  #1  
Old 9/8/08, 11:33 AM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 793
Andrew Cox is well trusted Andrew Cox is well trusted Andrew Cox is well trusted
Default A/C power supply

I have always assumed there is supposed to be a disconnect within reach of the outdoor unit, as a safety issue. On this house I inspected yesterday, there isn't one, it is hard-wired into the home, and the only breaker is the one inside the panel.
This is the first time I've come across this. Isn't there a requirement for this to have a disconnect close-by? And as this buyer will be financing with FHA, would this be something the FHA inspector would call out? Thanks.
Attached Images
File Type: jpg heatpump.jpg (68.2 KB, 38 views)



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #2  
Old 9/8/08, 11:54 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,994
Jeffrey R. Pope .
Default Re: A/C power supply

The panel-breaker can be used as the disconnect, as long as it is within sight of the appliance.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #3  
Old 9/8/08, 12:03 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 793
Andrew Cox is well trusted Andrew Cox is well trusted Andrew Cox is well trusted
Default Re: A/C power supply

Jeff, thanks. However, there is no breaker for it within sight. This is outside, and the panel breaker is inside the garage.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #4  
Old 9/8/08, 12:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,994
Jeffrey R. Pope .
Default Re: A/C power supply

Then it needs to be corrected. There must be a disconnect within sight of the appliance.

It's very unlikely that the FHA inspector will recognize this issue, but you should report it as a defect.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #5  
Old 9/8/08, 12:45 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 793
Andrew Cox is well trusted Andrew Cox is well trusted Andrew Cox is well trusted
Default Re: A/C power supply

Thanks Jeff.
I've already written it into my report and showed it to the client during the inspection. It's a bank-owned property, so she'll pay for it anyway, but I'll recommend it be repaired immediately.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #6  
Old 9/8/08, 1:33 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: A/C power supply

You assumed right, but you should never assume.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #7  
Old 9/8/08, 1:36 PM
John Allingham John Allingham is online now
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 288
John Allingham is generally well trusted John Allingham is generally well trusted
Default Re: A/C power supply

Hi Andrew
I quite often see older A/C units with no disconnect in sight . It wasn't in the code back then.
If this is an older installation you may want to check that out.
Reply With Quote
  #8  
Old 9/8/08, 1:48 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: A/C power supply

If you look at the picture of the building and the HVAC, it is quite obvious that an HVAC disconnect was required at the time of construction.

It really doesn't matter if it was building code at any time because it's not our job to interpret or enforce these building codes.

We are here to simply report there is no disconnect at the outside unit and it can kill your HVAC technician if he can't turn the power off!



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #9  
Old 9/8/08, 2:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,994
Jeffrey R. Pope .
Default Re: A/C power supply

Quote:
Originally Posted by jallingham
Hi Andrew
I quite often see older A/C units with no disconnect in sight . It wasn't in the code back then.
If this is an older installation you may want to check that out.
This may be true for Canada - I don't know Canadian Codes.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #10  
Old 9/8/08, 2:48 PM
Charles L. Harper Charles L. Harper is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: McDonough, GA
Posts: 155
Charles L. Harper is generally well trusted
Default Re: A/C power supply

Hey Jeff,
I saw your response concerning an ac disconnect. I had the same issue this morning. AC units were hardwired into main disconnect on outside of house. SO if you have to disconnect the ac unit for any reason than you will also shut off ALL power to the home. This doesn't seem right.



www.HomeInspectionGA.com
McDonough, GA.
770-954-0204
Reply With Quote
  #11  
Old 9/8/08, 3:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,994
Jeffrey R. Pope .
Default Re: A/C power supply

Well, the "required disconnect" is effectively in place, however, there are rarely any instances where the direct tap would be compliant, regardless of the equipment it serves.

It certainly isn't the most preferred method, however, if wired properly and not double-tapped, it may well be compliant.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #12  
Old 9/8/08, 3:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,994
Jeffrey R. Pope .
Default Re: A/C power supply

Actually, I think I may have given a bit of misinformation.

In your case, the service disconnect for the house must not exceed the maximum circuit rating for the condenser unit(s). So it's very unlikely that what you had was compliant.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #13  
Old 9/8/08, 8:46 PM
Charles L. Harper Charles L. Harper is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: McDonough, GA
Posts: 155
Charles L. Harper is generally well trusted
Default Re: A/C power supply

Jeff, you are 100% correct. Why I didn't think of that I don't know. This particular builder has done all of the houses in this sub division like this.



www.HomeInspectionGA.com
McDonough, GA.
770-954-0204
Reply With Quote
  #14  
Old 9/8/08, 8:56 PM
Terry B. Clayton Terry B. Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 80
Terry B. Clayton is generally well trusted
Default Re: A/C power supply

The only way I know this would pass would be if the interior disconnecting devise is capable of being locked out by the servicing tech. Hope they never have to replace the sealtite
Reply With Quote
  #15  
Old 9/8/08, 9:01 PM
Brian K. Doles's Avatar
Brian K. Doles Brian K. Doles is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 2,688
Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute
Default Re: A/C power supply

Quote:
Originally Posted by dandersen
If you look at the picture of the building and the HVAC, it is quite obvious that an HVAC disconnect was required at the time of construction.
To help educate me, what makes this so obvious in the picture?




Brian K Doles
Atlanta, GA - Providing Infrared Thermal Home Inspections
Home Inspections
Commercial Inspections
Infrared Thermal Imaging

Colby Home Services
All of metro Atlanta including Conyers, Covington, Stone Mountain, Midtown, Buckhead, Perimeter
Customer Testimonials


Home Inspector Pro Software - A Professionals choice in software.

Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Power Supply to Subpanel Mick D. Jones Electrical 6 8/27/08 5:55 PM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical 72 3/12/08 12:19 AM
Selected Electrical Incidents and Occurrences - First Quarter pabernathy Electrical 0 12/2/07 2:43 PM
supply in slab or walls? jeubank Plumbing 1 7/8/06 11:36 AM
Emergency Lighting (commercial) mcyr Electrical 24 6/10/06 11:06 AM


All times are GMT -4. The time now is 8:03 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members