Ac unit called for max size breaker of 30 amps. The breaker in the panel is 40 amps. Wrong yes, but what are the consequences? Is it necessary to put in a 30amp breaker?
David InterNACHI #08051301 NYS Lic. #16000038229 NYS DEC Cert # T4865884 518-505-8305 HouseAbout Home Inspections HouseAbout on Facebook NY Capital Region Chapter InterNACHI |
| Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
I call it out every time. Could void a warranty. But I also think the manufacture puts this on a data plate for a reason.
The way I look at it, is what if 2 years from now they sell the place and the next inspector calls it out. Do you think they would wonder why you didn't call it out? Comprehensive Building Consultants Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection. Donate here: or send checks to the Fl Home and Insurance Inspector Chapter 1103 W Hibiscus Blvd Ste 311 Melbourne, Fl 32901
|
|
#3
|
|||
|
|||
|
The consequences is the thing pulls more than 30 amps but not the 40 to trip the breaker and the insulation on the wires start to melt.
|
|
#4
|
||||
|
||||
|
Quote:
The concern with an oversized breaker is typically possible damage to the equipment. What are the size of the wires feeding the unit and the "minimum circuit ampacity" from the nameplate? Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#5
|
||||
|
||||
|
Perhaps the question should be; Is the breaker the appropriate size to protect the conductors attached to it. If so, then you can move on to the question of if the breaker is sufficient to protect the equipment.
Rick Strand, CPI CAHPI Associate Strand Home Inspections Inc. Calgary, Alberta, Canada Serving Calgary, Okotoks, Airdrie, Chestermere and Cochrane Alberta
|
|
#6
|
||||
|
||||
|
Quote:
David InterNACHI #08051301 NYS Lic. #16000038229 NYS DEC Cert # T4865884 518-505-8305 HouseAbout Home Inspections HouseAbout on Facebook NY Capital Region Chapter InterNACHI |
|
#7
|
||||
|
||||
|
I think the installer may have been confused with the HACR required breaker, and the 125% rule, thus the 40amp breaker.
Here's a discussion regarding HACR breakers... starts off a bit off topic, but get's right to the point of this topic further down... http://forums.mikeholt.com/showthrea...-HACR-Breakers Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#8
|
||||
|
||||
|
was the OCD in the panel the only means of disconnect or is there a disco at the condensing unit that is properly sized for the equipment in question
ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#9
|
||||
|
||||
|
Looks more like a #6 AL wire ... but either one would work (actually #12 CU or #10 AL with a 30A OCPD would work). My bet is it's replacement equipment that draws less, and they didn't bother to change the breaker ...
Quote:
If it doesn't have a 30A breaker/fuse disconnect, it's still a pretty easy breaker swap out (Yes it needs to be changed, and No it doesnt need to be an HACR type) ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 8/4/11 at 2:05 PM.. |
|
#10
|
||||
|
||||
|
Exterior disconnect is the pull type. The condenser was manufactured in 2002. The panel was upgraded a few years ago, after the AC unit was installed.
David InterNACHI #08051301 NYS Lic. #16000038229 NYS DEC Cert # T4865884 518-505-8305 HouseAbout Home Inspections HouseAbout on Facebook NY Capital Region Chapter InterNACHI |
|
#11
|
||||
|
||||
|
They may have just installed whatever was there before in terms of the breaker rating, or the old panel had a 30A breaker and they just installed a breaker to match the wire size. A #6 Al wire typically matches a 40A breaker so I can see that happening.
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#12
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The breaker is only there for short circuit and ground fault protection and is not sized to protect the conductors from overloading. That is accomplished by the thermal overloads in the unit. With a MCA of 18.9 amps you could use #14 conductors on a 30 amp OCPD and be 2008 NEC compliant.
|
|
#13
|
||||
|
||||
|
Quote:
A/C condensers are UL listed devices, simply follow the label. The conductor must meet minimum ampacity and the OCD must not exceed the listed rating (some also list a minimum). Just make sure that you refer to the true OCD. Chuck Evans (TREC #7657) Level III Infraspection Institute Certified Infrared Thermographer (#8402) HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook Houston Thermal Inspections & Infrared Imaging Find us on Facebook Houston Home Inspector Houston, TX |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| Main panel...recommendation ? | dnasser | Electrical Inspections | 6 | 11/22/09 9:55 PM |
| Re-Inspection | apolillo | Electrical Inspections | 7 | 11/14/09 7:01 PM |
| Breaker Question | rsole | Electrical Inspections | 6 | 11/23/08 9:57 PM |
| Breaker Question | mhawley | Electrical Inspections | 5 | 1/14/08 3:25 PM |