Default Condensate Drainage

Heat pump air handler located attic with drip pan. Condensate and pan drain pipes connect to a copper plumbing vent. Quality HVAC work!


condensate-drainage-greenway-189.jpg

condensate-drainage-greenway-187.jpg




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/30/10, 7:06 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Condensate Drainage

wow you don't see cooper vent much now days was it a commercial Building



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #3  
Old 10/30/10, 10:41 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Condensate Drainage

"The secondary condensate port was not plumbed to the attic drain pan. As a result, when the primary drain line becomes clogged, the condensate inside the air handler has no path to escape. It will rise in the air handler cabinet until it finds a seam in which to seep out, and may cause rust inside the cabinet. In the worst case scenario, the water may rise until it travels down a duct and will cause ceiling damage when it escapes out a duct seam. We recommend that the secondary port be plumbed to the bottom of the drain pan. Immediate service is not critical and can wait until the next scheduled maintenance."

condensate-drainage-2nd-port-good-example.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 10/30/10, 12:31 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Condensate Drainage

Joe,

Correct, but the drip pan drain should terminate at a conspicuous location. I also called out the vent pipe connection as non standard.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #5  
Old 10/30/10, 1:02 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Condensate Drainage

Quote:
Originally Posted by jevans View Post
Joe,

Correct, but the drip pan drain should terminate at a conspicuous location. I also called out the vent pipe connection as non standard.
I struggle with that when there is a float switch present. With a float switch, a pan drain isn't even required. But if it's there, it should be installed correctly I suppose. (One solution in your case is to remove the pan drain altogether, which I wouldn't want to do.)



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 10/30/10, 1:21 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Condensate Drainage

So what if there is only one visible drain line, attic installation, and it is at exterior of home?
Attached Thumbnails
condensate-drainage-hpim8207.jpg   condensate-drainage-hpim8213.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #7  
Old 10/30/10, 1:26 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Condensate Drainage

Quote:
Originally Posted by ccurrins View Post
So what if there is only one visible drain line, attic installation, and it is at exterior of home?
If that's the primary, I would certainly call that out as unorthodox. While there is no specific rule against it, it will cause discoloration to the roof and is just generally unsightly.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 10/30/10, 1:31 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Condensate Drainage

Quote:
Originally Posted by jfunderburk View Post
If that's the primary, I would certainly call that out as unorthodox. While there is no specific rule against it, it will cause discoloration to the roof and is just generally unsightly.
So in this setup you wouldn't recommend a secondary?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #9  
Old 10/30/10, 1:53 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Condensate Drainage

Quote:
Originally Posted by ccurrins View Post
So in this setup you wouldn't recommend a secondary?
Where damage may occur, you always need a pan with either a float switch, an auxiliary pan drain, or both.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 10/30/10, 4:08 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Condensate Drainage

Around here its common practice for drain line to run into the sewer lines. With a larger trap on the condesate line, it should not pose an issue unless you have a back up (then there is poo in the coil). But with both lines running into the vent, both drains should have traps on them.

Many times I see just one line, and a float switch.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #11  
Old 10/30/10, 4:33 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Condensate Drainage

What happens if the trap is dry during the heating season? Float switches can fail, just had one last week that was not functional.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #12  
Old 10/30/10, 5:32 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Condensate Drainage

Quote:
Originally Posted by sfogarty View Post
Around here its common practice for drain line to run into the sewer lines. With a larger trap on the condesate line, it should not pose an issue unless you have a back up (then there is poo in the coil). But with both lines running into the vent, both drains should have traps on them.

Many times I see just one line, and a float switch.
Being common does not necessarily equal being acceptable. Any direct discharge like that into a plumbing vent is never acceptable.

Putting a trap on a pan drain is absurd. The pan drain is there for emergencies. And think about it...what would the pan drain trap do? The pan itself is open into the attic!

Be careful about making up your own rules and giving people your own solutions. The next inspector in the house, one who understands the codes, will laugh when he hears the homeowner say, "My inspector said all it needed was a larger trap."

2006 IRC:

"M1411.3.1 Auxiliary and secondary drain systems. In
addition to the requirements of Section M1411.3, a secondary
drain or auxiliary drain pan shall be required for each
cooling or evaporator coil where damage to any building
components will occur as a result of overflow from the
equipment drain pan or stoppage in the condensate drain
piping. Such piping shall maintain a minimum horizontal
slope in the direction of discharge of not less than 1/8 unit
vertical in 12 units horizontal (1-percent slope). Drain piping
shall be a minimum of 3/4-inch (19 mm) nominal pipe
size. One of the following methods shall be used:
1. An auxiliary drain pan with a separate drain shall be
installed under the coils on which condensation will
occur. The auxiliary pan drain shall discharge to a
conspicuous point of disposal to alert occupants in the
event of a stoppage of the primary drain. The pan shall
have a minimum depth of 1.5 inches (38 mm), shall
not be less than 3 inches (76 mm) larger than the unit
or the coil dimensions in width and length and shall be
constructed of corrosion-resistant material. Metallic
pans shall have a minimum thickness of not less than
0.0276-inch (0.7 mm) galvanized sheet metal. Nonmetallic
pans shall have a minimum thickness of not
less than 0.0625 inch (1.6 mm).

2. A separate overflow drain line shall be connected to
the drain pan provided with the equipment. This overflow
drain shall discharge to a conspicuous point of
disposal to alert occupants in the event of a stoppage
of the primary drain. The overflow drain line shall
connect to the drain pan at a higher level than the primary
drain connection.

3. An auxiliary drain pan without a separate drain line
shall be installed under the coils on which condensate
will occur. This pan shall be equipped with a water
level detection device conforming to UL 508 that will
shut off the equipment served prior to overflow of the
pan. The auxiliary drain pan shall be constructed in
accordance with Item 1 of this section.

4. A water level detection device conforming to UL 508
shall be provided that will shut off the equipment
served in the event that the primary drain is blocked.
The device shall be installed in the primary drain line,
the overflow drain line or the equipment-supplied
drain pan, located at a point higher than the primary
drain line connection and below the overflow rim of
such pan."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 11/2/10 at 10:04 AM..
Reply With Quote
  #13  
Old 11/1/10, 10:52 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Condensate Drainage

Joe never acceptable is pretty strong words AHJ around here allows connection to a sewer vent in the attic if the trap is considered as a wet trap and the only time a condensate drain trap can be considered as wet is if the furnace is a 90% efficient and produces condensate in the heat mode



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/2/10, 5:41 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Condensate Drainage

Quote:
Originally Posted by jevans View Post
Heat pump air handler located attic with drip pan. Condensate and pan drain pipes connect to a copper plumbing vent. Quality HVAC work!


Attachment 39854

Attachment 39855
As shown, the connection to the Vent pipe is not allowed. That is not an approved way to connect to a Vent Pipe.

The alarm is cool.
Reply With Quote
  #15  
Old 11/2/10, 7:50 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Condensate Drainage

I always tell my clients to have the secondary drain hose penetrating an area near the main entry door. This configuration will allow the secondary drainage piping to be monitored on a daily basis. Attic air handler installations should have the secondary drain piping installed out to the soffit area and right over the main entry door. This would drop secondary condensate right in front of the homeowner, alarming them.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Condensation Drain line question acassady Inspecting HVAC Systems 25 2/26/12 11:40 AM
Condensate drainage to sump pit gbottomley Plumbing Inspections 3 3/24/10 10:00 PM
Site grading and drainage wdevries Canadian Inspectors 5 10/6/09 10:23 PM
Options in selecting materials for basement construction wdevries Canadian Inspectors 2 8/4/08 1:30 PM
shared condensate drainage dbucknavich Inspecting HVAC Systems 1 7/15/08 9:37 PM


All times are GMT -4. The time now is 11:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts