Default CO detection, TPI775 meter different from gas co.

On a recent inspection I noted high (35ppm +)levels of CO at the heat outlets (gas forced air furnace - I'm in Canada). I was actually in the house on two different days and took readings at two different times on both days with similar results. Each reading was taken over a 15 minute time span. The seller is in denial and had the gas co come out to check. They gave a report saying no problems.

1. is anyone else using the tpi775 meter? have you ever suspected false readings?

2. is there any condition in which a furnace can give off differing levels of CO? Can the length of time the furnace has been running influence this?
Reply With Quote
Find an InterNACHI certified Alabama Home Inspector (and anywhere else in North America)
  #2  
Old 11/6/09, 1:58 PM
gkay gkay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CO detection, TPI775 meter different from gas co.

When was the last time you had your meter calibrated?
Reply With Quote
  #3  
Old 11/6/09, 4:07 PM
kbartsch kbartsch is offline
InterNACHI Member
 
Join Date: Sep 2009
Posts: 6
Default Re: CO detection, TPI775 meter different from gas co.

I've had this meter for about a year and a half.
Reply With Quote
  #4  
Old 11/6/09, 4:13 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: CO detection, TPI775 meter different from gas co.

There are variables such as down drafting.
Filter should be changed every year with heavy use.
Reply With Quote
  #5  
Old 11/6/09, 6:47 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: CO detection, TPI775 meter different from gas co.

Consider a training course such as this:
http://www.nationalcomfortinstitute....ontraining.cfm

Measuring for CO in ambient air is not as simple as waving the wand of your meter around a supply duct. Many inspectors do not understand or realize this.
Calibration of your equipment is important as well.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...

Last edited by wwarner; 11/6/09 at 8:13 PM.. Reason: sp
Reply With Quote
  #6  
Old 11/7/09, 7:11 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,226
Default Re: CO detection, TPI775 meter different from gas co.

Quote:
Originally Posted by kbartsch View Post
On a recent inspection I noted high (35ppm +)levels of CO at the heat outlets (gas forced air furnace - I'm in Canada). I was actually in the house on two different days and took readings at two different times on both days with similar results. Each reading was taken over a 15 minute time span. The seller is in denial and had the gas co come out to check. They gave a report saying no problems.

1. is anyone else using the tpi775 meter? have you ever suspected false readings?

2. is there any condition in which a furnace can give off differing levels of CO? Can the length of time the furnace has been running influence this?
Kevin
Try calibrating , But keep testing. I had a furnace guy denied there was a problem the agent insisted it be checked . Seller agent said i was being to picky. They sent a fellow in he found 3 small cracks. Trust your tools but keep them updated. test it where you know the air is clear. so far sense i started checking i have found 5 furnaces with problems Kinda makes you wonder how many problems are hiding.
Reply With Quote
  #7  
Old 11/7/09, 7:28 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: CO detection, TPI775 meter different from gas co.

Wayne the "Deal Killer"




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
CPSC -----> Recall on electric meter panels pbolliger Electrical Inspections 0 10/15/09 11:23 PM
Panel and Meter jwilliams7 Electrical Inspections 10 6/21/06 5:49 PM


All times are GMT -4. The time now is 6:44 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts