Default Boiler in garage Part II

OK - It's "boiler in garage" week. The oil boiler is considered a sealed combustion device, right? However, the burner (source of ignition) should still be 18 off the floor. Bollards or some other form of protection should be installed --- or --- the whole mess can be enclosed and get its source of combustion air from the outside. Your thoughts?
Attached Thumbnails
boiler-garage-part-ii-oil-boiler-garage.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/6/11, 9:19 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Boiler in garage Part II

Quote:
Originally Posted by bsmith View Post
OK - It's "boiler in garage" week. The oil boiler is considered a sealed combustion device, right? However, the burner (source of ignition) should still be 18 off the floor. Bollards or some other form of protection should be installed --- or --- the whole mess can be enclosed and get its source of combustion air from the outside. Your thoughts?
Is that a gas dryer too?

Same problem as before.

Should build a room around both with a sealed door to the garage.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 8/6/11, 9:52 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Boiler in garage Part II

Electric dryer.
I wrote it up as a concern. Once again, it's been there since the house was built in '70 and I doubt anything will be changed. Thanks.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #4  
Old 8/6/11, 8:27 PM
Kenneth R. Brittain Kenneth R. Brittain is offline
InterNACHI Member
 
Join Date: Jul 2011
Location: Charlotte NC
Posts: 224
Default Re: Boiler in garage Part II

what happens if its in a sealed room with a door that open to the garage and there are combustible gasses in the garage and you open the door to the boiler room....Kaboom...so I would think that it either needs to be elevated 18" or the door needs to open to the outside.
Reply With Quote
  #5  
Old 8/6/11, 8:46 PM
Harry D. Vandermeulen Harry D. Vandermeulen is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sarasota, FL
Posts: 57
Default Re: Boiler in garage Part II

Is that a gas hot water heater also? Both need to be elevated and protected.
Reply With Quote
  #6  
Old 8/6/11, 9:36 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Boiler in garage Part II

The combustion air source should be from the exterior. The WH is an indirect-fired unit. Thanks guys.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage door inspection procedure bgromicko General Inspection Discussion 5 8/7/09 12:47 PM
Boiler Recall bwiley Inspecting HVAC Systems 5 12/20/06 6:20 AM
Peerless gas boiler 53bako Plumbing Inspections 6 11/29/06 6:50 AM
Boiler question dmacy Inspecting HVAC Systems 15 2/22/06 10:56 PM
Romex on a Boiler? mgifford Electrical Inspections 7 1/10/06 4:27 PM


All times are GMT -4. The time now is 11:22 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts