Question Cold air return

I have had some issues with renovators, the question being, placement of the cold air return in a finished basement. What is acceptable, ceiling height or floor height, not common practice.
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/10/11, 4:13 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Cold air return

Quote:
Originally Posted by btreacy View Post
I have had some issues with renovators, the question being, placement of the cold air return in a finished basement. What is acceptable, ceiling height or floor height, not common practice.
Opposite of supply vent.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #3  
Old 12/10/11, 4:37 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Cold air return

You want the cold air coming back to the furnace if you can do it, that is near the floor or if you can't follow what Christopher said.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #4  
Old 12/10/11, 5:16 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Cold air return

Quote:
Originally Posted by kwood View Post
You want the cold air coming back to the furnace if you can do it, that is near the floor or if you can't follow what Christopher said.
Kevin I am going to pick on you if ya don't mind and if you do mind I am going to anyway

The title of this thread was aimed at cold air return would someone define the word cold air why not the word warm air return In the world I worked in it was always referred to as simply return air. Where in the world would a return come back to if not the furnace do yous have a separate blower circulating air this makes no sense to me explain please



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 12/10/11, 5:43 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Cold air return

Cold air return or air return. The biggest mistake people make when it comes to the air return is putting it on the ceiling in the basement. I know it is a challenge to get the air return near the floor but this is wear the cold air resides. You want the coldest air going back to the furnace and not the heated air. If you take back the heated air you are left with the cold air still at floor level. This is why in a cold climate it is next to impossible to keep a floor warm unless it is heated or well insulated. To combat the loss of warm air many put a door to the basement at the top of the stairs. This is no good because the heat will escape up to the door. If the door is installed on the bottom of the stairs the heat is maintained in the basement area and it prevents the stack effect.
Now the opposite is needed for cooling conditions but that is a new topic for discussion.
We use the same principle in installation of a HRV, have all the warm air possible at the highest point pass across the cold air coming into the unit and extract the warm air from the exhaust. Not doing these simple tricks will make either your furnace or HRV not perform to its maximum potential.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 12/10/11, 11:22 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Cold air return

I was just wondering why the word cold is always attached to the words return air in the home inspecting world to me its like having an elevator in a out house



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 12/10/11, 11:29 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Cold air return

Quote:
Originally Posted by cbottger View Post
I was just wondering why the word cold is always attached to the words return air in the home inspecting world to me its like having an elevator in a out house
The same reason as using the term "hot water heater".

Get with the program Charlie.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 12/10/11, 11:50 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Cold air return

Quote:
Originally Posted by ccurrins View Post
The same reason as using the term "hot water heater".

Get with the program Charlie.
I wuz about 18 years of age when I quit using the term (Hot water heater) that wuz immediately following the smack up side of my head with a pipe wrench by and old plumber



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 12/13/11, 7:30 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Cold air return

Quote:
Originally Posted by kwood View Post
Cold air return or air return. The biggest mistake people make when it comes to the air return is putting it on the ceiling in the basement. I know it is a challenge to get the air return near the floor but this is wear the cold air resides. You want the coldest air going back to the furnace and not the heated air. If you take back the heated air you are left with the cold air still at floor level. This is why in a cold climate it is next to impossible to keep a floor warm unless it is heated or well insulated. To combat the loss of warm air many put a door to the basement at the top of the stairs. This is no good because the heat will escape up to the door. If the door is installed on the bottom of the stairs the heat is maintained in the basement area and it prevents the stack effect.
Now the opposite is needed for cooling conditions but that is a new topic for discussion.
We use the same principle in installation of a HRV, have all the warm air possible at the highest point pass across the cold air coming into the unit and extract the warm air from the exhaust. Not doing these simple tricks will make either your furnace or HRV not perform to its maximum potential.
So are you suggesting putting both the supply and return at floor level at opposite ends of the room?
Reply With Quote
  #10  
Old 12/13/11, 10:52 PM
Rick Strand's Avatar
Rick Strand Rick Strand is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Calgary, Alberta, Canada
Posts: 266
Default Re: Cold air return

Cold air falls down the stairs to the basement, that's where the return air inlet belongs, on the floor at the foot of the stairs. If you have natural draft furnace, do not have the return air inlet too close to the furnace as back drafting can result.



Rick Strand, CPI
CAHPI Associate
Strand Home Inspections Inc.
Calgary, Alberta, Canada
Serving Calgary, Okotoks, Airdrie, Chestermere and Cochrane Alberta
Reply With Quote
  #11  
Old 12/14/11, 5:59 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Cold air return

Agreed



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #12  
Old 12/14/11, 6:01 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Cold air return

Quote:
Originally Posted by jallingham View Post
So are you suggesting putting both the supply and return at floor level at opposite ends of the room?
It would depend on the lay out of where the stairs is and If the stairs had a door at the bottom and other considerations. Finding the coldest area for the return is best.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cold air return duct placement abishop Inspecting HVAC Systems 3 5/26/11 3:09 PM
Cold air return mthiltgen Inspecting HVAC Systems 13 3/27/09 4:20 PM
cold air return salstad Inspecting HVAC Systems 5 3/9/09 8:48 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Cold air return and electrical romex dmacy Electrical Inspections 12 1/3/06 6:16 PM


All times are GMT -4. The time now is 11:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts