Default Condensate in the Drip Pan

I was checking the drip pan for the evaporator coil and saw condensate. Is it ever normal to see condensate in the drip pan?
Attached Thumbnails
condensate-drip-pan-i9.jpg  
Reply With Quote
  #2  
Old 7/20/06, 7:44 AM
away away is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Aledo, TX
Posts: 229
Default Re: Condensate in the Drip Pan

Not usually. There is no insulation on the suction line so it could just be from moisture condensing on the line and dripping down into the pan. From the limited area shown in the photo, the rust in the pan seems to be concentrated just under where the lineset enters the cabinet.



Andrew Way
Keystone Residential Inspection Services PLLC
www.keystoneinspections.com
Reply With Quote
  #3  
Old 7/20/06, 8:11 AM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Condensate in the Drip Pan

I agree with Andrew Uninsulated suction line will sweat like a cold coke can (or beer, or margrita glass) at a picnic. If the system is working properly.

Last edited by bgraham; 7/20/06 at 1:27 PM..
Reply With Quote
  #4  
Old 7/20/06, 8:47 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Condensate in the Drip Pan

Quote:
Originally Posted by Skip Erwin
I was checking the drip pan for the evaporator coil and saw condensate. Is it ever normal to see condensate in the drip pan?
This is a secondary drip pan that should never have signs of condensation build-up.

I concur with Andrew.
Reply With Quote
  #5  
Old 7/20/06, 11:45 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Condensate in the Drip Pan

You should never be able to see the suction refrigerant pipe!

A 2" section of uninsulated pipe next to the a/c cased coil will cause this amount of water.

All joints must be glued and sealed.
The use metal tape for this repair (which often happens around here) is not acceptable as the foil tape conducts heat as sweats like the pipe.

The insulation on the pipe is not to prevent thermal transfer, but to prevent contact with the air and the condensate that occurs.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
1 condensate line...... Scott Schultz Inspecting HVAC Systems 2 11/4/07 6:18 AM
Drip legs Scott Schultz Plumbing Inspections 7 3/31/07 7:46 AM
Condensate piping dmacy Inspecting HVAC Systems 15 3/13/07 12:17 AM
Lack of aluminum drip edge Brenda Exterior Inspections 26 6/16/06 7:28 AM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 7:59 AM


All times are GMT -4. The time now is 6:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts