Cool A/C Disconnect question

Hello evryone ! I have a quick question regarding an A/C unit at an Inspection today. Sorry I don't have a pic but I will describe it the best I can.

The A/C unit has no disconnect next to it. There is a breaker for the A/C unit in the Service Panel located approx. 30 feet away on the same wall. The panel itself is a Square D all in one(Meter and panel) and is kind of a b**ch to open if you are not familiar with this type. Anyway, back to my question. Does there need to be a disconnect closer to the A/C unit?

I know the IRC and NEC state that the disconnect needs to be in sight of the condensor. I am recommending having a disconnect installed next to the unit.



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #2  
Old 9/20/06, 8:18 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: A/C Disconnect question

Richard, if you are familiar with the IRC and NEC with regards to this situation, how did you come up with your recommendation?



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #3  
Old 9/20/06, 8:28 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Elizabeth, CO
Posts: 215
Default Re: A/C Disconnect question

Hi Brian. My recommendation is based on the fact that the disconnect isn't TRUELY in sight of the condenser. Even though I know and the Client knows that there is a breaker in the Service panel (which is located on the same wall and in sight of the condenser) dedicated to the A/C.

Would you have done anything differently? I am always trying to learn something from you guys out there!

Rick



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #4  
Old 9/20/06, 8:33 PM
tgodfrey tgodfrey is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Dunsford, ON
Posts: 8
Default Re: A/C Disconnect question

It is my belief that the disconnect should be in sight of the unit and within 5' I'm not 100% on this. Anyone else?
Reply With Quote
  #5  
Old 9/20/06, 8:44 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: A/C Disconnect question

I think you did the right thing Richard a disconnect needs to be insight for the condenser. I initially did not read your question correctly



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #6  
Old 9/20/06, 8:57 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Elizabeth, CO
Posts: 215
Default Re: A/C Disconnect question

No prob Brian. Thanks for the input!



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #7  
Old 9/20/06, 8:58 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Elizabeth, CO
Posts: 215
Default Re: A/C Disconnect question

Thanks Thaine!



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #8  
Old 9/20/06, 9:10 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,095
Default Re: A/C Disconnect question

A breaker in a service panel 30 feet away would be just fine by me and I would not even remotely think to write that up as deficient in any way. Anything more would really be nit-picking I think. Wouldn't you say the attached example is OK?
Attachment 5664

Last edited by mboyett; 4/9/09 at 10:38 PM..
Reply With Quote
  #9  
Old 9/20/06, 9:25 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: A/C Disconnect question

Hey Guys,

In this application if the outside unit is on the same wall as a exterior panel and " Within Sight" then it should be fine.

Keep in mind that their is a limit to within sight....it is 50' and no more.....check out how the NEC defines " In Sight From" to up to 50'.....so keep that in mind.....their is STILL a limit to "within sight"



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 9/20/06, 9:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,028
Default Re: A/C Disconnect question

I'm with Michael and Paul here. A breaker in a panel is a disconnect. If it's within site, there's no need to add another.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 9/21/06, 12:13 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: A/C Disconnect question

Quote:
Originally Posted by mboyett
A breaker in a service panel 30 feet away would be just fine by me and I would not even remotely think to write that up as deficient in any way. Anything more would really be nit-picking I think. Wouldn't you say the attached example is OK?
Attachment 5664
That is a service disconnect is it not? So yes that is ok by me.


What does the IRC say about condensers? I do not think the breaker in the main panel counts for condensers does it? I do not think even a lockable breaker counts. Hey, I have already miss read this post once, so what do I know.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #12  
Old 9/21/06, 12:32 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,095
Default Re: A/C Disconnect question

One, I do believe a breaker in a main panel within sight of the condenser is sufficient. I can't find a reference to that in the IRC right now but I'll keep looking. Two, I think the original question was asking if it was OK that the breaker that was admittedly within 30 feet of the condenser was behind a panel cover and therefore 'not within sight'...that's where I was going with my 'nit-picking' remark.
Reply With Quote
  #13  
Old 9/21/06, 12:41 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: A/C Disconnect question

I read it that way too at first Michael. But I think the IRC frowns on a breaker in the main panel being the service disconnect. But, I have been wrong before.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #14  
Old 9/21/06, 1:07 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: A/C Disconnect question

And I am wrong again, 03 IRC T4001.5 covers it. As long as it is in sight.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #15  
Old 9/21/06, 1:12 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,028
Default Re: A/C Disconnect question

Quote:
Originally Posted by bkelly2
And I am wrong again, 03 IRC T4001.5 covers it. As long as it is in sight.
Yep. A disconnect can be a breaker, switch, pull-out, etc., etc., and it doesn't matter if it's in a service panel, remote panel, switch or fuse box or whatever. It just needs to be accessible and within sight.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Service disconnect question wsiegel Electrical 3 8/28/07 10:59 AM
Well pump disconnect sfalvey Plumbing 0 11/17/06 1:23 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical 8 8/15/06 1:32 PM


All times are GMT -4. The time now is 10:15 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts