Default Boiler / W/H in garage?

Picture 1 is the garage
Picture 2 is the back of the garage
Picture 3 - a left and another left
Picture 4 - Boiler and WH.

To my way of thinking, they are still in the garage, even though a wall separates them from direct contact with the garage.
BTW - The WH is an FVIR unit.

Picture 5 is a flue tile lined vent to the exterior that runs under the house (currently blocked by a piece of wood). This vent must have been the source of combustion air before the renovation. Your thoughts?
Attached Thumbnails
boiler-w-h-garage-1.jpg   boiler-w-h-garage-2.jpg   boiler-w-h-garage-3.jpg   boiler-w-h-garage-4.jpg   boiler-w-h-garage-5.jpg  




"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/3/11, 2:59 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Boiler / W/H in garage?

My first thought is "oh no" which melted to Boilers are not like HVAC units in that you are not bringing air in to the house from the garage.

Is the space big enough that combustion air is not an issue?

many areas require 18 inches above the floor but some do not .
Check pipe penetrations or any for that matter which lead into the home .

Why are garages (both attached and detached) fire hazards?
Oil or gasoline can drip from cars. These fluids may collect unnoticed and eventually ignite.
Flammable liquids, such as gasoline, oil and paint, are commonly stored in garages. Some other examples are brake fluid, degreaser, motor oil, varnish, lighter fluid, and fluids containing solvents, such as paint thinner. These chemicals are flammable in their fluid form, and some may create explosive vapors.
Heaters and boilers, which are frequently installed in garages, create sparks that can ignite fumes or fluids. Car batteries, too, will spark under certain conditions.
Mechanical or electrical building projects are often undertaken in the garage. Fires can easily start while a careless occupant is welding near flammable materials.
Doors
Reply With Quote
  #3  
Old 8/3/11, 3:07 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Boiler / W/H in garage?

This is a garage/basement type arrangement. All of the living spaces are above.
The space is definitely big enough, but I'm concerned about gas vapors from the cars hitting the boiler flames.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #4  
Old 8/3/11, 3:21 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Boiler / W/H in garage?

Ask Robert he is the AHJ in your area.
It would be a no go for Ontario. We are still on the same page for B149.1-05 and the B139, 18 inches minimum elevation is required and no passage of air through the home. I cannot comment on your air requirements coming from under the garage.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #5  
Old 8/3/11, 3:51 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Boiler / W/H in garage?

he 2006 edition of the IRC states the following concerning garage walls and ceilings:

********* R309.2 Separation Required
The garage shall be separated from the residence and its attic area by not less than ½-inch (12.7 mm) gypsum board applied to the garage side. Garages beneath habitable rooms shall be separated from all habitable rooms above by not less than 5/8-inch (15.9 mm) Type X gypsum board or equivalent. Where the separation is a floor-ceiling assembly, the structure supporting the separation shall also be protected by not less than ½-inch (12.7 mm) gypsum board or equivalent. Garages located less than 3 feet (914 mm) from a dwelling unit on the same lot shall be protected with not less than 1/2–inch (12.7 mm) gypsum board applied to the interior side of exterior walls that are within this area. Openings in these walls shall be regulated by Section 309.1. This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall.
In addition, inspectors can check for the following while inspecting walls and ceilings:

In garages that have access to the attic, a hatch cover made from an approved, fire-rated material should protect this access at all times. Missing or opened covers should be called out, as should covers made from flammable materials, such as thin plywood.*Garage attic door must be constructed such that the 45 minute rating*is maintained; any drywall edges on both the hatch and the surrounding*area exposed to physical damage are protected.*The cover or door is installed so that it is permanent (non removable)*with hardware to maintain it in a closed position with latching*hardware to maintain it in a closed position. This could be*accomplished by the use of spring loaded hinges, door closer, or*hardware that will not allow it to be left in an open position when not in*use. A single bolt type or hook and eye hardware does not provide a*positive closure since these would allow the door to be left open.*Likewise drywall screws are "fasteners" and not hardware so they*cannot be used as the only means of keeping access doors closed.
The living space is separated from the garage by a firewall that extends from the floor to the roof. If the ceiling material is fire-rated, the firewall can terminate at the ceiling.
Drywall joints*shall be taped or sealed.*Joints shall be fitted so that the gap is no more than 1/20-inch*with joints backed by either solid wood or another layer of drywall*such that the joints are staggered.*
Reply With Quote
  #6  
Old 8/3/11, 4:18 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Boiler / W/H in garage?

Quote:
Originally Posted by belliott View Post
he 2006 edition of the IRC states the following concerning garage walls and ceilings:

********* R309.2 Separation Required
The garage shall be separated from the residence and its attic area by not less than ½-inch (12.7 mm) gypsum board applied to the garage side. Garages beneath habitable rooms shall be separated from all habitable rooms above by not less than 5/8-inch (15.9 mm) Type X gypsum board or equivalent. Where the separation is a floor-ceiling assembly, the structure supporting the separation shall also be protected by not less than ½-inch (12.7 mm) gypsum board or equivalent. Garages located less than 3 feet (914 mm) from a dwelling unit on the same lot shall be protected with not less than 1/2–inch (12.7 mm) gypsum board applied to the interior side of exterior walls that are within this area. Openings in these walls shall be regulated by Section 309.1. This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall.
In addition, inspectors can check for the following while inspecting walls and ceilings:

In garages that have access to the attic, a hatch cover made from an approved, fire-rated material should protect this access at all times. Missing or opened covers should be called out, as should covers made from flammable materials, such as thin plywood.*Garage attic door must be constructed such that the 45 minute rating*is maintained; any drywall edges on both the hatch and the surrounding*area exposed to physical damage are protected.*The cover or door is installed so that it is permanent (non removable)*with hardware to maintain it in a closed position with latching*hardware to maintain it in a closed position. This could be*accomplished by the use of spring loaded hinges, door closer, or*hardware that will not allow it to be left in an open position when not in*use. A single bolt type or hook and eye hardware does not provide a*positive closure since these would allow the door to be left open.*Likewise drywall screws are "fasteners" and not hardware so they*cannot be used as the only means of keeping access doors closed.
The living space is separated from the garage by a firewall that extends from the floor to the roof. If the ceiling material is fire-rated, the firewall can terminate at the ceiling.
Drywall joints*shall be taped or sealed.*Joints shall be fitted so that the gap is no more than 1/20-inch*with joints backed by either solid wood or another layer of drywall*such that the joints are staggered.*
My concern is for the possibility of gas vapors igniting, not the fire wall. -



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #7  
Old 8/3/11, 4:25 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Boiler / W/H in garage?

I would then recommend the 18.
Reply With Quote
  #8  
Old 8/3/11, 6:26 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Boiler / W/H in garage?

Quote:
Originally Posted by kwood View Post
Ask Robert he is the AHJ in your area.
Nope... a former AHJ (one of the hats I have worn). I run my own business now ...

Quote:
Originally Posted by bsmith View Post
My concern is for the possibility of gas vapors igniting, not the fire wall. -
Spaces adjacent to the garage that are not part of the house with the required fire separation are considered part of the garage. So the boiler as an ignition source is a concern (not the FVIR WH). The boiler could either be elevated (pretty involved) or they might be able to create a fire separated mechanical room with a self closing door and combustion air intake. Also recommend permits for any work like that.

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 8/4/11 at 10:31 AM..
Reply With Quote
  #9  
Old 8/3/11, 7:19 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Boiler / W/H in garage?

I meant you are from NY and an authority according to your position.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #10  
Old 8/4/11, 10:48 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Boiler / W/H in garage?

Quote:
Originally Posted by roconnor View Post
Nope... a former AHJ (one of the hats I have worn). I run my own business now ...


Spaces adjacent to the garage that are not part of the house with the required fire separation are considered part of the garage. So the boiler as an ignition source is a concern (not the FVIR WH). The boiler could either be elevated (pretty involved) or they might be able to create a fire separated mechanical room with a self closing door and combustion air intake. Also recommend permits for any work like that.

JMO & 2-Nickels ...
That's how I wrote it. Thanks.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #11  
Old 8/4/11, 10:53 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Boiler / W/H in garage?

I hope you added at least 18 inches as a reference. They may think you need to raise it to prevent rust and you know what that means.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #12  
Old 8/4/11, 2:12 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Boiler / W/H in garage?

The boiler was on a small raised concrete platform so rust wasn't an issue. I just recommended closing off that portion of the garage and getting combustion air from the exterior. Apparently the AHJ approved the set up years ago, so I don't expect them to do much (if anything), but at least I made my recommendations.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #13  
Old 8/4/11, 6:33 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Boiler / W/H in garage?

That is what I would do also in this application. Raising it would be much more expensive as to a plumbers prices over a wall with X-type drywall and sealed fire proof door with a closing hinge.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inspecting Forced Hot Water Boiler help jscaparo Inspecting HVAC Systems 2 8/12/10 1:32 PM
Garage floor same level as house a safety concern? thorn2 General Inspection Discussion 11 1/25/10 3:33 PM
Garage door inspection procedure bgromicko General Inspection Discussion 5 8/7/09 12:47 PM
Boiler in garage sfalvey Inspecting HVAC Systems 6 8/17/07 9:04 PM
Boiler Control Recall ldapkus Inspecting HVAC Systems 0 1/25/07 4:50 PM


All times are GMT -4. The time now is 11:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts