Default A/C condensate line

I always call-out a A/C condensate line that drain directly into the plumbing system (no air gap) even if a p-trap in the line is provided, over here that p-trap will dry out during the winter, am I calling this right ? would the same apply to furnace condensate line
Reply With Quote
  #2  
Old 8/25/08, 9:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: A/C condensate line

All modern installations in my area will drain to the tailpiece of a sink drain or laundry drain. What makes you think this is improper?

I don't think I've ever seen a furnace that produces condensation. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 8/25/08, 10:26 PM
jcote's Avatar
jcote jcote is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Smooth Rock Falls, On
Posts: 143
Default Re: A/C condensate line

I am in north Ontario A/C are 95% install on force air furnace and if the condensate line is install direct to the sewer pipe it could draw sewer gas .In this area high efficiency furnace have condensation line that goes to a drain of some kind.

Jeannot
Reply With Quote
  #4  
Old 8/25/08, 10:39 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: A/C condensate line

Quote:
Originally Posted by jcote
In this area high efficiency furnace have condensation line that goes to a drain of some kind.Jeannot
We have the same, Jeannot.

Typically the condensate drains to a condensate pump and that pumps it up and into an airgapped drain line.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 8/25/08, 10:40 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: A/C condensate line

Quote:
Originally Posted by jcote
I always call-out a A/C condensate line that drain directly into the plumbing system (no air gap) even if a p-trap in the line is provided, over here that p-trap will dry out during the winter, am I calling this right ? would the same apply to furnace condensate line
\

If the condensate line is plumbed to a sink tail piece I do not call it out as the sink will most likely have water in the trap. Same if it is plumbed to the washer drain. Now if it is plumbed to a trap that you think will go dry, by all means call it out.

If it is plumbed into a waste vent I always call those out.
Reply With Quote
  #6  
Old 8/25/08, 11:34 PM
jcote's Avatar
jcote jcote is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Smooth Rock Falls, On
Posts: 143
Default Re: A/C condensate line

Thanks for your comment, that's what I thought. I wonder why HVAC technicians keep installing them directly in the sewer line
Reply With Quote
  #7  
Old 8/26/08, 12:42 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: A/C condensate line

Quote:
Originally Posted by jcote
Thanks for your comment, that's what I thought. I wonder why HVAC technicians keep installing them directly in the sewer line
Because they have not been properly trained or just don't care just because one works at a HVAC company does not necessarily make one a Tech



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 8/26/08, 12:44 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: A/C condensate line

Quote:
Originally Posted by jpope
All modern installations in my area will drain to the tailpiece of a sink drain or laundry drain. What makes you think this is improper?

I don't think I've ever seen a furnace that produces condensation. . .
Jeff you lost me don't they have 95% furnaces in CA??????



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 8/26/08, 12:51 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: A/C condensate line

Quote:
Originally Posted by bkelly2
\

If the condensate line is plumbed to a sink tail piece I do not call it out as the sink will most likely have water in the trap. Same if it is plumbed to the washer drain. Now if it is plumbed to a trap that you think will go dry, by all means call it out.

If it is plumbed into a waste vent I always call those out.
Bk always is a very broad statement what if the unit is installed within the attic and is a 95% furnace with a trap between the unit and a vent stack what is your call on that set up



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 8/26/08, 1:10 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: A/C condensate line

I call a waste vent, a vent. And a drain a drain. Usually it is an easy call because HVAC guys make lousy plumbers.
Reply With Quote
  #11  
Old 8/26/08, 4:34 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: A/C condensate line

Quote:
Originally Posted by bkelly2
I call a waste vent, a vent. And a drain a drain. Usually it is an easy call because HVAC guys make lousy plumbers.
and plumbers are always worse as HVAC guys, well maybe not in all cases, there is always an exception



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 8/26/08 at 4:41 AM..
Reply With Quote
  #12  
Old 8/26/08, 9:43 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: A/C condensate line

Quote:
Originally Posted by cbottger
Bk always is a very broad statement what if the unit is installed within the attic and is a 95% furnace with a trap between the unit and a vent stack what is your call on that set up
I had to think about this a bit Charley.

If I am not mistaken a 95% efficient furnace the condensate comes from the flue exhaust. Which would mean that if the trap ran dry sewer would not enter the attic or the furnace air stream, I would be ok with it.
Reply With Quote
  #13  
Old 8/26/08, 10:19 PM
jcote's Avatar
jcote jcote is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Smooth Rock Falls, On
Posts: 143
Default Re: A/C condensate line

I have run across another's one today, a/c had a p-trap in the line but was connected directly to sewer line. This summer here in northern Ontario a/c might have run two days that p-trap will spent most of the year dry. Worst the H.R.V. condensate line was connected directly no p-trap.
Reply With Quote
  #14  
Old 8/27/08, 12:08 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: A/C condensate line

Quote:
Originally Posted by bkelly2
I had to think about this a bit Charley.

If I am not mistaken a 95% efficient furnace the condensate comes from the flue exhaust. Which would mean that if the trap ran dry sewer would not enter the attic or the furnace air stream, I would be ok with it.
Me too local AHJ allows it also as long as the trap at the unit is wet



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #15  
Old 8/27/08, 12:15 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: A/C condensate line

Quote:
Originally Posted by jcote
I have run across another's one today, a/c had a p-trap in the line but was connected directly to sewer line. This summer here in northern Ontario a/c might have run two days that p-trap will spent most of the year dry. Worst the H.R.V. condensate line was connected directly no p-trap.
You did good just keep calling them out trap must be wet 365 if not it is wrong no ifs ands or buts



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
condensate drain to sewer line?? wcook2 Inspecting HVAC Systems 5 5/1/08 10:27 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
1 condensate line...... Scott Schultz Inspecting HVAC Systems 2 11/4/07 7:18 AM
Condensate line. jlybolt Inspecting HVAC Systems 10 3/21/07 10:05 PM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 8:59 AM


All times are GMT -4. The time now is 7:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts