Default Combustable air

Trane furnace high efficiency 13 years old. Basement was finished and there is no air vent installed at the walls or door to the furnace room that is maybe 10X10.

There is a small hole at the furnace cabinet but no space under the utility room door

Does this unit need a compustable air vent?

Thanks
Attached Thumbnails
combustable-air-91607-038-small-.jpg.jpg
Views:	150
Size:	40.2 KB
ID:	9382  
Reply With Quote
  #2  
Old 2/22/07, 4:36 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Combustable air

Quote:
Originally Posted by dmacy
Trane furnace high efficiency 13 years old. Basement was finished and there is no air vent installed at the walls or door to the furnace room that is maybe 10X10.

There is a small hole at the furnace cabinet but no space under the utility room door

Does this unit need a compustable air vent?

Thanks
Is that vent not a pipe within a pipe can not tell from the pic and if it is it is getting combustion air.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 2/23/07, 4:03 AM
Paul Tos Paul Tos is offline
New User
 
Join Date: Feb 2007
Posts: 15
Please Note: Paul Tos is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustable air

Usually on HE Furnace (90+) install, should have two pipes coming off of furnace one for intake air and one for exhaust. Termination to outside air (also special procedures).Picture seems to show only one pipe hook up (exhaust). Would check model number, go to Trane Site and pull the PDF file that covers the venting procedure for model.
Reply With Quote
  #4  
Old 2/23/07, 6:45 AM
Paul Tos Paul Tos is offline
New User
 
Join Date: Feb 2007
Posts: 15
Please Note: Paul Tos is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustable air

80+ or less installs (non self-contained combustion chamber)

National Fuel Gas Code section on Air for Combustion and Ventilation or applicable provision of the local building codes should apply to both 80 & 90.



Circa 93-96, we were required to bring in outside air and terminate down wall within 12 inches of floor adjacent to any furnace. Did not matter if space was considered confined or unconfined or if furnace was 80 or 90.


Definition back then from manufacturer requirement on an 80+ or less install.

UNCONFINED SPACE - An unconfined space must have at least 50 cu ft for each 1000 Btuh of input for all the appliances (such as furnaces, clothes dryer, water heaters, etc.) in the space.

If unconfined space is constructed usually tight, aire for combustion and ventilation MUST come from either the outdoors or spaces freely communicating with the outdoors. Combustion and ventilation openings must be sized the same as for a confined space. A minimum opening with a total of at least 1 sq in / 5000 Btuh of total input rating for all equipment must be provided. Return air must not be taken from the room unless an equal or greater amount of air is supplied to the room.


CONFINED SPACE

A confined space is one whose volume is less than 50 sq ft per 1000 Btuh of the total input rating for all appliances installed in that space. A confined space MUST have 2 permanent openings. 1 within 12 in of the ceiling and the other within 12 in of the floor. Different requirements then came into play depending on where one was drawing the required air from.
Attached Thumbnails
combustable-air-venting-1.jpg   combustable-air-venting-2.jpg  
Reply With Quote
  #5  
Old 2/23/07, 6:55 AM
Paul Tos Paul Tos is offline
New User
 
Join Date: Feb 2007
Posts: 15
Please Note: Paul Tos is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustable air

Images may need to be saved then enlarged in a viewer, to be able to read the text
Attached Thumbnails
combustable-air-venting-1.jpg  
Reply With Quote
  #6  
Old 3/5/07, 1:48 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Combustable air

David,

I'm not sure "Trane" offers a "Concentric vent design" on their 90% + Condensing type furnaces. The type unit I think I'm looking at in your picture would typically use a Exhaust & Intake pipe system. At worst, any enclosed area must have external combustion air (High/Low) installed to the area of any Gas-Fired appliance (ie: Furnace, Water Htr, etc.).
I'm sure you are aware, but I can't tell you the number of times I've seen piped Exhaust/Intake venting of the furnace, and no C/A designed for the non-sealed HWH operation. I mean the Co. Insp's. miss it all the time.
Reply With Quote
  #7  
Old 3/7/07, 8:29 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustable air

This is a TUC x x x B series furnace. On the right hand side of the venter motor is a blower assembly for pulling combustion air pipe into the furnace. The furnace may be vented either with or without the combustion air pipe depending upon installation location. Recommend that HVAC company install the combustion air pipe to the furnace.
Reply With Quote
  #8  
Old 3/7/07, 10:22 PM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,391
Default Re: Combustable air

As to combustion air, when in doubt, give an opinion or a description of existing conditions, and then recommend that a specialist comment.



InterNACHI Vice President, InterNACHI Editor-in-Chief, co-founder CalNACHI

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combustable air dmacy Inspecting HVAC Systems 15 1/11/07 5:19 PM