Default Can you explain this to a client

If you had a client ask you questions about this duct arrangement could you answer or dance. A rather strange system here 3 zone dampers and one zone stat with a duct between the supply and return as illustrated in the pics the supply side is to the top of the pic and the return is toward the bottom with the cross over in between
Attached Thumbnails
can-you-explain-client-sdfh-1-medium-.jpg (Medium).jpg
Views:	90
Size:	69.9 KB
ID:	27002   can-you-explain-client-sdfh-2-medium-.jpg (Medium).jpg
Views:	83
Size:	80.1 KB
ID:	27003   can-you-explain-client-sdfh-medium-.jpg.jpg
Views:	88
Size:	82.4 KB
ID:	27004  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #2  
Old 2/20/09, 7:39 PM
Charles Jones Charles Jones is offline
New User
 
Join Date: Jul 2007
Location: new jersey
Posts: 24
Please Note: Charles Jones is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can you explain this to a client

from what I see is coming off the back of the supply plenum is 1 zone,comeing off the front of the plenum is the 2nd zone. and comeing off the top of the supply plenum going into the return is a bypass with a barametric damper installed.the bypass is used when one of the zones is to small to handle the full cfm required for the a/c to function properly.(example A 2 ton system = 800 cfm) zone 1 requires 400 cfm and zone 2 need 400 cfm. when both zones are calling for cooling you have a perfect and quite system, But what happens when any 1 zone shuts off ? The remaining zone still operating is now TRYING to push 800 cfm in a 400 cfm duct system.very noisey and will distroy the system early.This is why a barametric bypass damper is installed. the extra 400 cfm will be put back into the return system to release preasur and keep the volocity down.
Reply With Quote
  #3  
Old 2/20/09, 7:50 PM
Harry E. McClard's Avatar
Harry E. McClard Harry E. McClard is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Raymond, NH
Posts: 103
Default Re: Can you explain this to a client

Some sort of flow balancer? Hard to comprehend with available info.



Harry "Bud" McClard
Serving All of New Hampshire
Reply With Quote
  #4  
Old 2/20/09, 9:31 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Can you explain this to a client

I don't let my clients accompany me in attics or crawl spaces for this reason: I can't dance.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 2/21/09, 12:51 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Can you explain this to a client

Quote:
Originally Posted by Charles Jones View Post
from what I see is coming off the back of the supply plenum is 1 zone,comeing off the front of the plenum is the 2nd zone. and comeing off the top of the supply plenum going into the return is a bypass with a barametric damper installed.the bypass is used when one of the zones is to small to handle the full cfm required for the a/c to function properly.(example A 2 ton system = 800 cfm) zone 1 requires 400 cfm and zone 2 need 400 cfm. when both zones are calling for cooling you have a perfect and quite system, But what happens when any 1 zone shuts off ? The remaining zone still operating is now TRYING to push 800 cfm in a 400 cfm duct system.very noisey and will distroy the system early.This is why a barametric bypass damper is installed. the extra 400 cfm will be put back into the return system to release preasur and keep the volocity down.
Well Mr. Charles Jones you described very well for what you could see except all 3 zones where gathered at one end of the plenum nice job



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 2/21/09, 2:55 PM
Charles Jones Charles Jones is offline
New User
 
Join Date: Jul 2007
Location: new jersey
Posts: 24
Please Note: Charles Jones is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can you explain this to a client

I would say that it has the 2 control dampers installed for future zoneing since you say you have only 1 t-stat controling that furnace.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inspection Agreement Review. bsavage General Inspection Discussion 21 5/11/08 9:20 PM
Clueless Client? jpassailaigue Plumbing Inspections 5 8/2/07 3:35 PM
ILLINOIS Section 1410.200 Standards of Practice jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 11 3/9/06 11:22 AM


All times are GMT -4. The time now is 11:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts