Default Condensate piping

In the recent Nachi HVAC class the instuctor talked about condensate lines.

The photo shows a high efficiency furnace with the vent condensate and A/C condensate.

Shouldnt there be a trap at the lower pipe? Is there not the possability that the A/C condenstae could flow back into the furnace threw the vent condensate pipe.
Attached Thumbnails
condensate-piping-93207-062-small-.jpg.jpg
Views:	461
Size:	25.5 KB
ID:	9939   condensate-piping-93207-064-small-.jpg.jpg
Views:	507
Size:	42.6 KB
ID:	9940  
Reply With Quote
  #2  
Old 3/12/07, 7:36 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Condensate piping

The trap for that line is, typically, inside the furnace cabinet.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 3/12/07, 7:37 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Condensate piping

Isn't the lower pipe connected to the secondary drip pan?
Reply With Quote
  #4  
Old 3/12/07, 7:42 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Condensate piping

Quote:
Originally Posted by lkage
The trap for that line is, typically, inside the furnace cabinet.
There is a small plastic tube between the condensate pipe and the draft induced fan components. Is this an acceptable install.

I just wanted to make sure. At the NACHI seminar there were all sorts of issues with the condensate pipes.
Reply With Quote
  #5  
Old 3/12/07, 7:44 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Condensate piping

Quote:
Originally Posted by bkelly2
Isn't the lower pipe connected to the secondary drip pan?
I believe it's for the vent piping.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 3/12/07, 7:53 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Condensate piping

Quote:
Originally Posted by dmacy
There is a small plastic tube between the condensate pipe and the draft induced fan components. Is this an acceptable install.

I just wanted to make sure. At the NACHI seminar there were all sorts of issues with the condensate pipes.
I'm not following you, David...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 3/12/07, 8:03 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Condensate piping

It looks like a nice compliant install to me.
Reply With Quote
  #8  
Old 3/12/07, 8:20 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Condensate piping

Quote:
Originally Posted by Marc D. Shunk
It looks like a nice compliant install to me.
I thought the same thing. It was the seminar that I went to. I wish I knew what the instuctor knows.
Reply With Quote
  #9  
Old 3/12/07, 8:39 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Condensate piping

Quote:
Originally Posted by dmacy
I thought the same thing. It was the seminar that I went to. I wish I knew what the instuctor knows.
Trap or no trap on the furnace condensate line, if the downsream line becomes clogged, the AC condensate can backup into the furnace. The only way to eliminate that possibility is to run a seperate line for each to the open receptor in the floor, or to run each seperately to an air gap then run one line to the open receptor.
Reply With Quote
  #10  
Old 3/12/07, 8:54 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Condensate piping

Quote:
Originally Posted by Marc D. Shunk
Trap or no trap on the furnace condensate line, if the downsream line becomes clogged, the AC condensate can backup into the furnace. The only way to eliminate that possibility is to run a seperate line for each to the open receptor in the floor, or to run each seperately to an air gap then run one line to the open receptor.
Now I am confused. Is this install acceptable or should a second line be added?
Reply With Quote
  #11  
Old 3/12/07, 8:57 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Condensate piping

Quote:
Originally Posted by dmacy
Now I am confused. Is this install acceptable or should a second line be added?
I case you're asking me, I have no idea. I was just thinking out loud. I'm not a home inspector. I just have a fat head.
Reply With Quote
  #12  
Old 3/12/07, 9:05 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Condensate piping

Quote:
Originally Posted by dmacy
Now I am confused. Is this install acceptable or should a second line be added?
Who is the manufacturer you can probably find an installation guide on the web?
Reply With Quote
  #13  
Old 3/12/07, 9:07 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Condensate piping

Quote:
Originally Posted by dmacy
In the recent Nachi HVAC class the instuctor talked about condensate lines.

The photo shows a high efficiency furnace with the vent condensate and A/C condensate.

Shouldnt there be a trap at the lower pipe? Is there not the possability that the A/C condenstae could flow back into the furnace threw the vent condensate pipe.
I don't mean to hog this thread but you guys are talking my language I can not help myself I'm addicted hope you don't mind.

The piping that I see in the Pic is traveling to an open floor drain that resolves all of any issues that may arise with condensate drainage. The pipe is required to have an air gap which it has at the floor drain. Most of the high efficiency furnaces have a built in trap for the vent or an open ended hose that drains into the condensate line.

My big concern is when I see the condensate hard piped to the sewer, trap or no trap on the older furnaces because these traps go dry when in the heat mode allowing sewer gas into the air stream of the furnace.

On the high efficiency furnaces where water is being discharged the year round down these drains, traps are required. I only write up high efficiency furnaces if the condensate does not have a air gap or a P-trap and I look for one or the other.

I see nothing wrong in your Pics but I can not see everything from here.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #14  
Old 3/12/07, 9:20 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Condensate piping

Quote:
Originally Posted by cbottger
I don't mean to hog this thread but you guys are talking my language I can not help myself I'm addicted hope you don't mind.

The piping that I see in the Pic is traveling to an open floor drain that resolves all of any issues that may arise with condensate drainage. The pipe is required to have an air gap which it has at the floor drain. Most of the high efficiency furnaces have a built in trap for the vent or an open ended hose that drains into the condensate line.

My big concern is when I see the condensate hard piped to the sewer, trap or no trap on the older furnaces because these traps go dry when in the heat mode allowing sewer gas into the air stream of the furnace.

On the high efficiency furnaces where water is being discharged the year round down these drains, traps are required. I only write up high efficiency furnaces if the condensate does not have a air gap or a P-trap and I look for one or the other.

I see nothing wrong in your Pics but I can not see everything from here.
Thanks, You have cleared my clouded head.
Attached Thumbnails
condensate-piping-93207-059-small-.jpg.jpg
Views:	102
Size:	41.7 KB
ID:	9951  
Reply With Quote
  #15  
Old 3/12/07, 9:40 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Condensate piping

My comments were based on the theory that any condensate snot at either of the yellow arrows would cause AC condensate to back up into the furnace. I know that it remains quite normal for both condensate drains to share common pipework.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Bonding both hot and hold supply pipes kshepard Plumbing Inspections 22 5/4/08 8:00 AM
1 condensate line...... Scott Schultz Inspecting HVAC Systems 2 11/4/07 6:18 AM
Bonding Piping 101....Good To Know ! pabernathy Electrical Inspections 37 4/28/07 11:25 AM


All times are GMT -4. The time now is 6:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts