I am looking for possible causes of the following. It is a central air unit with exterior condensor unit and indoor A-coil, above the furnace. It is a 18 year old unit, and a 10 year forced air gas furnace.

The central air temperature thermostat is set to 74 degrees F. The compressor operates adequately, at that temp, however, the concern is that after running for several hours during the day - a small amount of heat discharges from the "supply" floor registers after the cycle has finished when the fan is on. When the air cycles back on the air cools again.

Comments please.



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.
"Those who can do. Those who CARE, teach" or
“Teaching is the highest form of understanding.” Aristotle
Reply With Quote
  #2  
Old 6/11/07, 11:21 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,928
Default Re: Central air problem

Quote:
Originally Posted by clawrenson
I am looking for possible causes of the following. It is a central air unit with exterior condensor unit and indoor A-coil, above the furnace. It is a 18 year old unit, and a 10 year forced air gas furnace.

The central air temperature thermostat is set to 74 degrees F. The compressor operates adequately, at that temp, however, the concern is that after running for several hours during the day - a small amount of heat discharges from the "supply" floor registers after the cycle has finished when the fan is on. When the air cycles back on the air cools again.

Comments please.
Not an AC expert but has this happened other years or do you know .
Could it be going into a defrost cycle to make sure the coils are not covered in Ice.



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #3  
Old 6/12/07, 1:47 AM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,824
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Central air problem

It's a bit out of the SOP, but check the thermostat wiring to make sure that it is wired properly and there are no wires contacting where they shouldn't be. Just had to fix someone's (friend from work - not a client) system not to long ago because the previous home owner installed a digital thermostat and crushed the wires in the housing causing the heat control wires to contact some of the AC wire contacts. Everytime the AC would turn on, it would also turn on the heater. Both of her systems pretty much ran constantly.
Reply With Quote
  #4  
Old 6/12/07, 2:28 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Central air problem

How could heat come through unless the burners are fired up?
Anyone?
Reply With Quote
  #5  
Old 6/12/07, 9:11 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,874
Default Re: Central air problem

Quote:
Originally Posted by clawrenson
I am looking for possible causes of the following. It is a central air unit with exterior condensor unit and indoor A-coil, above the furnace. It is a 18 year old unit, and a 10 year forced air gas furnace.

The central air temperature thermostat is set to 74 degrees F. The compressor operates adequately, at that temp, however, the concern is that after running for several hours during the day - a small amount of heat discharges from the "supply" floor registers after the cycle has finished when the fan is on. When the air cycles back on the air cools again.

Comments please.
You are describing a downflow furnace with the registers in the floor but say the A-coil is above the furnace telling me that the return air is being drawn thru the A-coil. This does not compute with me as the standard installation would be on a down flow system the A-coil would be below the furnace with the fan discharging thru the A-coil.

On a system of that age I would think the fan would cycle off when ever the outside unit cycled off not continuing to run. It sounds to me you have an improperly wired control system and a improper location of the A-coil.

I would also check all of the return air duct for loss of insulation; sounds also as if you are picking up excessive heat from the return side of the system.

Very hard to trouble shoot a system from this monitor.

Roy does not do home inspections from pictures but I can trouble shoot from pics do you have any



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 6/12/07, 9:16 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Central air problem

I have had a lot of units run in heat and cooling at the same time.

In this case Robert is correct. Did you check the furnace to see if it was running?

If it is, it is the T-Stat or control wiring.

By the way; furnaces do not have a defrost cycle unless they are a duel-fuel (at this age it is unlikely).

Newer furnaces use an electronic control board which is often the cause of a run-a-way furnace.
Reply With Quote
  #7  
Old 6/17/07, 12:19 AM
lfoster's Avatar
lfoster lfoster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Central air problem

Would it be the end of the cycle and the unit is clearing the conditioned air from the ducts? Like the heating does?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is MAC a problem bemelander General Inspection Discussion 2 9/6/07 12:34 PM
Plumbing problem at home. mnahrgang Plumbing Inspections 25 7/10/07 6:32 PM
Oil Heat Association of Central PA joins NACHI. gromicko Miscellaneous Discussion for Inspectors 0 6/13/07 5:25 PM
Central Virginia Chapter Web Site Live pabernathy General Inspection Discussion 0 6/14/06 10:40 AM


All times are GMT -4. The time now is 10:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts