I've read the discussions regarding the pro's and con's of using the temperature split (supply -vs- return temps) on freon based a/c systems. Earlier this week I inspected a fairly expensive hi-rise condo unit that used a chiller for the a/c system. The building purchased btu's from the city, ran city chilled water thru a heat exchanger for the entire building and then circulated the resulting secondary chilled water thru-out the building for each unit's individual a/c. For lack of a better method I used the temp split as an indicator of the proper performance of that system. My question is, can I use the 14° to 21° split that I normally use for a freon based split system as a guide for a chiller system? If not, then what split temp or other method should I have used to judge the performance of the system?
Reply With Quote
  #2  
Old 8/10/07, 6:34 PM
Thomas Duchesneau's Avatar
Thomas Duchesneau Thomas Duchesneau is offline
New User
 
Join Date: Aug 2007
Location: Rocky Hill, CT
Posts: 10
Please Note: Thomas Duchesneau is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Chillers

Depending on how well the CHW lines are insulated, and how far the unit is away from the chiller, usually one would get about 40/45*F into the coil, and 55/60*F out. These would be the readings with the apt. at 70-75*F.
The only problems likely are dirty air filters, coil, or defective water modulating valve.
Discounting problems with the primary water chiller, of course...
Reply With Quote
  #3  
Old 8/10/07, 7:59 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Chillers

Thanks Thomas. This was a 5 year old upscale condo ($440,000 for 820 sf), the unit was on the 9th floor of the 12-14 story building. I was getting a 12° temp differential and the building maintenace supervisor told me even before I checked the differential to expect 10° to 12°. Sounds like you agree with those numbers. I did not call anything out as in need of repair or service.

chillers-dt-austin_condo.jpg

Last edited by mboyett; 8/10/07 at 8:06 PM..
Reply With Quote
  #4  
Old 8/13/07, 8:31 PM
Bruce D. Pinel Bruce D. Pinel is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: North Kingstown, RI
Posts: 158
Default Re: Chillers

You may also want to make sure they are not using any reheat devices, (electric coils) to raise the discharge air if they are doing dehumidification.
Reply With Quote
  #5  
Old 8/13/07, 9:02 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Chillers

Interesting...I hadn't considered that possibility. I may call the building super and ask him if they do dehumidify the air. Thanks!
Reply With Quote
  #6  
Old 8/13/07, 9:10 PM
Bruce D. Pinel Bruce D. Pinel is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: North Kingstown, RI
Posts: 158
Default Re: Chillers

There may be 2 stats or a single, dual element device in the room for sensing both T&H. Real easy to do if they have an Energy Management System, (EMS). If no EMS, they may not be doing it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:24 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts