Did an inspection today on a single story home on a crawl.
The question is they are using the crawl space for the cold air return. There are no outside vents and no vapor barrier. This is a first for me in 5 years. Is there an issue using the crawl. Thanks Bill Bill Emelander Professional Edge Home Inspection Grand Rapids and all of West Michigan NACHI #03111914 www.proedgehi.com |
|
#2
|
||||
|
||||
|
2003 IRC M1602.1 Return Air. Return air shall be taken from inside the dwelling. Dilution of return air with outdoor air shall not be prohibited.
|
|
#3
|
||||
|
||||
|
Quote:
Jeff Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#4
|
||||
|
||||
|
Bill,
If this is a fueled furnace...Or is it a simple air handler for A/C only? The return should not be in the same room as the furnace. The return/duct must be installed in a completely different room. In a worse case scenario...If the furnace was to burn carbon monoxide, these deadly gases would get sucked right into the return and sent directly into the living area. The return must be installed so it's taking it's air from anywhere other than the same room as the furnace. |
|
#5
|
||||
|
||||
|
FYI. There shouldn't be any romex type wiring in the crawlspace. All wiring methods used in the crawl need to be plenum rated, such as MC cable or conduit. Doorbell, computer, phone and thermostat wire, also need to be plenum rated.
|
|
#6
|
||||
|
||||
|
Quote:
|
|
#7
|
|||
|
|||
|
A little added information. The furnace is not in the crawl space. It's in the utility room and the return air is drawn fron the bottom. also there are no outside vents in the crawl so it is not getting outside air.
Bill Bill Emelander Professional Edge Home Inspection Grand Rapids and all of West Michigan NACHI #03111914 www.proedgehi.com |
|
#8
|
||||
|
||||
|
Very easy to get around that nonsense. Return air is not allowed to be taken from a non-conditioned space. Just as well take the return from the attic????
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#9
|
||||
|
||||
|
Quote:
Jeff (Thanks for the clarification) </IMG></IMG></IMG> Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Cold Air Return | Sherri Bradshaw | Inspecting HVAC Systems | 9 | 11/15/07 3:55 PM |
| Reduced return air duct | mmorgan | Inspecting HVAC Systems | 4 | 6/6/07 8:39 PM |
| cold climates: insulating floors w/plumbing above cold crawlspaces | kshepard | Plumbing Inspections | 6 | 9/26/06 12:09 AM |
| cold air return in basement? | bmargiotti | Inspecting HVAC Systems | 9 | 1/24/06 6:51 PM |
| Cold air return and electrical romex | dmacy | Electrical Inspections | 12 | 1/3/06 7:16 PM |