Default Combustion air?

Bear with me, this could be long winded. Just went though the NACHI HVAC course and also the video course. Needed a refresher. They talk about the combustion air coming in high & low within 12 inches top and bottom. I never see two sources, if it's outside air though tube it comes in at floor level. There is also return air coming back from house. Is this only for natural draft (which I don't see much any more) or also mid-level Induced draft? Should I be looking for something else and I'm not seeing it?
One other thing, in the gas furnace section it talks about if furnace upgraded to a mid or high-level efficiency that the masonry chimney flue might not be able to handle it because of gases. Does that mean that all masonry chimneys should have a metal liner? Saw something else that said if chimney is on exterior wall it should have metal liner because of cold.
Well, there ya go, you might just read this and go WTF is this guys problem! I'll check back later, thanks
Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/5/11, 6:58 PM
rmangas's Avatar
rmangas rmangas is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Wisconsin
Posts: 57
Default Re: Combustion air?

Return air has nothing to do with draft or combustion air.

There is still natural draft with residential boilers and the burners will usually be "open" and near the bottom. I do not see forced air furnaces with natural draft at all, anymore. I think that the video is talking about what area is important to keep open and clear for the the proper intake of combustion air, but I am not sure.

Some mid efficiency and high efficiency units use outside air for combustion and either exhaust the combustion gases through the wall or up a chimney, depending on temperature of gases (or whether it goes through a secondary heat exchanger). The reason some of these are required to go directly through the wall, up a lined chimney or chimneys on the outside need a liner is because of temperature. In any of these situations, the combustions gases can be cooled too quickly to escape and will end up condensing in the chimney and creating corrosive and acidic liquid.
Generally, it is always required to have a liner, if there is a chimney, in new installations and probably a safe practice, even if not required.

I hope this helps and didn't make things worse.
Reply With Quote
  #3  
Old 3/5/11, 9:11 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: Combustion air?

Most of what I see now is the single opening line coming in and going to floor. I keep seeing and reading about the openings 12" from ceiling and 12" from floor and wonder if I'm missing something. I know it's not all installations that's what I'm trying to determine which ones should have it? thankyou for your feed back
Reply With Quote
  #4  
Old 3/5/11, 9:12 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Combustion air?

Mark feel free to call me and I will explain everything, as that might help you more than a forum answer.
I explain this stuff to clients all the time .
Reply With Quote
  #5  
Old 3/5/11, 9:49 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: Combustion air?

Thanks for the talk and the info Bob! It's a lot easier talking about it then doing 20 posts for info. Had to take that call the daughter just had our first grandson and needed to catch up. thanks again
Reply With Quote
  #6  
Old 3/5/11, 10:02 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Combustion air?

Quote:
Originally Posted by mthiltgen View Post
Thanks for the talk and the info Bob! It's a lot easier talking about it then doing 20 posts for info. Had to take that call the daughter just had our first grandson and needed to catch up. thanks again
Anytime.
I am much more educational and informative on the phone than typing.
Unless in the report of course.
Reply With Quote
  #7  
Old 3/7/11, 6:14 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Combustion air?

A pic is worth a lot more than words here is typically what I see in my area high and low vent natural air flow/movement as a result of temp differential between the attic and the enclosed closet
Attached Thumbnails
combustion-air-1605-club-house-dr-enid-3-7-11-053.jpg   combustion-air-1605-club-house-dr-enid-3-7-11-054.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 3/7/11, 6:35 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Combustion air?

combustion-air-make-up-air.jpg

Rule of thumb is 1 square inch per 1,000 btu.
Reply With Quote
  #9  
Old 3/7/11, 7:12 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Combustion air?

Quote:
Originally Posted by belliott View Post
Attachment 42787

Rule of thumb is 1 square inch per 1,000 btu.
What if one has no Thumb 3 inch pipe is used if water heater only in the closet when furnace and water heater both in the closet size is increased to 6 inches



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 3/7/11, 7:27 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Combustion air?

Quote:
Originally Posted by cbottger View Post
What if one has no Thumb 3 inch pipe is used if water heater only in the closet when furnace and water heater both in the closet size is increased to 6 inches
Really?
No matter what size?
Reply With Quote
  #11  
Old 3/7/11, 8:07 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Combustion air?

Quote:
Originally Posted by belliott View Post
Really?
No matter what size?
Well no silly basically talking 40 and 50 gallon water heaters jump to 80 and going to increase the pipe size to 8 inch and so forth. Your quote was correct 1 square inch per K BTU is correct I was just messing with you gona get Linas after you



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 3/13/11, 3:13 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion air?

Quote:
Originally Posted by rmangas View Post
Return air has nothing to do with draft or combustion air.


Not true leaky returns can depressurize a mechanical room interferring with combustion air and venting.
Reply With Quote
  #13  
Old 3/13/11, 5:49 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Combustion air?

Quote:
Originally Posted by Gary Reecher View Post
Not true leaky returns can depressurize a mechanical room interferring with combustion air and venting.
So we are gonna play diff scenarios on top of all this?
Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/13/11, 5:50 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Combustion air?

Quote:
Originally Posted by cbottger View Post
Well no silly basically talking 40 and 50 gallon water heaters jump to 80 and going to increase the pipe size to 8 inch and so forth. Your quote was correct 1 square inch per K BTU is correct I was just messing with you gona get Linas after you
Oh man ....you really think he needs prodding ?
Reply With Quote
  #15  
Old 3/13/11, 7:02 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Combustion air?

Hey, my ears started burning. I was listening to Carlos and thought it was the music but noooooo, it's you guys.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combustion Air hmcbride Inspecting HVAC Systems 18 10/25/08 6:27 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM
Combustion Air Availability? cradan Inspecting HVAC Systems 4 2/19/06 9:16 AM


All times are GMT -4. The time now is 11:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts