad cold or the flu, got cold and turned his boiler up to warm the house. He didn't hear the boiler fire up, so he went to the basement and saw that the pilot light wasn't lit. He got a lighter, and as soon as he ignited the lighter, there was a tremendous explosion. The Fire Marshalls determined that the boiler (30 to 50 years old) was leaking water, and dripped and put the pilot light out. As there were no safety features on a boiler that old, the pilot light continued to pump propane in to the basement. As soon as he sparked the lighter, it blew. Look at the picture of the front of the house...it almost blew the entire front wall of the house off. Keep in mind, the boiler was in the basement on the other side of the house. His wife should get out of the hospital today, but he isn't doing so good...burns over 85% of his body...still in critical condition and they are giving him a 50/50 chance as of last night. Thought I would share the pics with you to emphasize the importance of safety with these older boilers and furnaces we sometimes see.
Attached Thumbnails
boiler-explosion-dsc01800.jpg   boiler-explosion-dsc01803.jpg   boiler-explosion-boiler.jpg  



Jeff Vogan
Vogan Home Inspections
Bevier, MO 63532
660-676-8835
www.reporthost.com/vogan
Reply With Quote
  #2  
Old 2/11/09, 12:06 PM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,024
Default Re: Boiler Explosion

Wow, poor guy.

You'd think that he would have smelled the propane upon entering the basement....
Reply With Quote
  #3  
Old 2/11/09, 12:10 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: Boiler Explosion

Thanks, Jeff.
Reply With Quote
  #4  
Old 2/11/09, 12:34 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Boiler Explosion

Quote:
Originally Posted by jvogan View Post
The title is a little misleading. The boiler didn't explode, but there was a gas explosion while trying to light it. I got called out at 3:00 a.m. night before last in the small town where I live. A gentleman who had a bad cold or the flu, got cold and turned his boiler up to warm the house. He didn't hear the boiler fire up, so he went to the basement and saw that the pilot light wasn't lit. He got a lighter, and as soon as he ignited the lighter, there was a tremendous explosion. The Fire Marshalls determined that the boiler (30 to 50 years old) was leaking water, and dripped and put the pilot light out. As there were no safety features on a boiler that old, the pilot light continued to pump propane in to the basement. As soon as he sparked the lighter, it blew. Look at the picture of the front of the house...it almost blew the entire front wall of the house off. Keep in mind, the boiler was in the basement on the other side of the house. His wife should get out of the hospital today, but he isn't doing so good...burns over 85% of his body...still in critical condition and they are giving him a 50/50 chance as of last night. Thought I would share the pics with you to emphasize the importance of safety with these older boilers and furnaces we sometimes see.
Considering all they were very lucky to be alive this Mobile home 4 miles from my home yesterday was not so lucky two fatalities burnt to the ground in less than 30 minutes had to pass right by it on my way to first inspection
Attached Thumbnails
boiler-explosion-zxv.jpg   boiler-explosion-zxv-1-.jpg.jpg
Views:	50
Size:	143.3 KB
ID:	26838  



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #5  
Old 2/11/09, 12:45 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: Boiler Explosion

Jeff i have worked on boilers older than that and still had safety features Are they sure it wasn't tampered with ?
Reply With Quote
  #6  
Old 2/11/09, 3:06 PM
Jeff S. Vogan's Avatar
Jeff S. Vogan Jeff S. Vogan is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Default Re: Boiler Explosion

David, the guy had a bad cold/flu, so we are guessing that is why he didn't smell the propane. Wayne, I don't know about that. After something like that, we call the State Fire Marshal and they send investigators. The investigator that works our area called in their "Pressure Vessel Specialist" to investigate it, and that was his best guess, that the leak put the pilot light out and pumped the basement full of propane. I have no idea about whether or not it was tampered with...



Jeff Vogan
Vogan Home Inspections
Bevier, MO 63532
660-676-8835
www.reporthost.com/vogan
Reply With Quote
  #7  
Old 2/11/09, 3:11 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Boiler Explosion

Those are terribly tragic stories.

Were you called out as a peace officer or an inspector?

Thanks for sharing Jeff,

Bill
Reply With Quote
  #8  
Old 2/11/09, 3:13 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Boiler Explosion

Quote:
Originally Posted by cbottger View Post
Considering all they were very lucky to be alive this Mobile home 4 miles from my home yesterday was not so lucky two fatalities burnt to the ground in less than 30 minutes had to pass right by it on my way to first inspection

That is a depressing sight. Is it common to see the ATF on a house/trailer fire?

Bill
Reply With Quote
  #9  
Old 2/11/09, 3:19 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,701
Default Re: Boiler Explosion

Charlie, I was going to give you a call this morning but I had to go out early. Glad to see that you're still out and about. Your storm has passed my way. I had to stop my car for fear of being rolled over! My neighbor's garage has come off the foundation and flipped over onto the roof. His car and tractor are sitting out in the middle of nowhere with all kinds of used lumber in the front yard!



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #10  
Old 2/11/09, 3:36 PM
Ian A. Niquette's Avatar
Ian A. Niquette Ian A. Niquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,193
Send a message via ICQ to iniquette
Default Re: Boiler Explosion

Charley and Jeff, thanks for sharing. This just brings out the point that we need to drive home to clients. They need to maintain this equipment on a regular basis. Some lives may have been saved if the maintenance was performed. Sad stories indeed.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network



What we've got here is......failure......to communicate.....
Reply With Quote
  #11  
Old 2/11/09, 4:49 PM
Russ L. Myers, CMI Russ L. Myers, CMI is offline
InterNACHI Member
 
Join Date: Dec 2007
Location: Chicago, IL
Posts: 67
Default Re: Boiler Explosion

This system appears to have several newer components, including some newer piping.
Also appears to have a thermocouple or thermopile system. ( safety controls).
I have serviced many boilers of this age (50 / 60) years old and all had some sort of safety controls.
If you can, let us know what the investigators find.



Board Certified Master Inspector
Chairman, InterNACHI Education Committee / Retired
Founder, Past President, NACHI Chicago
InterNACHI, State of Illinois Educational Administrator / Retired
President, InterNACHI, State of Illinois Chapter
Moderator, Inspectors Journal, Retired
Reply With Quote
  #12  
Old 2/11/09, 5:19 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,859
Default Re: Boiler Explosion

Quote:
Originally Posted by dvalley View Post
Wow, poor guy.

You'd think that he would have smelled the propane upon entering the basement....
Propane, being 1 1/2 times the density of air, is heavier than air and sinks to the floor. For this reason it sometimes is difficult to detect by smell.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #13  
Old 2/11/09, 5:26 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Boiler Explosion

Quote:
Originally Posted by wthacker View Post
That is a depressing sight. Is it common to see the ATF on a house/trailer fire?

Bill
BIA & ATF was on site Native American Reservation



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #14  
Old 2/11/09, 6:36 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Boiler Explosion

Ahhhh....

Thanks Charley,

I was wondering why they were on scene.

Truly terrible situation.

Bill
Reply With Quote
  #15  
Old 2/12/09, 12:41 AM
Jeff S. Vogan's Avatar
Jeff S. Vogan Jeff S. Vogan is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Default Re: Boiler Explosion

Russ, the Fire Marshals are done with their investigation. They stated that they found no other propane leaks in the system, so they deduce that it had to be from the pilot light being put out by a drip from the leaky boiler. Maybe the safety measures didn't work? I too, saw what I thought was a thermocoupler, but I am not an expert like these guys. The entire basement filled up with propane somehow...my bet, from the looks of the boiler, is that the pilot leaked.



Jeff Vogan
Vogan Home Inspections
Bevier, MO 63532
660-676-8835
www.reporthost.com/vogan
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Boiler Shutdown dkoniuk HVAC 2 8/6/07 10:34 AM
Boiler Control Recall ldapkus HVAC 0 1/25/07 5:50 PM
Boiler Recall bwiley HVAC 5 12/20/06 7:20 AM
Peerless gas boiler 53bako Plumbing 6 11/29/06 7:50 AM
Romex on a Boiler? mgifford Electrical 7 1/10/06 5:27 PM


All times are GMT -4. The time now is 7:02 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts