Default Buried Suction/liquid lines?

What problems will these buried lines cause?

Thanks,
Reese
Attached Thumbnails
buried-suction-liquid-lines-aclines.jpg  
Reply With Quote
  #2  
Old 5/24/07, 12:05 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Buried Suction/liquid lines?

Are they actually buried, or just covered with a thick layer of fallen pine needles?
Reply With Quote
  #3  
Old 5/24/07, 12:21 AM
rmc3inspection's Avatar
rmc3inspection rmc3inspection is offline
New User
 
Join Date: Jul 2006
Location: North Carolina
Posts: 24
Please Note: rmc3inspection is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Suction/liquid lines?

I pulled the loose pine straw back (which was placed there, no pine trees in the area) and dug a little with my hands to see if I could get a look at the insulation. But only removed about an inch of loose dirt/decomposed mulch before I hit solid soil. I spread the pinestraw back over before I took the picture. I would guess that it was buried maybe 3-4 inches at it's deepest spot. (just a guess)
Reply With Quote
  #4  
Old 5/24/07, 7:54 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Buried Suction/liquid lines?

Quote:
Originally Posted by rmc3inspection
What problems will these buried lines cause?

Thanks,
Reese
Does not appear to have enough trap built in to cause any significant oil return problems.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 5/24/07, 9:08 AM
rmc3inspection's Avatar
rmc3inspection rmc3inspection is offline
New User
 
Join Date: Jul 2006
Location: North Carolina
Posts: 24
Please Note: rmc3inspection is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Suction/liquid lines?

Would you write anything about possible damage to the insulation? Is there any effect of the soils extra insulation of the lines? What about deterioration of lines from minerals in the soil and soil moisture? Would you write this up?

Thanks guys,
Reese
Reply With Quote
  #6  
Old 5/24/07, 1:51 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Buried Suction/liquid lines?

Quote:
Originally Posted by rmc3inspection
Would you write anything about possible damage to the insulation? Is there any effect of the soils extra insulation of the lines? What about deterioration of lines from minerals in the soil and soil moisture? Would you write this up?

Thanks guys,
Reese
Nope would not write it up we bury copper in the ground on a regular basis (Water lines) the ground is a pretty good insulator to begin with. Too picky for me.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 5/24/07, 8:47 PM
rmc3inspection's Avatar
rmc3inspection rmc3inspection is offline
New User
 
Join Date: Jul 2006
Location: North Carolina
Posts: 24
Please Note: rmc3inspection is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Suction/liquid lines?

What about not being able to inspect the buried portion of the lines for leaks and deteriorated insulation?
Reply With Quote
  #8  
Old 5/24/07, 9:45 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Suction/liquid lines?

That is such a small section of line, there is no need to worry about it. As for deterioration of insulation, the situation is no worse than the effects of weather. And if there is no oily residue in the soil, there is no leak.
Reply With Quote
  #9  
Old 5/25/07, 7:00 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Buried Suction/liquid lines?

Quote:
Originally Posted by rmc3inspection
What about not being able to inspect the buried portion of the lines for leaks and deteriorated insulation?
As a Hi I don't inspect for leaks in freon lines the unit either works as intended or not. As for the insulation the soil is probally a better insulator than the foam. I see to many suction lines with the insulation totally missing dogs like to chew it off. I don't even write that up consider it normal wear. Some inspectors may perfer to write things like that up I don't to me that is just window dressing for reports fluffing the reports. I go for the good stuff
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 5/25/07, 7:07 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Buried Suction/liquid lines?

The purpose of the insulation on a refrigerant line set is not to thermally insulate the pipe for efficiency purposes, it is to prevent contact with the outdoor air which has a high concentration of moisture in it. The suction line operates at 40°F if the refrigeration pressure is 70 PSI. This causes a substantial amount of condensation and if it occurs inside the house or inside a wall or ceiling, guess what happens?


There are no issues that I know of with burying a refrigeration line set.
Reply With Quote
  #11  
Old 5/25/07, 7:24 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Buried Suction/liquid lines?

Quote:
Originally Posted by dandersen
The purpose of the insulation on a refrigerant line set is not to thermally insulate the pipe for efficiency purposes, it is to prevent contact with the outdoor air which has a high concentration of moisture in it. The suction line operates at 40°F if the refrigeration pressure is 70 PSI. This causes a substantial amount of condensation and if it occurs inside the house or inside a wall or ceiling, guess what happens?


There are no issues that I know of with burying a refrigeration line set.
Good morning David how the Hell are you.

I also agree with your statement but I also like that suction temp to be as cold coming back as possible as you know that is what cools the compressor windings and the cooler it operates the longer it last just my thoughts.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 5/25/07, 8:34 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Buried Suction/liquid lines?

Yup, I call out and report on sub-cooling temps at the compressor during my HAVC Inspections.

You may have sufficient refrigerant to cool the house, but the compressor will fail from thermal.

An old fart, partner of mine taught me how to charge refrigerant with his hand (forget all those tools, he would say!) when I first got started. Lesson learned; if there is insufficient capacity of the refrigerant to draw heat from your hand, there is nothing left for the compressor.
Reply With Quote
  #13  
Old 5/25/07, 8:40 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Buried Suction/liquid lines?

Quote:
Good morning David how the Hell are you.
I'm fine! I see your in there kicking ***** with the rest of us!

Was thinking of going fishing this morning! No wind! Bad weekend coming up and don't want to fight the crowd! Did my quota for the week and have them stacked up for next week! I think I'll slip out of here!
Reply With Quote
  #14  
Old 5/25/07, 9:43 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Buried Suction/liquid lines?

Quote:
Originally Posted by dandersen
Yup, I call out and report on sub-cooling temps at the compressor during my HAVC Inspections.

You may have sufficient refrigerant to cool the house, but the compressor will fail from thermal.

An old fart, partner of mine taught me how to charge refrigerant with his hand (forget all those tools, he would say!) when I first got started. Lesson learned; if there is insufficient capacity of the refrigerant to draw heat from your hand, there is nothing left for the compressor.
This is very true can tell more with my hands than most of the younger guys with two sets of gages Old fart you know

Don't have time for fishing wished I did use to chase the strippers heavy in the old days. Got two big inspects and a re-inspect today gotta go its that time Don't catch them all save some for seed
</IMG></IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #15  
Old 5/25/07, 11:29 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Suction/liquid lines?

Amen to the hand check! And I thought I was alone on this! When you feel that suction line begin to draw heat from your hand, cut it off! In a few seconds, voila! You have a perfectly charged unit. Considering the unit is clean, the head and suction pressures should be right on given the ambient temp.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas supply lines to water heaters. dkoehl Plumbing Inspections 5 3/6/11 2:07 AM
Buried Oil storage tank brepanshek Inspecting HVAC Systems 6 1/29/07 10:07 PM
Blackened Copper Lines thejnicki Plumbing Inspections 3 8/1/06 9:47 AM
Flexible stainless steel lines? five.five Plumbing Inspections 9 7/27/06 7:01 PM


All times are GMT -4. The time now is 11:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts