Default Can you see it

This is a 4 ton A-coil set up non adjustable expansion valve with external equalizer line IMO there is a engineering flaw in the design set up can you see it and would you have the intestinal fortitude to call it if you would have seen this.

BTW did you know the color of the sticker on the expansion valve denotes the type of freon the valve is designed for green=R-22

The odds of it ever happening are almost non-existing but if the expansion valve was visible and had a yellow sticker and the name plate data on the condensing unit stated R-22 would you have noticed this.
Attached Thumbnails
can-you-see-junk-four-001.jpg   can-you-see-junk-four-003.jpg   can-you-see-junk-four-004.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 8/19/08 at 11:28 AM..
Reply With Quote
  #2  
Old 8/20/08, 3:06 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Can you see it

Quote:
Originally Posted by cbottger
This is a 4 ton A-coil set up non adjustable expansion valve with external equalizer line IMO there is a engineering flaw in the design set up can you see it and would you have the intestinal fortitude to call it if you would have seen this.

BTW did you know the color of the sticker on the expansion valve denotes the type of freon the valve is designed for green=R-22

The odds of it ever happening are almost non-existing but if the expansion valve was visible and had a yellow sticker and the name plate data on the condensing unit stated R-22 would you have noticed this.
Come on guys this is basic refrigeration you are disappointing me, any HI worth his salt should be able to spot this problem.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 8/20/08, 5:19 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Can you see it

Quote:
Originally Posted by cbottger
Come on guys this is basic refrigeration you are disappointing me, any HI worth his salt should be able to spot this problem.
Well, let me be the first to say that I don't have the foggiest idea and I don't work for salt so we're good to go deferring...but always willing to learn something.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 8/20/08, 5:20 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Can you see it

The only thing I see is that the dynamic barometric overload compensator is positioned in such a way as to likely render it ineffective during a polyphase rendering occurance. It would certainly lose efficiency with that condition and I probably would have noted it in the report. I hope this doesn't disappoint you.
Reply With Quote
  #5  
Old 8/20/08, 6:10 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Can you see it

Quote:
Originally Posted by mboyett
The only thing I see is that the dynamic barometric overload compensator is positioned in such a way as to likely render it ineffective during a polyphase rendering occurance. It would certainly lose efficiency with that condition and I probably would have noted it in the report. I hope this doesn't disappoint you.
I saw that exact same thing, too. However, I thought that was too obvious for what he was looking for.

Just a guess... would it have something to do with unequal pressure. Possibly a lower amount of r-22 going into the second set of coils, based on the 'parallel' set up of the line.

Jeff
Reply With Quote
  #6  
Old 8/20/08, 8:12 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Can you see it

Quote:
Originally Posted by mboyett
The only thing I see is that the dynamic barometric overload compensator is positioned in such a way as to likely render it ineffective during a polyphase rendering occurance. It would certainly lose efficiency with that condition and I probably would have noted it in the report. I hope this doesn't disappoint you.
Hi Mike that was really good LOL could not have stated it that well myself. I think it is just great that someone will just say I don't know.
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 8/20/08, 8:18 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Can you see it

Quote:
Originally Posted by lkage
Well, let me be the first to say that I don't have the foggiest idea and I don't work for salt so we're good to go deferring...but always willing to learn something.
Hi Larry I don't have any salt either. I am going somewhere with this just hang in there. This A-coil was out of my old furnace and I had to modified it to make it work back in 1991. For the Pic I un installed my modification what you are seeing is just the way it came from the factory.
</IMG>

I thought my second post would raise an eyebrow



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 8/20/08, 8:31 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Can you see it

Quote:
Originally Posted by cbottger
I am going somewhere with this just hang in there.
10-4 chief, look forward to it.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 8/20/08, 8:32 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Can you see it

Excessive corrosion, call out a HVAC guy to certify remaining life.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #10  
Old 8/20/08, 8:58 PM
dgagneur's Avatar
dgagneur dgagneur is offline
Active Poster
 
Join Date: Dec 2005
Location: Alpena, MI
Posts: 444
Please Note: dgagneur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can you see it

Is that blue and green thingy the flux-capacitor???
Reply With Quote
  #11  
Old 8/20/08, 9:09 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Can you see it

Ok guys I am going to finger the problem tell me why it would be wrong
Attached Thumbnails
can-you-see-junk-four-002.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 8/20/08, 10:44 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can you see it

Quote:
Originally Posted by cbottger
Ok guys I am going to finger the problem tell me why it would be wrong
So how/why did it get there Charley?
I's been operating like that?
Reply With Quote
  #13  
Old 8/21/08, 12:39 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Can you see it

Sorry I'm late to class Charlie!
Can I play?




"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #14  
Old 8/21/08, 1:01 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Can you see it

Quote:
Originally Posted by dandersen
Sorry I'm late to class Charlie!
Can I play?
Not yet Dave, let's see how long it takes for him to break and tell on himself



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #15  
Old 8/21/08, 7:27 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Can you see it

Oh, okay...............



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts