Default Boiler in garage

Am I correct to say a boiler located in a garage should be mounted a minimum of 18" above the floor?

The boiler is in its "seperate" little room, however there is no door to seal it away from the garage.

Would it be acceptable to make an 18" sealed "barrier" at the door to correct this?

Thanks,
Attached Thumbnails
boiler-garage-img_31941.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 8/15/07, 7:41 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Boiler in garage

Comments would be appreciated.

Thanks,



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #3  
Old 8/15/07, 7:58 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Boiler in garage

Quote:
Originally Posted by sfalvey
Am I correct to say a boiler located in a garage should be mounted a minimum of 18" above the floor?

Yes, the burners need to be 18" above the floor.

The boiler is in its "seperate" little room, however there is no door to seal it away from the garage.

Would it be acceptable to make an 18" sealed "barrier" at the door to correct this?

I am not familiar with an 18" tall barrier such as you describe.

A fume sealed door would be acceptable but then don't forget about combustion air.

Thanks,
See above notes.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 8/15/07, 10:53 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Boiler in garage

Thank you Larry,



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #5  
Old 8/15/07, 11:20 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: Boiler in garage

I have a home in FL with a gas water heater in the garage that is NOT elevated 18 inches above the finished floor. It was not required at the time the house was built. I do not know how old the home in question is, but something to keep in mind; What was the requirement at the time of construction?



Doug Edwards, CMI







Reply With Quote
  #6  
Old 8/16/07, 8:56 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Boiler in garage

Quote:
Originally Posted by dedwards
I have a home in FL with a gas water heater in the garage that is NOT elevated 18 inches above the finished floor. It was not required at the time the house was built. I do not know how old the home in question is, but something to keep in mind; What was the requirement at the time of construction?
Regardless, I would recommend it for enhanced safety.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 8/17/07, 10:04 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Boiler in garage

The house was renovated 8 years ago.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Evaporative cooler in garage chellickson HVAC 9 7/23/07 1:08 AM
Garage ceiling & door header Al Barb Interior 7 3/27/07 1:07 PM
Boiler Control Recall ldapkus HVAC 0 1/25/07 5:50 PM
Boiler Recall bwiley HVAC 5 12/20/06 7:20 AM
Romex on a Boiler? mgifford Electrical 7 1/10/06 5:27 PM


All times are GMT -4. The time now is 10:23 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts