Default combustion air and exhaust appear merged

good day americas finest.....a mid efficiency furnace with combustion air and exhaust pipes was looking nice and typical to me but theres only one pipe exiting the roof which looked about four inch, and had what looked something like a draft hood, (larger then the bottom pipe so it wasnt simply an adapter) and on top of that a reduced pipe, perhaps 1 1/2 (roof was too steep to walk and I'm getting this via binocs and silly me I didnt take a pic) so when I looked in the attic they were joined by T or something...again couldnt get close but at least got a pic. can these be joined? doesnt that suck exhaust products back as combustion air? only theory I can come up with is there is some kind of pipe within pipe device so theres only one hole in the roof. the 'draft hood' looking dealy, maybe a rain deflector for combustion air? well I seek the opinions of those more experienced then I.
mike in MN
Attached Thumbnails
combustion-air-and-exhaust-appear-merged-brianlee-054.jpg  
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/3/11, 5:19 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: combustion air and exhaust appear merged

Quote:
pipe within pipe device
That's what you have.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #3  
Old 9/3/11, 5:42 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: combustion air and exhaust appear merged




CONCENTRIC VENT TERMINATION KIT



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 9/3/11, 7:01 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: combustion air and exhaust appear merged

Quote:
Originally Posted by ccurrins View Post
Yep, and surprised I do not see them more often with cat 4 furnaces.

One hole is easier than two.
Reply With Quote
  #5  
Old 9/3/11, 8:36 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: combustion air and exhaust appear merged

Quote:
Originally Posted by minwards View Post
good day americas finest.....a mid efficiency furnace with combustion air and exhaust pipes...
A mid efficiency furnace using a pvc flue...



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #6  
Old 9/3/11, 8:53 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: combustion air and exhaust appear merged

Quote:
Originally Posted by mgratton View Post
A mid efficiency furnace using a pvc flue...
I doubt it.
Must be a typo.
Reply With Quote
  #7  
Old 9/3/11, 8:59 PM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 1,948
Default Re: combustion air and exhaust appear merged

90% efficiency and greater are condensing furnaces, and require two pipes for intake air and exhaust, and can use PVC due to their lower stack temperatures.




Steven Waskewicz

Professional Building Analyst, BPI
Colorado Springs, Colorado
719-510-7703
Rest Assured Inspection Services, LLC.
719-510-7703 mobile all the time





Reply With Quote
  #8  
Old 9/3/11, 11:17 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: combustion air and exhaust appear merged

Quote:
Originally Posted by swaskewicz View Post
90% efficiency and greater are condensing furnaces, and require two pipes for intake air and exhaust, and can use PVC due to their lower stack temperatures.
Yes, but keep in mind that many manufacturer's permit the intake on a 90%+ to be a plastic mesh like cover right at the unit (special part supplied with the equipment) if the space is big enough to provide sufficient "combustion air" (called single pipe venting)

And the exhaust has to be PVC or a special stainless steel (very expensive) due to how corrosive the flue exhaust/condensate is. Typical galvanized single wall or double wall type B/L vent shouldn't be used on the higher efficiency units because of that.

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #9  
Old 9/4/11, 7:20 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: combustion air and exhaust appear merged

Just a question.
The galvinized pipe to the right. Any perpose in the system?
Attachment 47902



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:36 PM..
Reply With Quote
  #10  
Old 9/4/11, 7:22 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: combustion air and exhaust appear merged

Mr.C those 2 nickels you keep given = a dime you know.
Would not the proper use of the phrase be, JMO & a dime?



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #11  
Old 9/4/11, 9:02 AM
Michael Inwards Michael Inwards is offline
InterNACHI Member
 
Join Date: Dec 2010
Location: Pelican Rapids MN
Posts: 64
Default Re: combustion air and exhaust appear merged

thanks for all that input, I greatly benefit. no it was no 'typo' when I said mid effeciency....I was just displaying my lack of experience which I exhibit freely in the midst of pros to be able to learn. I thought this to be mid because it had 'glow plug' but the burners where right out in the open...i could easily reach right in and burn my little pinkies. I thought high eff was totally enclosed. so again Im open to all input....since I plan to someday be the best darn inspector in the area....have to hurry, 55 old right now so thanks for the help. straighten me out on the mid/high eff
Reply With Quote
  #12  
Old 9/4/11, 9:37 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: combustion air and exhaust appear merged

Michel.
You will do fine.
You attitude is commendable. The ability to see ones errors is most important.
I made and still make errors. We are all human.
Great question. Keep asking.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #13  
Old 9/4/11, 10:37 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: combustion air and exhaust appear merged

Quote:
Originally Posted by ryoung7 View Post
Mr.O those 2 nickels you keep given = a dime you know. Would not the proper use of the phrase be, JMO & a dime?
It's a US thing, eh ... ... and sometimes it's a quarter due to inflation ...

Quote:
Originally Posted by minwards View Post
... Im open to all input....since I plan to someday be the best darn inspector in the area ....
And you will get there if you keep asking good questions about things you dont understand or haven't seen before ...

Quote:
Originally Posted by minwards View Post
I thought this to be mid because it had 'glow plug' but the burners where right out in the open...i could easily reach right in and burn my little pinkies. I thought high eff was totally enclosed.
Typically the combustion chamber on a 90%+ high efficiency furnace would be enclosed. What was the make and model for the furnace?



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/4/11, 5:36 PM
Greg W. Mathias, CCHI Greg W. Mathias, CCHI is offline
InterNACHI Member
 
Join Date: May 2010
Location: Lloydminster,Ab
Posts: 658
Default Re: combustion air and exhaust appear merged

Quote:
Originally Posted by minwards View Post
thanks for all that input, I greatly benefit. no it was no 'typo' when I said mid effeciency....I was just displaying my lack of experience which I exhibit freely in the midst of pros to be able to learn. I thought this to be mid because it had 'glow plug' but the burners where right out in the open...i could easily reach right in and burn my little pinkies. I thought high eff was totally enclosed. so again Im open to all input....since I plan to someday be the best darn inspector in the area....have to hurry, 55 old right now so thanks for the help. straighten me out on the mid/high eff
If you have some time, take the advanced HVAC course offered here. I just finished it and learned alot about the different units.
http://www.nachi.org/hvacclass2008.htm



Greg Mathias, CCHI
Journeyman Carpenter
Global Property Inspections
Lloydminster, AB. Canada
(780)205-9912
Reply With Quote
  #15  
Old 9/4/11, 7:44 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: combustion air and exhaust appear merged

Thanks for reminding me to finish my advanced course.
Mr. Mele or (Mr.Apple)and Kenton as the streight man do a great job of explaning the HVAC system in detail.
Be prepared for a 4 or 5 part course last time I looked.
Bring you note pad with you.Loads of detialed education.
HAY NO TALKING IN CLASS.
Take your books young man and sit in the front where I can watch you better. who me!!
Attachment 47912 sorry teacher.sorry class.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:36 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts