so what do you think, my AC was warm today, the suction line was icing up so I shut down the unit and left the fan on to thaw it out. checked the filters for restriction, they were clean. fired it back up after the unit thawed out and now my High pressure line is pretty cold and sweating, the suction line is near ambient temperature.
this is not a reverse cycle unit, electric heat strips, Builder grade Goodman 10 years old. The compressor is noisy. and the condensing unit fan is pushing cool air as if it were in reverse cycle. could the expansion valve have stuck? I have a service contract on it, but just curious if anyone has any ideas. Last edited by kdolin; 11/17/10 at 7:25 PM.. |
| Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Most likely problem is a clogged drier. If one is not used on your system the next best guess is a clogged expansion valve. I would make sure they install a new drier during the repair.
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#3
|
||||
|
||||
|
Thanks Bruce, thought about it this am with a fresh head, has to be a restriction causing the pressure drop, The line is sweating all the way to the unit, I will have to look for a change in the temp of the line to indicate where the restriction is.
|
|
#4
|
||||
|
||||
|
May be a freon leak.
Robert Newland Tyrone, GA 30290 NACHI05101290 http://www.CertifiedHI.com http://www.HomeInspectorTyroneGa.com Home Inspection Reports Powered by: HomeGauge eServices |
|
#5
|
||||
|
||||
|
so the tech was out this morning. low side pressures were 35 high side just over 100. ambient temp today was around 73. The unit was showing about 5-8 degrees of temperature differential. Still cool liquid line and the condenser fan was pushing cool air.
The tech pushed refrigerant into the system and the low side came up to 55 or so and the high side only reached about 120. He is going to throw a compressor on the unit. (filter, capacitor, fan motor as well) Not really sure what his diagnosis was in the end, stated that the evap coil could be the cause for the compressor failure. funny thing is he stated the year of the unit was 1995. House was built in 2000. I looked at the number on the unit, its a goodman first five are 00095. That of course makes it a 2000 model year unit 9th month. Not a 95 anyway we will see what the end result is. But I thought you all would benefit from the process |
|
#6
|
||||
|
||||
|
Quote:
Quote:
Quote:
If your giving us the correct facts, your getting screwed. You had a low charge and have a leak. May damage your new stuff if not repaired... New parts = > than the cost of a new condenser after you add in the fact that you get little or no warranty vs a new condenser. Seeing R-22 is out the door, you will be looking at a totally new unit in the near future. Should consider the replacement now. Got any questions, call me. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#7
|
||||
|
||||
|
I recently had a similar problem, and for the reasons David mentioned, I opted for a complete new system (heat and air). The $1500.00 gov rebate did me no good (5 ton units were not part of the program
Ken, if you decide to replace, find a reputable installer. When I researched all the various brands, it all boiled down to how good your installer is. Good luck! Robert Newland Tyrone, GA 30290 NACHI05101290 http://www.CertifiedHI.com http://www.HomeInspectorTyroneGa.com Home Inspection Reports Powered by: HomeGauge eServices |
|
#8
|
||||
|
||||
|
I called, he's not paying for the repair.
Though condemning the unit would be nice to get off the R-22... "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#9
|
||||
|
||||
|
This is just an experiment in diagnosis and repair. I have a service contract on this, no cost to me. I am certainly not comfortable with the diagnosis, but it will be interesting to see the outcome. So far 24 hours to get a tech for the diagnosis and he called today and scheduled the install for next Wednesday! Good thing I have another house around the corner or I would be putting my Wife and her dogs up at the Breakers for the week!
On the other note, its not due to lack of freon even though it did ice up at the evaporator. The key to this is that the liquid line was cold. That has to indicate either a restriction near the compressor allowing the liquid to transition to a gas prior to the expansion valve/orfice tube. |
|
#10
|
||||
|
||||
|
BTW thanks for the call Dave
|
|
#11
|
||||
|
||||
|
So just a final on this. They came out and dropped a new compressor, filter and condensing fan motor on the unit. fired it up and all was back to normal. The new compressor sounded quiet and smooth.
Never did I find out definitely what the cause was but I would guess it was valving in the compressor. So back to an 18 degree differential just in time for the cold weather. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Hot Liquid Line on AC | krigler | Inspecting HVAC Systems | 19 | 7/17/10 8:00 PM |
| Liability question | jcahill | Legislation, Licensing & Legal Issues for Inspectors | 30 | 8/24/08 4:10 PM |
| Slope of waste drain line. | mlong | Plumbing Inspections | 5 | 4/23/08 9:54 PM |
| 980 Questions/Answers to the NHIE....Free! | jbushart | Legislation, Licensing & Legal Issues for Inspectors | 50 | 4/20/08 1:26 AM |