I'm sure this has been asked before, I did a search of the MB, but couldn't find a definitive answer. A new (6 month old) high efficiency nat. gas hot air furnace has it's condensate pump on the floor. The drain tubing ran up to a floor joist, across the basement, and is connected directly into the septic main. There is no trap or air gap, and the horizontal portion of the tube is full of water- I observed an air bubble travel up FROM the septic line to the horizontal section of the clear vinyl tubing. Seems to me that this has to be wrong! Am I right?
Reply With Quote
  #2  
Old 4/28/08, 7:38 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: condensate drain to sewer line??

Yes. It needs an air gap/indirect connection where it can't syphon back.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 4/28/08 at 7:43 PM..
Reply With Quote
  #3  
Old 4/29/08, 6:31 PM
Wendell F. Cook's Avatar
Wendell F. Cook Wendell F. Cook is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Hudson, NY
Posts: 818
Default Re: condensate drain to sewer line??

Thanks, Larry. I was pretty sure that I was correct, but wanted to be sure.
Reply With Quote
  #4  
Old 5/1/08, 12:02 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: condensate drain to sewer line??

Won't an air gap allow sewer gasses to enter the living space? I think it needed a trap. A furnace won't siphon but you could wind up with sewer gas entering the supply air stream via the condensate tube at times when it's not full of condensate.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #5  
Old 5/1/08, 9:17 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: condensate drain to sewer line??

And that needs to be an air gap, not an air break... which means that most of the indirect receptors for HVAC systems I see are wrong.
Attached Thumbnails
condensate-drain-sewer-line-dwv-air-gap-vs-air-break-diagram.gif  

Last edited by mthomas2; 5/1/08 at 9:22 AM..
Reply With Quote
  #6  
Old 5/1/08, 9:27 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: condensate drain to sewer line??

Quote:
Originally Posted by kshepard
Won't an air gap allow sewer gasses to enter the living space? I think it needed a trap. A furnace won't siphon but you could wind up with sewer gas entering the supply air stream via the condensate tube at times when it's not full of condensate.
Yes Kenton a trap is needed and a funace condensate line can siphon back to overflowing the condensate pump and all over the floor. I've seen it from a laundry tub.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Slope of waste drain line. mlong Plumbing Inspections 5 4/23/08 9:54 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
1 condensate line...... Scott Schultz Inspecting HVAC Systems 2 11/4/07 6:18 AM
condensate drain lprinzi Inspecting HVAC Systems 3 8/11/06 5:57 PM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 7:59 AM


All times are GMT -4. The time now is 6:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts