Clay lined masonry chimney used to vent both the water heater and boiler both NG. The w/h vent has a liner that extends to the top of the chimney. The boiler is a 12 year old 80+ efficiency that has no liner. Evidence of condensation rusting out galv at point where the vent enters the chimney. Is a liner required for the boiler?
Thanks "He is no fool who gives what he cannot keep to gain that which he cannot lose." Jim Elliot 1949 Gerald Wilcox Harvey, ND CMIA, RMT www.housecheckhomeinspections.com www.homeinspectorinnorthdakota.com 701.324.4075 Minot, ND Home Inspections Devil's Lake, ND Home Inspections Bismarck, ND Home Inspections Jamestown, ND Home Inspections Home Inspector in North Dakota North Dakota Home Inspection |
| Need a home inspection in California? Check out InterNACHI's listing of California certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Don't go there.
Recommend a level 2 chimney inspection by a qualified person. As a research project I would acquaint yourself with the boiler mfg. recommendations for the flue. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#3
|
||||
|
||||
|
Yes, it needs a liner or b-vent if it is vented in a masonry chimney.
Thanks "He is no fool who gives what he cannot keep to gain that which he cannot lose." Jim Elliot 1949 Gerald Wilcox Harvey, ND CMIA, RMT www.housecheckhomeinspections.com www.homeinspectorinnorthdakota.com 701.324.4075 Minot, ND Home Inspections Devil's Lake, ND Home Inspections Bismarck, ND Home Inspections Jamestown, ND Home Inspections Home Inspector in North Dakota North Dakota Home Inspection |
|
#4
|
|||
|
|||
|
I agree with the requirement of a pipe. If it was a old oil furnace that would be ok. The exhaust gases are not hot enough to warm the whole mass of cold air in the chimney and it's causing your rusting issues. Plus if the seal between the pipe and the masonry isn't good you could be getting spillage back into the structure.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Water heater vent pipe...Question | dnasser | Inspecting HVAC Systems | 4 | 11/27/10 12:59 PM |
| Black stove vent pipe on oil boiler | jcampbell | Inspecting HVAC Systems | 6 | 5/3/10 11:18 PM |
| Plumbing vent Routing Question | kweiss | Plumbing Inspections | 7 | 11/1/06 9:57 PM |