Default Boiler vent question

Clay lined masonry chimney used to vent both the water heater and boiler both NG. The w/h vent has a liner that extends to the top of the chimney. The boiler is a 12 year old 80+ efficiency that has no liner. Evidence of condensation rusting out galv at point where the vent enters the chimney. Is a liner required for the boiler?
Thanks
Reply With Quote
Need a home inspection in California? Check out InterNACHI's listing of California certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/9/11, 11:11 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Boiler vent question

Don't go there.

Recommend a level 2 chimney inspection by a qualified person.

As a research project I would acquaint yourself with the boiler mfg. recommendations for the flue.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 1/9/11, 2:24 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Boiler vent question

Yes, it needs a liner or b-vent if it is vented in a masonry chimney.
Thanks
Reply With Quote
  #4  
Old 1/9/11, 2:41 PM
Robert Ernst Robert Ernst is online now
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Boiler vent question

I agree with the requirement of a pipe. If it was a old oil furnace that would be ok. The exhaust gases are not hot enough to warm the whole mass of cold air in the chimney and it's causing your rusting issues. Plus if the seal between the pipe and the masonry isn't good you could be getting spillage back into the structure.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water heater vent pipe...Question dnasser Inspecting HVAC Systems 4 11/27/10 12:59 PM
Black stove vent pipe on oil boiler jcampbell Inspecting HVAC Systems 6 5/3/10 11:18 PM
Plumbing vent Routing Question kweiss Plumbing Inspections 7 11/1/06 9:57 PM


All times are GMT -4. The time now is 11:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts