Default Combustion Air

I see this everyday. Natural gas furnace in garage with no outside combustion air source. Is a combustion air source required in a garage that is not sealed shut? Will the small opening around a main garage door provide enough combustion air for the furnace? Like I said I see this every single day. I would like to know once and for all is it okay or do not need to note that a combustion air source is not present. Thanks in advance.
Reply With Quote
  #2  
Old 10/13/08, 12:00 AM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 216
Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted
Default Re: Combustion Air

I would recommend a qualified HVAC Tech. evaluate the combustion air requirements for the unit. Even if there were enough gaps around the doors to provide the required combustion air. If the homeowner were to seal them to keep the bugs out heat in or for some other reason, the unit could start producing co2.



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
  #3  
Old 10/13/08, 1:34 AM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 423
Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information
Default Re: Combustion Air

First off, it's not living space so risk of issues is minimized.
Secondly you can use an open space for combustion air relative to the number of BTU per cubic feet of space, and most garages have a relatively large amount of cubic feet of space. (50 cu.ft / 1000 BTU/hr)
Third, a furnace uses a relatively small amount of combustion air, and I can't imagine a vehicle garage door that would be so tight as to not allow that much air to pass.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr
"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold
Reply With Quote
  #4  
Old 10/13/08, 11:08 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: Combustion Air

Ralph's post: Ditto.

Also new furnaces are all induced draft, they will win the draft game in most cases with an open garage. You can't seal a garage door that good or it will not open.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 10/17/08, 12:28 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 444
Greg Veal is generally well trusted
Default Re: Combustion Air

Local and National codes require C/A design for this situation.
In my area, local codes meet/exceed the National, with specific design criteria. They basically account for TODAYS design of equipment and structual energy envelop design.
In our area, a typical two (2) bay garage with a gas-fired furnace/water heater requires introduction of exterior C/A ventilation, and if a second gas-fired furnace or water heater is added, additional sq inches of lovered ventilation is calculated into the installation of this fixed (high/low) louverd design.
I agree with David about induced-draft design capabilities in theory, but conditions vary so greatly with construction quality, design, interpretation of conditions existing, that design for external C/A is or should be standard procedure throughout.
IMHO
Reply With Quote
  #6  
Old 10/17/08, 12:42 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: Combustion Air

We must view the situation in accordance with our local standards. Some localities here require makeup air in garages and others fall on the BTU capacity/free air space of the utility room/garage ratios.

Personally, because I have the equipment from a past life I do test the effects of inadequate makeup air. This is outside of the SOP. I generally address the combustion air issue when I can specifically document the deficiency through testing.

I hate to get involved in deciphering the building code dates and interpretations, so I avoid it as much as possible. We don't really have a mechanical code in my area. They said have one but it's just a combination of electrical/plumbing to formulate mechanical. It is nothing like the commercial mechanical codes I am familiar with.

I am just addressing points of perspective to be considered a home inspector who must make a decision in light of regional practices. It is always safe to report on the fact that there is or is not a source of outdoor combustion air. Remember, system performance evaluation is not in our job description.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #7  
Old 10/17/08, 2:13 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,248
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air

Quote:
Originally Posted by gveal View Post
Local and National codes require C/A design for this situation.
In my area, local codes meet/exceed the National, with specific design criteria. They basically account for TODAYS design of equipment and structual energy envelop design.
In our area, a typical two (2) bay garage with a gas-fired furnace/water heater requires introduction of exterior C/A ventilation, and if a second gas-fired furnace or water heater is added, additional sq inches of lovered ventilation is calculated into the installation of this fixed (high/low) louverd design.
I agree with David about induced-draft design capabilities in theory, but conditions vary so greatly with construction quality, design, interpretation of conditions existing, that design for external C/A is or should be standard procedure throughout.
IMHO
Is this fan powered or passive?
Reply With Quote
  #8  
Old 10/17/08, 3:38 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 444
Greg Veal is generally well trusted
Default Re: Combustion Air

Brian,

No powered/mechanical ventilation is required normally, just a fixed ventilation louver allowing ambient movement of air.
My explanation above is just that, and explanation of basic/typical design for ensuring adequate C/A for the safe and reliable operation of gas-fired mechanical equipment.
I am a Home Inspector now, practicing as suggested by industry SOP, etc. I would always yield to the industry experts of today, and I ALWAYS recommend further evaluation/inspection to my Client.
Sorry if I wasn't clear in my previous reply.
Reply With Quote
  #9  
Old 10/17/08, 4:08 PM
Dylan J. Bucknavich Dylan J. Bucknavich is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 568
Dylan J. Bucknavich is almost always very helpful Dylan J. Bucknavich is almost always very helpful Dylan J. Bucknavich is almost always very helpful Dylan J. Bucknavich is almost always very helpful Dylan J. Bucknavich is almost always very helpful
Default Re: Combustion Air

I don't call this out. The garage itself and the opening should supply all the necessary air. If there are vents provided and they are obstructed, then I will mention that. An inspection of the unit should determine if insufficient combustion air is present.

Let me ask this, do you believe the unit will draw air through the garage/house entry door before the garage bay door? Basically, the garage floor space and bay doors work. In my opinion of course.



Dylan Bucknavich
Arizona Professional Home Inspection L.L.C.
www.AzProHomeInspection.com
Chandler, AZ
Nachi ID# 06020796
Council-Certified Residential Mold Inspector
Reply With Quote
  #10  
Old 10/19/08, 10:42 AM
Harry V. McBride, III's Avatar
Harry V. McBride, III Harry V. McBride, III is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Alachua, FL
Posts: 91
Harry V. McBride, III is generally well trusted
Default Re: Combustion Air

I appreciate the responses guys. I will need to find the local code out. I did not even think that modern systems may not require C/A in the garage space. Thanks again!
Reply With Quote
  #11  
Old 10/19/08, 11:29 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,248
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air

Quote:
Originally Posted by gveal View Post
Brian,

No powered/mechanical ventilation is required normally, just a fixed ventilation louver allowing ambient movement of air.
My explanation above is just that, and explanation of basic/typical design for ensuring adequate C/A for the safe and reliable operation of gas-fired mechanical equipment.
I am a Home Inspector now, practicing as suggested by industry SOP, etc. I would always yield to the industry experts of today, and I ALWAYS recommend further evaluation/inspection to my Client.
Sorry if I wasn't clear in my previous reply.
This style of required ventilation can fail and suck air out of the furnace room when the direction of strong winds put the vent hood in the lee of the wind where negative pressures develop.

The Wood Energy Technology Transfer org in Canada has a homeowner video of wood smoke actually being drawn out of a directly connected c/a duct/supply hood at the main floor joist level (wood appliance was on the main floor ) while combustion air was being drawn down the chimney and the fire burnt down through the wood!! Not as designed!!!
Reply With Quote
  #12  
Old 10/19/08, 11:52 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is online now
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,319
Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted
Default Re: Combustion Air

Harry,
Section M1702 of 2003 IRC has some of the info you are looking for. There ar a lot of R309.2 violations around here with unducted vents. When are you going to buy lunch, Sonny's works.



Bungalows to Mansions
Professional Inspection Services, LLC
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.bungalowstomansions.com

Last edited by bgraham; 10/19/08 at 12:15 PM.
Reply With Quote
  #13  
Old 10/19/08, 11:57 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 4,199
Larry D. Kage .
Default Re: Combustion Air

Quote:
Originally Posted by Brian A. MacNeish View Post

The Wood Energy Technology Transfer org in Canada has a homeowner video of wood smoke actually being drawn out of a directly connected c/a duct/supply hood at the main floor joist level (wood appliance was on the main floor ) while combustion air was being drawn down the chimney and the fire burnt down through the wood!! Not as designed!!!
I'd enjoy viewing that. Do you have a link?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #14  
Old 10/19/08, 10:47 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,248
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air

Quote:
Originally Posted by lkage View Post
I'd enjoy viewing that. Do you have a link?
Haven't found a link yet but here's some info on outdoor air supplies from a Canadian guy I call Mr. Wood Heat, John Gulland. He was one of my trainers in 1988 when I received my Master System Advisor certificate.

http://woodheat.org/outdoorair/outdoorairmyth.htm
Reply With Quote
Old 10/19/08, 10:59 PM
Mario A. Kyriacou, CHI
This message has been deleted by mkyriacou.
  #15  
Old 10/19/08, 11:12 PM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 216
Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted
Default Re: Combustion Air

Mario,
Your right! My bad



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Another reason to recommend CO testers rnewman1 Interior 2 10/12/06 8:47 AM
Combustion Air Availability? cradan HVAC 4 2/19/06 10:16 AM


All times are GMT -4. The time now is 5:53 PM.