Read past posts, and I'm still confused. Is this proper, allowed, etc. etc. ?????? If wrong, how would you write it up?
Note- It was a high efficiency furnace. |
| Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Quote:
It cannot be connected directly. It must be indirect with an air gap. Recommend correction. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#3
|
||||
|
||||
|
The problem is that the trap will dry out in the winter time unless it's a high-efficiency furnace that produces condensate in the heating mode.
The trap must be a wet trap design, meaning that the trap will remain sealed by some water source, other than the HVAC system. Is the furnace an up flow or down flow configuration? Up flow causes positive air pressure during operation, down flow causes negative pressure and will suck sewer gases into the air handling system and distribute them throughout the house. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#4
|
||||
|
||||
|
Nothing in code against it, but indirect waste receptors are not recommended for crawl spaces. Releases humidity into the already humid air there.
Recommend that it terminate outdoors 6 to 12 inches above grade where it can be routinely monitored. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#5
|
|||
|
|||
|
The international mechanical code refers to manufacturers installation instructions.
|
|
#6
|
||||
|
||||
|
Please Note:
rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The correction should be determined by the specialist. Was the furnace in the crawl? |
|
#7
|
||||
|
||||
|
That line looks huge. Looks more like a waste pipe. A typical condensation line is only 1 inch.
I normally see primary condensation lines terminating next to the condenser. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| A/C drain line question | rhorton | Inspecting HVAC Systems | 12 | 9/4/08 8:19 PM |
| near correct condensate drain | bking | Inspecting HVAC Systems | 2 | 9/19/07 1:51 PM |
| If the primary condensate drain fails... | jfunderburk | Inspecting HVAC Systems | 2 | 3/6/07 2:47 PM |
| TPRV line and condensate line marriage | ccarrington | Plumbing Inspections | 3 | 4/29/06 7:59 AM |
| Dishwasher Drain Line | msimmons | Plumbing Inspections | 9 | 1/19/06 11:27 AM |