Heat pump air handler located attic with drip pan. Condensate and pan drain pipes connect to a copper plumbing vent. Quality HVAC work!
![]()
|
| Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
wow you don't see cooper vent much now days was it a commercial Building
Wayne Wilson East TN Home Inspections LLC Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-1490 http://site.myhomeinspection.net |
|
#3
|
||||
|
||||
|
"The secondary condensate port was not plumbed to the attic drain pan. As a result, when the primary drain line becomes clogged, the condensate inside the air handler has no path to escape. It will rise in the air handler cabinet until it finds a seam in which to seep out, and may cause rust inside the cabinet. In the worst case scenario, the water may rise until it travels down a duct and will cause ceiling damage when it escapes out a duct seam. We recommend that the secondary port be plumbed to the bottom of the drain pan. Immediate service is not critical and can wait until the next scheduled maintenance."
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#4
|
|||
|
|||
|
Joe,
Correct, but the drip pan drain should terminate at a conspicuous location. I also called out the vent pipe connection as non standard. |
|
#5
|
||||
|
||||
|
I struggle with that when there is a float switch present. With a float switch, a pan drain isn't even required. But if it's there, it should be installed correctly I suppose. (One solution in your case is to remove the pan drain altogether, which I wouldn't want to do.)
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#6
|
||||
|
||||
|
So what if there is only one visible drain line, attic installation, and it is at exterior of home?
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#7
|
||||
|
||||
|
If that's the primary, I would certainly call that out as unorthodox. While there is no specific rule against it, it will cause discoloration to the roof and is just generally unsightly.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#8
|
||||
|
||||
|
So in this setup you wouldn't recommend a secondary?
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#9
|
||||
|
||||
|
Where damage may occur, you always need a pan with either a float switch, an auxiliary pan drain, or both.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#10
|
||||
|
||||
|
Around here its common practice for drain line to run into the sewer lines. With a larger trap on the condesate line, it should not pose an issue unless you have a back up (then there is poo in the coil). But with both lines running into the vent, both drains should have traps on them.
Many times I see just one line, and a float switch. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#11
|
|||
|
|||
|
What happens if the trap is dry during the heating season? Float switches can fail, just had one last week that was not functional.
|
|
#12
|
||||
|
||||
|
Quote:
Putting a trap on a pan drain is absurd. The pan drain is there for emergencies. And think about it...what would the pan drain trap do? The pan itself is open into the attic! Be careful about making up your own rules and giving people your own solutions. The next inspector in the house, one who understands the codes, will laugh when he hears the homeowner say, "My inspector said all it needed was a larger trap." 2006 IRC: "M1411.3.1 Auxiliary and secondary drain systems. In addition to the requirements of Section M1411.3, a secondary drain or auxiliary drain pan shall be required for each cooling or evaporator coil where damage to any building components will occur as a result of overflow from the equipment drain pan or stoppage in the condensate drain piping. Such piping shall maintain a minimum horizontal slope in the direction of discharge of not less than 1/8 unit vertical in 12 units horizontal (1-percent slope). Drain piping shall be a minimum of 3/4-inch (19 mm) nominal pipe size. One of the following methods shall be used: 1. An auxiliary drain pan with a separate drain shall be “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com Last edited by jfunderburk; 11/2/10 at 10:04 AM.. |
|
#13
|
||||
|
||||
|
Joe never acceptable is pretty strong words AHJ around here allows connection to a sewer vent in the attic if the trap is considered as a wet trap and the only time a condensate drain trap can be considered as wet is if the furnace is a 90% efficient and produces condensate in the heat mode
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
| Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
The alarm is cool. |
|
#15
|
||||
|
||||
|
I always tell my clients to have the secondary drain hose penetrating an area near the main entry door. This configuration will allow the secondary drainage piping to be monitored on a daily basis. Attic air handler installations should have the secondary drain piping installed out to the soffit area and right over the main entry door. This would drop secondary condensate right in front of the homeowner, alarming them.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Condensation Drain line question | acassady | Inspecting HVAC Systems | 25 | 2/26/12 11:40 AM |
| Condensate drainage to sump pit | gbottomley | Plumbing Inspections | 3 | 3/24/10 10:00 PM |
| Site grading and drainage | wdevries | Canadian Inspectors | 5 | 10/6/09 10:23 PM |
| Options in selecting materials for basement construction | wdevries | Canadian Inspectors | 2 | 8/4/08 1:30 PM |
| shared condensate drainage | dbucknavich | Inspecting HVAC Systems | 1 | 7/15/08 9:37 PM |