Default breaker too large for AC

Ac unit called for max size breaker of 30 amps. The breaker in the panel is 40 amps. Wrong yes, but what are the consequences? Is it necessary to put in a 30amp breaker?



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/3/11, 7:11 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: breaker too large for AC

I call it out every time. Could void a warranty. But I also think the manufacture puts this on a data plate for a reason.

The way I look at it, is what if 2 years from now they sell the place and the next inspector calls it out. Do you think they would wonder why you didn't call it out?



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #3  
Old 8/3/11, 7:15 PM
Robert Ernst Robert Ernst is online now
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: breaker too large for AC

The consequences is the thing pulls more than 30 amps but not the 40 to trip the breaker and the insulation on the wires start to melt.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #4  
Old 8/4/11, 10:48 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: breaker too large for AC

Quote:
Originally Posted by dokeefe View Post
Ac unit called for max size breaker of 30 amps. The breaker in the panel is 40 amps. Wrong yes, but what are the consequences? Is it necessary to put in a 30amp breaker?
Could have been a bad initial install. But it's likely replacement equipment with the circuit wires sized for the old unit nameplate/breaker. Newer equipment typically draws less current, so this is a common defect for replacement equipment.

The concern with an oversized breaker is typically possible damage to the equipment. What are the size of the wires feeding the unit and the "minimum circuit ampacity" from the nameplate?



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #5  
Old 8/4/11, 12:14 PM
Rick Strand's Avatar
Rick Strand Rick Strand is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Calgary, Alberta, Canada
Posts: 266
Default Re: breaker too large for AC

Perhaps the question should be; Is the breaker the appropriate size to protect the conductors attached to it. If so, then you can move on to the question of if the breaker is sufficient to protect the equipment.



Rick Strand, CPI
CAHPI Associate
Strand Home Inspections Inc.
Calgary, Alberta, Canada
Serving Calgary, Okotoks, Airdrie, Chestermere and Cochrane Alberta
Reply With Quote
  #6  
Old 8/4/11, 12:42 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: breaker too large for AC

Quote:
Originally Posted by roconnor View Post
Could have been a bad initial install. But it's likely replacement equipment with the circuit wires sized for the old unit nameplate/breaker. Newer equipment typically draws less current, so this is a common defect for replacement equipment.

The concern with an oversized breaker is typically possible damage to the equipment. What are the size of the wires feeding the unit and the "minimum circuit ampacity" from the nameplate?
Looks to be #8 Al wire size? and min. circuit amp is 18.9
Attached Thumbnails
breaker-too-large-ac-019.jpg   breaker-too-large-ac-085.jpg  



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #7  
Old 8/4/11, 1:08 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: breaker too large for AC

I think the installer may have been confused with the HACR required breaker, and the 125% rule, thus the 40amp breaker.

Here's a discussion regarding HACR breakers... starts off a bit off topic, but get's right to the point of this topic further down... http://forums.mikeholt.com/showthrea...-HACR-Breakers
Reply With Quote
  #8  
Old 8/4/11, 1:34 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: breaker too large for AC

was the OCD in the panel the only means of disconnect or is there a disco at the condensing unit that is properly sized for the equipment in question



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #9  
Old 8/4/11, 1:50 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: breaker too large for AC

Quote:
Originally Posted by dokeefe View Post
Looks to be #8 Al wire size? and min. circuit amp is 18.9
Looks more like a #6 AL wire ... but either one would work (actually #12 CU or #10 AL with a 30A OCPD would work). My bet is it's replacement equipment that draws less, and they didn't bother to change the breaker ...

Quote:
Originally Posted by badair View Post
was the OCD in the panel the only means of disconnect or is there a disco at the condensing unit that is properly sized for the equipment in question
Good question ... most modern disconnects at the condenser are the pull-type. But there could be a breaker/fuse type disconnect at the unit with a 30A rating which would then be fine.

If it doesn't have a 30A breaker/fuse disconnect, it's still a pretty easy breaker swap out (Yes it needs to be changed, and No it doesnt need to be an HACR type) ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 8/4/11 at 2:05 PM..
Reply With Quote
  #10  
Old 8/4/11, 3:53 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: breaker too large for AC

Exterior disconnect is the pull type. The condenser was manufactured in 2002. The panel was upgraded a few years ago, after the AC unit was installed.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #11  
Old 8/4/11, 4:40 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: breaker too large for AC

Quote:
Originally Posted by dokeefe View Post
Exterior disconnect is the pull type. The condenser was manufactured in 2002. The panel was upgraded a few years ago, after the AC unit was installed.
They may have just installed whatever was there before in terms of the breaker rating, or the old panel had a 30A breaker and they just installed a breaker to match the wire size. A #6 Al wire typically matches a 40A breaker so I can see that happening.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #12  
Old 8/5/11, 6:33 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,253
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: breaker too large for AC

Quote:
Originally Posted by rstrand View Post
Perhaps the question should be; Is the breaker the appropriate size to protect the conductors attached to it. If so, then you can move on to the question of if the breaker is sufficient to protect the equipment.
The breaker is only there for short circuit and ground fault protection and is not sized to protect the conductors from overloading. That is accomplished by the thermal overloads in the unit. With a MCA of 18.9 amps you could use #14 conductors on a 30 amp OCPD and be 2008 NEC compliant.
Reply With Quote
  #13  
Old 8/5/11, 9:40 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: breaker too large for AC

Quote:
Originally Posted by roconnor View Post
Looks more like a #6 AL wire ... but either one would work (actually #12 CU or #10 AL with a 30A OCPD would work). My bet is it's replacement equipment that draws less, and they didn't bother to change the breaker ...


Good question ... most modern disconnects at the condenser are the pull-type. But there could be a breaker/fuse type disconnect at the unit with a 30A rating which would then be fine.

If it doesn't have a 30A breaker/fuse disconnect, it's still a pretty easy breaker swap out (Yes it needs to be changed, and No it doesnt need to be an HACR type) ...
Most of the "breakers" that you see as disconnects are not overcurrent devices regardless of the amp rating that you see on the handle. Read the labels on them carefully and you will see that most say that they are not overcurrent devices.

A/C condensers are UL listed devices, simply follow the label. The conductor must meet minimum ampacity and the OCD must not exceed the listed rating (some also list a minimum). Just make sure that you refer to the true OCD.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Re-Inspection apolillo Electrical Inspections 7 11/14/09 7:01 PM
Breaker Question rsole Electrical Inspections 6 11/23/08 9:57 PM
Breaker Question mhawley Electrical Inspections 5 1/14/08 3:25 PM


All times are GMT -4. The time now is 11:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts