#31
|
||||
|
||||
|
Quote:
|
|
#32
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
From a 1996 study, Air Of Importance, by Alternative Energy Corp: "In the last several years, building scientists across the country have been quantifying the contribution made by air distribution systems to building efficiency loss in site -built homes. Estimates vary, but the average duct system appears to reduce overall system efficiency by 20 to 40 percent. This efficiency loss can have a multiplying effect with air-flow sensitive, compressor-based space conditioning systems such as air conditioners and heat pumps. Meanwhile, air distribution systems in new manufactured homes have received very little attention. This study is a step forward in trying to better understand air distribution in manufactured homes and their affect on overall system performance." And the quality appears to still be going downhill in spec built mass housing! Most people don't realize that with bad duct installations, the air handler actually increases indoor/outdoor air exchange while the fan is running. Different areas of the building become unneccessarily or more pressurized than necessary and push conditioned (heated, humified or cooled, dehumidified) air out the unsealed wall/ceilings,etc while other areas become similarly depressurized to suck in outdoor air (or crawlspace/garage air) to increase HVAC operating costs. Sealing both ducts and the building envelope will substantially decrease these costs!! Last edited by Brian A. MacNeish; 9/5/07 at 8:43 AM.. |
|
#33
|
||||
|
||||
|
Please Note:
kweiss is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I have run into the situation where the sink drain is very close to the unit and some people complain about hearing the rushing air through the sink drain. |
|
#34
|
||||
|
||||
|
I don't know how sewer gas got into this trap conversation, or why I was red boxed.
Before more posts happen, these traps are typically 'dry' in the heating season/Non-AC season. Since they are there to prevent cold air constantly blowing through them, an efficiency problem yes, but was told to prevent condensation problem. So They are let to dry in the NON-AC season. tom http://ths.gardenweb.com/forums/load...574116920.html |
|
#35
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
If they persist, recommend your client obtain a statement on their letterhead that the installation is complaint with the manufacturer's instructions, and that the manufacturer's warranty remains in effect. If they provide it, fax to to the manufacturer "for verification" Last edited by mthomas2; 9/5/07 at 4:51 PM.. |
|
#36
|
||||
|
||||
|
Please Note:
kweiss is a non-member guest and is in no way affiliated with InterNACHI or its members.
It is enough to me to point it out and as Michael said, per typical manufacturer instructions. Most probably won't follow through. But at least I have made tehm aware of the possible concern.
Good dicussion guys. |
|
#37
|
|||
|
|||
|
Please Note:
jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
If the primary condensate is connected to a lav it should be trapped at the HVAC unit. If not I always call it out as in need of repair.
|
|
#38
|
||||
|
||||
|
As I stated before my biggest concern is no sewer gas into the air stream of the furnace I did not say that was my only concern. I see all kinds of crazy connections most of them wrong.
I look at both ends of this condensate line yes most MFG recommend a trap at the outlet of the coil which is very proper. But to me the most important item is where it drains. I see a lot of lines in attic installs that connect to a vent stack and have had HVAC contractors tell me that it is alright because they placed a P-trap on the outlet of the coil. To me if there is a trap or not at the coil or if the vent is on the wrong side of the trap or there is no vent is still not as big a concern as where the condensate is being discharged. I want no possibility of a cross connect between the air stream and the sewer under any circumstances heat or cool season. Period I can give another scenario of a bad install that I see quite frequently on slab foundations. Spec houses Upflow furnace setting on top of a local return box with the return grill opening into a hall. The furnace is mounted in a hall closet with C-air provided from the attic. The condensate drains into an indirect stub-out within the return air box that has a P-trap installed below the slab. The P-trap in the slab goes dry in the heating season and the blower for the furnaces sucks sewer gas into the air stream. The only cure for this is to extend the P-trap inlet to above the return box within the furnace closet which is not really a cure because when the trap goes dry sewer gas is allowed into the furnace closet but with the indirect drain in the furnace closet at least water or a product such as Baby oil can be added to the trap to seal it in the heating season. I will say this again again again and again it is not as important if there is a trap at the outlet of the A-coil as compared to where the drain is discharging. Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#39
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#40
|
||||
|
||||
|
Quote:
badair ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes, accept the good |
|
#41
|
||||
|
||||
|
Quote:
Just stated that it was not the most important part #2 in my book. You guys are having a hard time prioritizing </IMG> Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#42
|
|||
|
|||
|
Please Note:
jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Charlie, every manual I have looked at within the last couple of years recommends the trap near the unit. ON top of that every HVAC gurro I have worked with installs one at this location on new construction if the the drain is connected to to a lav. Thats a good enough reason for me.
I list it as further evaluation is recommended and mark the in need of repair check box as required . As long as my client has been informed and I recommend this item to be further evaluated, that is a good enough reason for me. |
|
#43
|
||||
|
||||
|
Quote:
Quote:
Lets look at another situation upflow or downflow furnace installed in a hall closet the A-coil has a P-Ptrap on the condensate line at the coil the line then travels into a crawl space and connects hard piped into lets say the bathtub drain line after the tub P-trap. What would you report or would you report anything. Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#44
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
FWIW, I got curious enough about this to call Rheem's cooling division.
Their tech department gave me following reasons for requiring a trap at an evap coil under positive pressure: 1) Excessive condensation: Untrapped and under positive pressure, the cold air passing through the drain line will greatly increase condensation on discharge piping. 2) Efficiency: The drain line may be discharging to a location where conditioned air is exhausted from the structure or misdistributed within it, for example, back up the tailpiece if attached to a drain above its trap. 3) Reliability: a) You don't know what may be done post-installation to modify discharge trapping remote from the furnace or air handler. Trapping at the evap coil insures that the discharge line is trapped to start with and increases the probability that it will stay trapped in the future. b) For a trap to work properly it must be properly designed and constructed. A trap installed at the evap coil by a HVAC tech according to the manufacturer's instructions has a better chance of being right than something done later and/or at some other location by some other trade. 4) Serviceability: A trap and clean out provides access to clear blockage both up and down stream of the trap and allows easy anti-algae treatment of the entire length of the drain line. A trap ahead of the cleanout provides at least some protection against discharge of conditioned air if the cleanout is uncapped. If I get a chance I'll call Trane as well, to see what they have to say. Last edited by mthomas2; 9/6/07 at 11:10 AM.. |
|
#45
|
||||
|
||||
|
Quote:
Does this statement you have posted say one word about where the condensate line is connected to where does it drain to. How is it connected to what. You guys have a one track mind just keep going back to the P-trap thats not the question. I already know what Rheem states what Trane states What Carrier States and all of the rest of them. What I am trying to get you to understand is what they are not telling you. Read my post above and answer the question Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| near correct condensate drain | bking | Inspecting HVAC Systems | 2 | 9/19/07 1:51 PM |
| Drain only for HVAC condensate? | psiposs | Plumbing Inspections | 6 | 6/5/07 12:39 AM |
| If the primary condensate drain fails... | jfunderburk | Inspecting HVAC Systems | 2 | 3/6/07 2:47 PM |
| condensate drain | lprinzi | Inspecting HVAC Systems | 3 | 8/11/06 5:57 PM |