Can anyone give some verbiage on this issue.
Rheem 2005 sealed combustion cat 4 furnace installed in an attic room. The combustion intake air vent was open to the attic, not taken outside. Buyer talked to the village code people and theu said it was OK. I was always informed that Cat 4 sealed furnaces should take their air from outside. The attic room had 2 vents to the attic. Comments to support my arguement? Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#2
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#3
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
If a CAT IV furnace has *both* a combustion vent pipe *and* a combustion air intake pipe, every installation instructions I've seen require that the termination of *both* pipes be in the same atmospheric pressure zone. If the combustion air intake pipe (connected directly to the furnace) terminates in the attic, and the combustion vent pipe is venting to the exterior, they are not. (Note that this is NOT the same as the same furnace drawing combustion air from a utility closet drawing combustion air from the attic.)
Last edited by mthomas2; 5/3/07 at 9:10 PM.. |
|
#4
|
|||
|
|||
|
There are some cat 4 furnace mfgr that allow you to pull combustion air from the surrounding space as long as it is not a confined space. York is one i can think of.Matt
|
|
#5
|
|||
|
|||
|
Read installation instructions,they should be at or near furnace area .Matt
|
|
#6
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
For an example, see item 2 at the top of page 11 (document page number, shows up as page 17 in my Adobe reader) here:
http://www.thermopride.com/manuals/mg1010.pdf An attic is not in the same "atmospheric pressure zone" as an exterior location as wind forces will often be produce pressure differences between the inside and outside of the attic. Again, note that this applies only to the situation where the furnace is drawing combustion air via direct connection to an intake pipe, not to an arrangement in which the furnace is drawing its combustion air from a utility closet with a properly sized connections to a vented attic. Last edited by mthomas2; 5/3/07 at 10:22 PM.. |
|
#7
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#8
|
||||
|
||||
|
Thanks, Mike.
Client is lawyer and the sellers are very defensive. Never allow the local AHJ to determine what is right. They are (usually) less informed than the local HVAC guys. No CE requirements. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#9
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
What do the furnace's installation instructions say? Though village codes say it may be alright if the installation instructions require a combustion air pipe outside of the structure then one will have to be installed.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Furnace Problem Comments Welcome | rfrost | Inspecting HVAC Systems | 28 | 10/21/07 6:26 PM |
| To hot too test the furnace | rcooke | Canadian Inspectors | 1 | 8/19/07 10:44 PM |
| Sweating decision:Settle for lower SEER to use existing furnace? | Fel Randolph | Inspecting HVAC Systems | 2 | 6/6/07 2:56 PM |
| Armstrong Ultra 80 Oil Forced air furnace | Stephen Frazer | Inspecting HVAC Systems | 19 | 4/9/07 8:00 PM |
| Condemned Furnaces Spark Safety Issues | Gary Reecher | Inspecting HVAC Systems | 7 | 3/8/07 8:17 PM |