Default Checking AC with temp differentials.

....



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.

Last edited by mnahrgang; 6/10/10 at 11:40 PM..
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/10/10, 7:30 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Checking AC with temp differentials.

I do it the same way . Write the split example 57/72 and give my recomendations example outside coil should be leveled and move on .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 6/10/10, 7:39 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,515
Default Re: Checking AC with temp differentials.

I recently inspected a home for a HVAC company owner. I was taking splits at registers and returns. He laughed and showed me the laser thermometer he had brought in his back pocket. He said he checks them the same way. I used to use thermometers at the air handler but found the closest register and return got right at the same results.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #4  
Old 6/10/10, 7:56 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Checking AC with temp differentials.

The deal with today's was that it was a sellers inspection. He just had the AC and the furnace installed last week prior to my inspection. I got a temp differential of 12 degrees from one bedroom, and 9 from another (return in hall). The AC guy who did the install claimed that I did it in the wrong place, and that I should have done it over the coils. His diff was 18 degrees...

From what you guys are telling me, something else was up, and he's blowing smoke to cover his but.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #5  
Old 6/10/10, 10:37 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 461
Default Re: Checking AC with temp differentials.

The only thing that counts is the coil temp. The supply air from the register will vary depending on the length of the duct as well as many other factors (like insulation). Don't worry so much about temp splits between the supply and return because they vary. If you just start the unit the return temp will be much higher than it is after the unit has run for an hour. You want a 40 degree evap coil or something close to that after the unit has been operating for some time.
Reply With Quote
  #6  
Old 6/10/10, 10:39 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Checking AC with temp differentials.

Quote:
Originally Posted by gheller View Post
The only thing that counts is the coil temp. The supply air from the register will vary depending on the length of the duct as well as many other factors (like insulation). Don't worry so much about temp splits between the supply and return because they vary. If you just start the unit the return temp will be much higher than it is after the unit has run for an hour. You want a 40 degree evap coil or something close to that after the unit has been operating for some time.
And where exactly would you take that 40 degree temperature at?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #7  
Old 6/10/10, 10:47 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Checking AC with temp differentials.

The 40° temperature that he is talking about is saturation temperature of the refrigerant within the coil. You need an oil filled well to take this temperature at the outlet of the evaporator coil or you can convert pressure to temperature (i.e. 70 psi G; R. 22 refrigerant is equivalent to about 40 degrees saturation).

None of this you're going to do because you need a EPA certification to touch the refrigerant.

As for your other question, your temperature differential is supposed to be taken across the coil.

The reason that your measurement is not accurate is because you are gaining heat from the air duct system which passes through unconditioned spaces and the air gets warmer as it travels down the pipe due to ambient temperatures as well as friction.

And as always; taking these measurements with the dry bulb thermometer (or a laser thermometer which is even less accurate) provides you with nothing unless you know what the baseline operating conditions of that designed equipment was one it was initially installed.

You need a hygrometer and a psychrometric chart to even come close.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #8  
Old 6/10/10, 10:51 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Checking AC with temp differentials.

An air air-conditioners primary work is done on latent heat (cannot be measured with a dry bulb thermometer).

The dry bulb temperature will not fall until the proper amount of latent heat is removed first before this can happen.

So you have absolutely no idea how many BTUs per hour the equipment is removing because you cannot measure latent temperature with a dry bulb thermometer.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #9  
Old 6/10/10, 11:32 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Checking AC with temp differentials.

Quote:
Originally Posted by dandersen View Post
An air air-conditioners primary work is done on latent heat (cannot be measured with a dry bulb thermometer).

The dry bulb temperature will not fall until the proper amount of latent heat is removed first before this can happen.

So you have absolutely no idea how many BTUs per hour the equipment is removing because you cannot measure latent temperature with a dry bulb thermometer.
So how does a home inspector test the ac?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #10  
Old 6/11/10, 12:24 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Checking AC with temp differentials.

Quote:
Originally Posted by mnahrgang View Post
So how does a home inspector test the ac?
Turn on the heating system and let it run until everyone complains about how hot it is.

Then turn on the cooling system and let it run until everyone complains about how cold it is.

Obviously the system works, so when the new owner calls in six months, remind them about their complaints, tell them to call an HVAC tech, and move on.

