Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information
Send a message via ICQ to kshepard
Default Boilerless radient in-floor heat using tankless water heaters

Wave of the future here and in any state with cold winters that offers sufficient tax incentives.
Closed burner chamber, but there should be a cleanable filter and a manifold installed which can be verified by inspectors according to the rep I spoke with today.




Kenton Shepard, NACHI member # 04082383
Peak to Prairie Inspection Service
Certified Master Inspector (CMI)

Inspection of Conventional,
Log, Strawbale and
Historic Homes
(303) 258-8289


Last edited by kshepard; 10/2/08 at 2:40 AM.
Reply With Quote
  #2  
Old 12/6/06, 9:55 PM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 846
Steven C. Waskewicz is almost always very helpful Steven C. Waskewicz is almost always very helpful Steven C. Waskewicz is almost always very helpful Steven C. Waskewicz is almost always very helpful Steven C. Waskewicz is almost always very helpful Steven C. Waskewicz is almost always very helpful
Default Re: Boilerless radient in-floor heat using tankless water heaters

Interesting system.
I currently have forced hot water, baseboard heat, and have thought that if
I add an addition, or retrofit our kitchen, I'd convert to a similar setup using the PEX type plumbing myself.
These seem to be a plumbers dream, considering how flexible they are.
Thanks Kenton. Great to see photos like this.
Steve



Steven Waskewicz
Rest Assured Inspection Services, LLC.
12615 Halleluiah Trail
Elbert, Colorado 80106
Office 719-510-7703 mobile all the time
Fax 719-495-7166
Serving Colorado Springs, and surrounding areas.

www.restassuredinspection.com
s_waskewicz@msn.com
NACHIiid=NACHI06032370



Reply With Quote
  #3  
Old 12/6/06, 11:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Boilerless radient in-floor heat using tankless water heaters




Pass the Salsa you are going to need it for all of that spaghetti
Reply With Quote
  #4  
Old 12/6/06, 11:33 PM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 447
jschulte is generally well trusted
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boilerless radient in-floor heat using tankless water heaters

Wow, it looks like they should have invested in a Manibloc. That is a mess. How big was the house?
Reply With Quote
  #5  
Old 12/7/06, 6:26 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 15,860
Russel Ray .
Default Re: Boilerless radient in-floor heat using tankless water heaters

No wonder why the cost of copper is so high.



  • Need a positive networking site? Click here to join Active Rain, a networking community of 125,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #6  
Old 12/7/06, 11:16 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Denver, CO
Posts: 1,940
Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information
Send a message via ICQ to kshepard
Default Re: Boilerless radient in-floor heat using tankless water heaters

Quote:
Originally Posted by jschulte
Wow, it looks like they should have invested in a Manibloc. That is a mess. How big was the house?
About 3000 sq ft




Kenton Shepard, NACHI member # 04082383
Peak to Prairie Inspection Service
Certified Master Inspector (CMI)

Inspection of Conventional,
Log, Strawbale and
Historic Homes
(303) 258-8289

Reply With Quote
  #7  
Old 12/22/06, 3:11 AM
Jeremy Tucker Jeremy Tucker is offline
New User
 
Join Date: Dec 2006
Location: Spruce Grove, Alberta, Canada
Posts: 7
Jeremy Tucker hasn't had much positive or negative feedback
Please Note: Jeremy Tucker is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boilerless radient in-floor heat using tankless water heaters

I hate to say it but as new as this is to you guys, we've been installing these sytems in Canada for a few years now. The "tankless water heater" as you call it is no less than a wall mount High efficient boiler. The rest of the system outside the boiler is standard with most heating systems... but yes I would definatly recommend the installation of a sidestream filter assembly with sight glass. It is a must with any heating system. It will save a fortune in repair bills from clogged or seized pumps due to sediment and debris. Also I would have the system water tested for TDS and ph. Depending on the local water source, corrosion inhibitors may be required. Who wants to pay more money 3 years after having it installed because the piping is corroding?
Reply With Quote
  #8  
Old 12/22/06, 5:18 AM
wforsyth's Avatar
wforsyth wforsyth is offline
Active Poster
 
Join Date: Feb 2006
Location: Brinnon, Wa
Posts: 7,928
wforsyth has posted mostly unhelpful information
Please Note: wforsyth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boilerless radient in-floor heat using tankless water heaters

Almost all of the homes I've been doing draw inspections for, have these systems. They're awesome. I really am impressed with the whole idea and would love to install something similar.

The other thing I'm very impressed with is:http://www.motherearthnews.com/Alter...e-Solar-Heater

Can be built for $300 and has a 20 year minimum life span.
Reply With Quote
  #9  
Old 12/22/06, 12:02 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Denver, CO
Posts: 1,940
Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information
Send a message via ICQ to kshepard
Default Re: Boilerless radient in-floor heat using tankless water heaters

Quote:
Originally Posted by Jeremy Tucker
I hate to say it but as new as this is to you guys, we've been installing these sytems in Canada for a few years now. The "tankless water heater" as you call it is no less than a wall mount High efficient boiler. The rest of the system outside the boiler is standard with most heating systems... but yes I would definatly recommend the installation of a sidestream filter assembly with sight glass. It is a must with any heating system. It will save a fortune in repair bills from clogged or seized pumps due to sediment and debris. Also I would have the system water tested for TDS and ph. Depending on the local water source, corrosion inhibitors may be required. Who wants to pay more money 3 years after having it installed because the piping is corroding?
Filter- is this basically a silt filter like we see on well equipment?

What's TDS?

What should the PH be?




Kenton Shepard, NACHI member # 04082383
Peak to Prairie Inspection Service
Certified Master Inspector (CMI)

Inspection of Conventional,
Log, Strawbale and
Historic Homes
(303) 258-8289

Reply With Quote
  #10  
Old 12/22/06, 12:27 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,403
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Boilerless radient in-floor heat using tankless water heaters

Quote:
Originally Posted by kshepard
Filter- is this basically a silt filter like we see on well equipment?

What's TDS?

What should the PH be?
TDS= Total Dissolved Solids

PH- Depends on the heat exchanger material - consult mfg. recommendations


The pH of water is an indication of how acid or alkaline it is. The scale runs from 0 to 14, with a pH of 7 being neutral. The nearer to 0 the pH value is, the more acidic and, conversely, the nearer the value is to 14, the more alkaline the water.

The corrosion rate of ferrous metals and copper becomes increasingly rapid as the pH falls below 6, and it is therefore important to ensure that all residues of acidic flushing chemicals are removed after power flushing.


Aluminium heat exchangers and radiators are prone to corrosion when the pH is less than 6, or above 8.5.

Copper
is adversely affected when the pH is above 9.5, as may happen when alkaline flushing chemicals or inhibitors are used, or when softened water is used to fill the system.

Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Tankless Water Heater Recall ldapkus Plumbing 1 2/22/07 9:34 PM
Need Help On Chimney Liners Nick Scibetta Exterior 10 1/11/06 10:53 PM


All times are GMT -4. The time now is 5:14 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics