Default Re: A/C power supply

Quote:
Originally Posted by acox
I have always assumed there is supposed to be a disconnect within reach of the outdoor unit, as a safety issue. On this house I inspected yesterday, there isn't one, it is hard-wired into the home, and the only breaker is the one inside the panel.
This is the first time I've come across this. Isn't there a requirement for this to have a disconnect close-by? And as this buyer will be financing with FHA, would this be something the FHA inspector would call out? Thanks.
Maybe I just can't see it, but where's the copper on this?
Reply With Quote
  #17  
Old 9/8/08, 9:31 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: A/C power supply

Quote:
Originally Posted by bdoles2
To help educate me, what makes this so obvious in the picture?
It's a relatively modern appliance. Probably from the 90's, I would guess. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #18  
Old 9/8/08, 9:43 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C power supply

Quote:
Originally Posted by jpope
It's a relatively modern appliance. Probably from the 90's, I would guess. . .
Ahh, yes!
Reply With Quote
  #19  
Old 9/8/08, 11:51 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: A/C power supply

This house was built in late 2006 - barely 2 years old. Initially, I just expected to see the d/c inside the main disconnect, which is within 10 feet, but it wasn't there. So, the only way to break the circuit for this unit is to walk inside the garage and flip the breaker there.
Code or not, I called it a safety issue. Even so, as I read it, IRC requires the disconnect be installed "within sight from unit". My client intends to get it fixed. The main question is if it has to be done before the FHA inspector is scheduled. Would he call this out as an issue affecting FHA loan approval? This is a bank-owned property and she has only a few days to get it done.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #20  
Old 9/9/08, 12:04 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: A/C power supply

It has been a code issue and a safety issue since mobey dick was a minnow I just recently called out two one with metal conduit out of a crawl space hard piped to the unit no disconnect within view and one with a disconnect that did not disconnect power to the unit it was faulty. I was having burner roll out problems on a Gas Pac unit and reached up to turn the disconnect off and whala it just kept on running belching flames everywhere </IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #21  
Old 9/9/08, 9:25 AM
dmcauley's Avatar
dmcauley dmcauley is offline
Active Poster
 
Join Date: Jan 2006
Location: Hoffman Estates, IL
Posts: 854
Please Note: dmcauley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C power supply

Maybe I'm not seeing something here. Why would your client have to have it repaired or brought to current standards? She does not own the property yet. Shouldn't the present owner pay? I know a bank owns it, but putting the responsibility of repair on an individual who does not own the proeprty is a new one to me.
Reply With Quote
  #22  
Old 9/9/08, 10:57 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: A/C power supply

Many FHA lenders are requiring certain items to be addressed before they will fund on a property. Generally, their "inspection" is usually done by their appraiser, who is required to indicate obvious-safety related issues or major defects such as a deteriorated roof.

Often they will request a copy of the actual inspection report, and will generate a list of items that must be addressed prior to funding.

I've done many, many inspections for FHA buyers. Trust me when I tell you, the FHA "inspector" is very unlikely to even notice the missing disconnect.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #23  
Old 9/9/08, 4:15 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: A/C power supply

Quote:
Originally Posted by jpope
Many FHA lenders are requiring certain items to be addressed before they will fund on a property. Generally, their "inspection" is usually done by their appraiser, who is required to indicate obvious-safety related issues or major defects such as a deteriorated roof.

Often they will request a copy of the actual inspection report, and will generate a list of items that must be addressed prior to funding.

I've done many, many inspections for FHA buyers. Trust me when I tell you, the FHA "inspector" is very unlikely to even notice the missing disconnect.
Ditto what Jeff stated and I might add a seller does not have to agree to sell FHA there is a box on the listing papers that the seller must check at the time of listing as to how they will except payment FHA, VA, conventional. I also do a lot of inspections for buyers that have purchased the property in a as in condition because the seller lower the price knowing there were problems



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #24  
Old 9/9/08, 4:22 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: A/C power supply

Quote:
Originally Posted by dmcauley
Maybe I'm not seeing something here. Why would your client have to have it repaired or brought to current standards? She does not own the property yet. Shouldn't the present owner pay? I know a bank owns it, but putting the responsibility of repair on an individual who does not own the proeprty is a new one to me.
Wrote in the contract selling as is very common for seller to do this.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #25  
Old 9/11/08, 8:36 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: A/C power supply

All the conversation/speculation won't change the fact that NEC and the Equip. Mfg. either requires or recommends line of sight/access by the service provider to a disconnect (fused or non-fused type).
Charles, I can't believe McDonough (Henry Co. ??) would let the Electrical Contr. for that Bldg. Contr. get away with this type of installation. I thought we were better than that.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Power Supply to Subpanel Mick D. Jones Electrical Inspections 6 8/27/08 4:55 PM
Selected Electrical Incidents and Occurrences - First Quarter pabernathy Electrical Inspections 0 12/2/07 1:43 PM
supply in slab or walls? jeubank Plumbing Inspections 1 7/8/06 10:36 AM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM


All times are GMT -4. The time now is 11:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts