  #1  
Old 3/17/08, 4:48 PM
Skip Erwin Skip Erwin is offline
New User
 
Join Date: Jun 2006
Posts: 91
Please Note: Skip Erwin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Combustion Air Requirements for Gas Furnaces

Is there a quick and easy way to calculate how many cubic feet of combustion air a natural gas furnace in a room needs? This is assuming all the combustion air comes from that room. I know I'm not supposed to be out there making calculations like this. The reason I ask is every once in a while I run across a furnace in a room with out a source of combustion air (no flues or louvers in the doors). I need a rule of thumb to calculate this and help me decide If I need to write it up for a HVAC professional to assess and correct.

I've looked all over the Internet and I get conflicting information.

Thanks in advance.
Reply With Quote
  #2  
Old 3/17/08, 5:09 PM
Linas Dapkus, CMI's Avatar
Linas Dapkus, CMI Linas Dapkus, CMI is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL.
Posts: 6,543
Default Re: Combustion Air Requirements for Gas Furnaces

Here's what I got:
Formula for combustion air:Take the cubic footage of the enclosed room. (HxWxD).
Multiply by 20.
If the resulting number is greater than the INPUT btu of the unit, it is OK.

I don't remember where I got it.



Linas Dapkus, CMI
Infraspection Institute Certified Infrared Thermographer Level III # 8510
Dapkus Home Inspections
Dapkus Home Inspections Inc. - No Gimmicks, No Kickbacks, Your personal contact information will not be sold to third parties. For 8 years & counting, quality home inspections is all we sell.
Reply With Quote
  #3  
Old 3/17/08, 5:10 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Missouri
Posts: 24,627
Default Re: Combustion Air Requirements for Gas Furnaces

Quote:
Originally Posted by Skip Erwin
Is there a quick and easy way to calculate how many cubic feet of combustion air a natural gas furnace in a room needs? This is assuming all the combustion air comes from that room. I know I'm not supposed to be out there making calculations like this. The reason I ask is every once in a while I run across a furnace in a room with out a source of combustion air (no flues or louvers in the doors). I need a rule of thumb to calculate this and help me decide If I need to write it up for a HVAC professional to assess and correct.

I've looked all over the Internet and I get conflicting information.

Thanks in advance.
There is more than one formula. For instance, outdoor air for combustion (according to CodeCheck) is:

Example: Appliance Btus = 120,000. If using outside air source only, opening (x) must be min 40 sq in (120,000 / 3,000).
Reply With Quote
  #4  
Old 3/17/08, 5:36 PM
Larry Kage, CMI Larry Kage, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: NW, MI
Posts: 10,883
Default Re: Combustion Air Requirements for Gas Furnaces

http://www.nachi.org/forum/showthread.php?t=24379&highlight=combustion


For a furnace located in an unconfined space, typically, 50 cubic feet of air is needed for each 1000 btu of total (add up all appliances) input.

For example with an 8 foot ceiling height:

50,000 btu = 18' x 18'
75,000 btu = 20' x 24'
100,000 btu = 25' x 25'
125,000 btu = 26' x 30'

And with "tight" construction outside air may still be required for the furnace to operate and vent properly.

Something I picked up with my recently needed furnace install. (I needed to bring in outside air.)[/font]



InterNachi Awards Portal: http://co.nachi.org/inachiawards/
____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
whis11 @ charter.net
The above post represents my personal opinion.
Reply With Quote
  #5  
Old 3/17/08, 6:21 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 30,889
Default Re: Combustion Air Requirements for Gas Furnaces

from Peoples gas
combustion-air-requirements-gas-furnaces-airforfurnace-small-.jpg.jpg
Views:	2492
Size:	48.0 KB
ID:	19643
Reply With Quote
  #6  
Old 3/17/08, 8:30 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 702
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air Requirements for Gas Furnaces

http://www.houseofcraig.net/combustion_air_calc.html
Reply With Quote
  #7  
Old 3/18/08, 12:28 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,601
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air Requirements for Gas Furnaces

There are no formulas that cover all situations as our houses are now as loose as sieves to as tight as sealed plastic baggies. Most of the trade HVAC stuff is behind the times in this regard and are based on "good guesses" from when houses were less complicated. I have consulted and trained on this stuff many times including a furnace manufacturer having me in to speak to a class of 22 oil burner mechanics "in training" and their instructor .

There are tests using micromanometers or sensitive magnahelic gauges that should be performed to determine if certain levels of depressurization will occur in the furnace room/area during certain house events. Higher depressurization levels than determined "safe" for each type of appliance puts them at risk of combustion gas spillage into the home!!!

The best system now is the "sealed combustion"/"direct vent" / "balanced flue" in which the furnace/boiler + exhaust system are sealed and exhuast is power vented by positive pressure. The system has a dedicated air supply from the exterior to the burner.
Reply With Quote
  #8  
Old 3/18/08, 6:13 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air Requirements for Gas Furnaces

Can't go just by unconfined space. Especially if there are clothes dryers in the basement. Testing of the draft with a draft meter while all exhaust fans or clothes dryers are operating is a test , IMHO, that should be conducted to determine if sufficient combustion air is present.

Recommend draft testing by HVAC company.
Reply With Quote
  #9  
Old 3/18/08, 7:25 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 8,053
Default Re: Combustion Air Requirements for Gas Furnaces

I am seeing, more and more, induced draft cat 1 and cat 3 furnaces in small condos. Some have adequit are and some do not.

In any case, all of them (when the furnace and dryer are run (air fluff)) cause significant air leakage around the windows.

The question is about more than just combustion air. If there is that much of a pressure differential, the conventionally drafted water heater, in the same utility closet, always back drafts.

Many variables, here.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 3/19/08, 6:55 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,601
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air Requirements for Gas Furnaces

Quote:
Originally Posted by wdecker
I am seeing, more and more, induced draft cat 1 and cat 3 furnaces in small condos. Some have adequit are and some do not.

In any case, all of them (when the furnace and dryer are run (air fluff)) cause significant air leakage around the windows.

The question is about more than just combustion air. If there is that much of a pressure differential, the conventionally drafted water heater, in the same utility closet, always back drafts.

Many variables, here.
Hence, depressurization testing recommended and CO detectors be made mandatory.
Reply With Quote
  #11  
Old 3/19/08, 6:58 AM
Linas Dapkus, CMI's Avatar
Linas Dapkus, CMI Linas Dapkus, CMI is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL.
Posts: 6,543
Default Re: Combustion Air Requirements for Gas Furnaces

CO detectors are mandatory in Illinois:
http://www.dapkusinspections.com/pag...tector-law.php



Linas Dapkus, CMI
Infraspection Institute Certified Infrared Thermographer Level III # 8510
Dapkus Home Inspections
Dapkus Home Inspections Inc. - No Gimmicks, No Kickbacks, Your personal contact information will not be sold to third parties. For 8 years & counting, quality home inspections is all we sell.
Reply With Quote
  #12  
Old 3/19/08, 10:35 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 7,675
Default Re: Combustion Air Requirements for Gas Furnaces

Quote:
The reason I ask is every once in a while I run across a furnace in a room with out a source of combustion air (no flues or louvers in the doors). I need a rule of thumb to calculate this
Keep out of an argument, just report that it is not there. !
Reply With Quote
  #13  
Old 3/19/08, 3:51 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 513
Default Re: Combustion Air Requirements for Gas Furnaces

David,

I have to agree with you on this one...hard to believe, HUH!

If you have noticed that the mechanical area(s) in question has no designed combustion air openings, note that in your report. If/when you start trying to design or quantify the necessary amount (trying to be helpful to your Client) needed, you have "STEPPED IN IT", "CROSSED THE LINE", ETC.

We hear it all the time, stick to what you know, what you can prove, leave the guessing to others.

IMHO and Good Luck
Reply With Quote
  #14  
Old 3/19/08, 5:52 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 8,053
Default Re: Combustion Air Requirements for Gas Furnaces

Quote:
Originally Posted by Brian A. MacNeish
Hence, depressurization testing recommended and CO detectors be made mandatory.
What Linas said.

I note the problem and defer it to a licensed and insured HVAC contractor (this passing on the liability).

I have run across many city code inspectors who OK it, and the contractor feels that they don't have to fix it (or, they get their own HVAC, the guy who installed the thing in the first place to OK it).

In such cases, I recommend that the client gets a signed, letterhead (with license number and insurance cert) from the codie or the HVAC contractor stating that it is OK. Some times, I go back (new construction) and re-check for backdrafting and get CO readings during normal usage. Many times, I get high CO readings. Then I have the client (and their lawyer) call the HVAC guy (the codies NEVER put in writing or sign anything!) and have him come out and fix it, on his dime.

BTW: The local gas utility (People's Energy) puts on a 12 hour (2 day, 6 hour lab) course for HIs to teach them this stuff. We all get the VP of operations personal cell phone number and are urged to call him, anytime, if we see something that is funky. I have done this, many times, and the PE guy agreed with me. Three times (new construction) he has turned off the gas to the building (condos) until the combustion air problem is fixed. It's nice to have that jind of backup.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #15  
Old 3/11/10, 9:01 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Combustion Air Requirements for Gas Furnaces

This is a BUMP to this thread.

Came across this combustion air calculator at State of Kentucky Dept of Housing web site.

http://www.dhbc.ky.gov/NR/rdonlyres/...calculator.xls

If this does load go to http://www.dhbc.ky.gov/plb/ and scroll down.

As they state "This is for estimating only. DHBC is not responsible for accuracy "

At another site that I posted this info at one person stated that they required a password after they downloaded it. I did not. So give it a try.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Florida Licensing Bill - Action Soon jburkeson1 Legislation, Licensing, Ethics & Legal Issues for Inspectors 250 7/1/10 4:50 PM
Commercial Electrical Inspections jtedesco1 Commercial Inspections 29 1/12/08 5:03 AM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM

All times are GMT -4. The time now is 5:01 AM.
no new posts