I've only had one person call me in 11,000 inspections, and she didn't move into the house until nine months later. She did a non-secured rentback to the previous owner. Stupid. But she learned.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 6/11/10, 1:36 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Checking AC with temp differentials.

Mark -

As a past HVAC Tech, taking the TD across the coil verifies for me that my equipment is doing (or not doing) what it should be.

Taking TD's at RA and SA tell me if its getting out into the room where your customers LIVE. If I've only got 9-12 degree TD's at my RA and SA sources thats as good as it gets for the people living there - It only goes downhill from there once it hits the room.

At 9-12 degrees TD at RA & SA, they're losing the conditioned air between Point A & Point B. At this point, they can have a COMPETENT hvac tech try to improve their lot in life OR the homes duct system, etc.
Reply With Quote
  #12  
Old 6/11/10, 7:57 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Checking AC with temp differentials.

As Dan points out, this test can be used as an indicator if the compressor is even running.

The problem is that all too often this process is used as a diagnostic tool to analyze the operation system.

Just this week I got a 70 page home inspection report that condemned three HVAC units because of Delta T. High relative humidity was in place and the Delta was low.

Delta can change with fan speed. Who's to say from our end, what is right and what is wrong. System design may be to handle humidity more than temperature. We don't know this. The equipment is still functioning as intended (or in some cases unintended), but it still is operating to full capacity though you're not getting the proper Delta that you feel you should achieve.

The best way you can test an HVAC system is like what Russel pointed out. Turn it on till they scream!
I still use this RR recommendation (many years later), and every time they scream I smile and think about Russel Ray!

I have posted in the past how you can test the HVAC system without using any tools. All I got was grief about it. The preferred method is the SOS put out by home inspector diploma mills.

Many years ago I had a service manager tell all of us that we must take the Delta before we leave a service call and record it on the invoice. I told him that I would start tracking mud through the client's living room to take those measurements when he explained to me how this useless process was going to be utilized. He couldn't, so I didn't. There are way too many variables involved and unless you fully understand all of the variables that affect the reading if you're getting they are worthless to you.

I always had mud on my shoes because I was one of the few service technicians that took coil cleaner and a water hose out of the truck before anything else and clean the unit (when needed) so that I could properly analyze its operation under factory design conditions (clean).

Granted, a large majority of the units tested will have an adequate Delta , which is in fact an indication they are performing. But unfortunately you will find that all too many of the units that fail your test are actually performing and you are generating an unnecessary additional expense to the buyer and/or seller. These additional expenses are starting to filter back to the home inspectors when HVAC contractors find nothing wrong.

HVAC contractors are thanking you though!

Give me a call Mark. If I'm cruising the interstate we can discuss HVAC testing.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #13  
Old 6/11/10, 11:42 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Checking AC with temp differentials.

After reading about Delta T for nine years now, I still have absolutely no idea what it is.

I'm sticking with my tried, tested, and proven method.



NACHI 2005 U.S. Member of the Year
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 6/11/10, 7:55 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Checking AC with temp differentials.

Please do and teach those that think otherwise!

I did three energy audit/thermal evaluations today.

Everyone was "Hot under the collar".

All three had HVAC equipment working their @ss off but could not perform.

All three had one or more HVAC professionals (alleged) there prior to my arrival.
They found nothing.

So much for deferral to those that should know!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #15  
Old 6/11/10, 10:10 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking AC with temp differentials.

Quote:
Originally Posted by dbowers View Post
Taking TD's at RA and SA tell me if its getting out into the room where your customers LIVE. If I've only got 9-12 degree TD's at my RA and SA sources thats as good as it gets for the people living there - It only goes downhill from there once it hits the room.
This is the method that I use. I'm looking more for consistent temperatures coming out of the resisters. If I'm at one end of a house and all the resisters in that area are reading at 64-69 degrees and I find one at 74 degrees, I call it out for further evaluation.


www.MauiHomeInspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Temp in elec dryer ? lfoster Ancillary Inspection Services & Additional Topics 1 12/29/09 7:41 PM
outside temp over 80F, still test? mschild Inspecting HVAC Systems 12 10/7/06 11:55 AM
Temp differential dlee2 Inspecting HVAC Systems 4 8/22/06 11:01 AM


All times are GMT -4. The time now is 11:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts