Default Combustion Air?

Wonder if there is enough combustion air for this furnace? The furnace and hot water tank are in a utility room together. The door to this room is solid. The only air coming into this room is in the lower right hand corner of this picture.

combustion-air-copy-pb080154.jpg



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #2  
Old 11/9/08, 11:06 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air?

Quote:
Originally Posted by nbhi View Post
Wonder if there is enough combustion air for this furnace? The furnace and hot water tank are in a utility room together. The door to this room is solid. The only air coming into this room is in the lower right hand corner of this picture.

Attachment 25099
Is the ceiling open joist work or closed in with drywall?
Where does the fluepipe/s leave the area?
Any signs of backdrafting/smoke spillage?
Reply With Quote
  #3  
Old 11/9/08, 3:17 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Combustion Air?

Quote:
Originally Posted by Frank Cece View Post
    1. Is that air supply from the exterior or the building envelope?
    2. Is the solid door hard to open when the furnace is working?
    3. What type of furnace is it, high efficiency, natural draft, induced?
    4. Is the chimney lined if used?
    5. More info is required dude
Certainly these appliances are spillage susceptible if natural draft.
? 1 The air is coming from the attic.
? 2 No
? 3 Natural draft
? 4 Yes
This is something I came across.

"Combustion air ("make-up air") is required for gas burning appliances at a rate of 50 cu ft / 1000 BTU or else external ventilation is required. External ventilation openings should be within 12 inches (305 mm) of the top of the enclosure, and one within 12 inches (305 mm) of the bottom of the enclosure. Inadequate supply of combustion air results in incomplete combustion; products of incomplete combustion include carbon monoxide. "
Do any of you do this extent of calculations?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #4  
Old 11/9/08, 3:43 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Combustion Air?

When I find mechanical's with combustion chambers, my report recommends a louvered door.
Reply With Quote
  #5  
Old 11/10/08, 10:59 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air?

Hopefully HVAC experts will correct these theories if wrong.

A possible thumb rule would be make-up air or combustion air should be at least equal in cross sectional area to exhaust air. So a water heater with a 3" vent should have a 3" air supply?

Louvers reduce the surface by 40 or 50%?

Far better to err on the side of more than enough?

John Kogel
www.allsafehome.ca
Reply With Quote
  #6  
Old 11/10/08, 11:32 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air?

Here's some more confusing info on the subject, .
Attached Thumbnails
combustion-air-0734.jpg   combustion-air-0735.jpg  
Reply With Quote
  #7  
Old 11/11/08, 12:26 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Combustion Air?

Quote:
Originally Posted by nbhi View Post
This is something I came across.

"Combustion air ("make-up air") is required for gas burning appliances at a rate of 50 cu ft / 1000 BTU or else external ventilation is required. External ventilation openings should be within 12 inches (305 mm) of the top of the enclosure, and one within 12 inches (305 mm) of the bottom of the enclosure. Inadequate supply of combustion air results in incomplete combustion; products of incomplete combustion include carbon monoxide. "
Whoever wrote that was a genius!

Add: "Sizing calculations were not conducted. The room housing the appliances may be inadequately ventilated for the purposes of providing combustion air and we recommend an evaluation and repair by a licensed plumbing or HVAC contractor."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combustion Air hmcbride Inspecting HVAC Systems 18 10/25/08 7:27 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 8:47 AM
Combustion Air Availability? cradan Inspecting HVAC Systems 4 2/19/06 10:16 AM


All times are GMT -4. The time now is 5:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts