Can anyone give some verbiage on this issue.

Rheem 2005 sealed combustion cat 4 furnace installed in an attic room. The combustion intake air vent was open to the attic, not taken outside.

Buyer talked to the village code people and theu said it was OK.

I was always informed that Cat 4 sealed furnaces should take their air from outside.

The attic room had 2 vents to the attic.

Comments to support my arguement?



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #2  
Old 5/3/07, 8:03 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Cat 4 furnace verbiage

Quote:
Originally Posted by wdecker
Can anyone give some verbiage on this issue.

Rheem 2005 sealed combustion cat 4 furnace installed in an attic room. The combustion intake air vent was open to the attic, not taken outside.

Buyer talked to the village code people and theu said it was OK.

I was always informed that Cat 4 sealed furnaces should take their air from outside.

The attic room had 2 vents to the attic.

Comments to support my arguement?
Cannot support you Buddy they are not required exterior to the home in my area just inspected one this week made its turn right in the middle of the attic space. Would be a different story if the attic was sealed but with a vented attic what is the difference. We have been taking combustion air from attics on other furnaces for a hundred years why not this one.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 5/3/07, 8:44 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cat 4 furnace verbiage

If a CAT IV furnace has *both* a combustion vent pipe *and* a combustion air intake pipe, every installation instructions I've seen require that the termination of *both* pipes be in the same atmospheric pressure zone. If the combustion air intake pipe (connected directly to the furnace) terminates in the attic, and the combustion vent pipe is venting to the exterior, they are not. (Note that this is NOT the same as the same furnace drawing combustion air from a utility closet drawing combustion air from the attic.)

Last edited by mthomas2; 5/3/07 at 9:10 PM..
Reply With Quote
  #4  
Old 5/3/07, 9:04 PM
Matt Berman, CMI Matt Berman, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 107
Wink Re: Cat 4 furnace verbiage

There are some cat 4 furnace mfgr that allow you to pull combustion air from the surrounding space as long as it is not a confined space. York is one i can think of.Matt
Reply With Quote
  #5  
Old 5/3/07, 9:08 PM
Matt Berman, CMI Matt Berman, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 107
Lightbulb Re: Cat 4 furnace verbiage

Read installation instructions,they should be at or near furnace area .Matt
Reply With Quote
  #6  
Old 5/3/07, 10:11 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cat 4 furnace verbiage

For an example, see item 2 at the top of page 11 (document page number, shows up as page 17 in my Adobe reader) here:

http://www.thermopride.com/manuals/mg1010.pdf

An attic is not in the same "atmospheric pressure zone" as an exterior location as wind forces will often be produce pressure differences between the inside and outside of the attic. Again, note that this applies only to the situation where the furnace is drawing combustion air via direct connection to an intake pipe, not to an arrangement in which the furnace is drawing its combustion air from a utility closet with a properly sized connections to a vented attic.

Last edited by mthomas2; 5/3/07 at 10:22 PM..
Reply With Quote
  #7  
Old 5/4/07, 12:03 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Cat 4 furnace verbiage

Quote:
Originally Posted by mberman
There are some cat 4 furnace mfgr that allow you to pull combustion air from the surrounding space as long as it is not a confined space. York is one i can think of.Matt
So Is American Standard



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 5/4/07, 10:26 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Cat 4 furnace verbiage

Thanks, Mike.

Client is lawyer and the sellers are very defensive.

Never allow the local AHJ to determine what is right. They are (usually) less informed than the local HVAC guys. No CE requirements.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 5/6/07, 10:13 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cat 4 furnace verbiage

What do the furnace's installation instructions say? Though village codes say it may be alright if the installation instructions require a combustion air pipe outside of the structure then one will have to be installed.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace Problem Comments Welcome rfrost Inspecting HVAC Systems 28 10/21/07 6:26 PM
To hot too test the furnace rcooke Canadian Inspectors 1 8/19/07 10:44 PM
Sweating decision:Settle for lower SEER to use existing furnace? Fel Randolph Inspecting HVAC Systems 2 6/6/07 2:56 PM
Armstrong Ultra 80 Oil Forced air furnace Stephen Frazer Inspecting HVAC Systems 19 4/9/07 8:00 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM


All times are GMT -4. The time now is 6:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts