Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information
Send a message via Yahoo to jfunderburk
Default Condensate pump in the attic

First time I've seen this in 4 years. Last week I saw it twice. HVAC condensate pumps in the attic. Neither had the pump in a drip pan. Bad idea? Poor design? What are your thoughts?

This is what I said about it:

"Condensation from the attic unit evaporator coil is pumped to the exterior. Although this may be permissible, we consider it to be a poor design. It is highly unusual and rarely seen. This mechanical pump will eventually fail and when that happens the reservoir may overflow and may damage the ceilings below, particularly if the pump is not in the drip pan or wired to shut down the HVAC system. We recommend that this installation be evaluated by a licensed and competent HVAC contractor and replaced with a conventional gravity flow condensate drain if practical."



Joe Funderburk
Alpha & Omega Home Inspections, LLC
Hickory Grove, SC
NACHI ID: NACHI05120170
www.aohomeinspection.com
Reply With Quote
Find an InterNACHI certified District Of Columbia Home Inspector (and anywhere else in North America)
  #2  
Old 9/15/08, 11:34 AM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 416
Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information
Default Re: Condensate pump in the attic

Some of those pumps (maybe all) have a float (or some other means) to disable the furnace when the resivour fills too much. I comment on whether it looks like it is set up to do that (extra thermostat type wires going back to the furnace) or not. They can also install a floodstop device if the pump does not have the shut-off capability.


Edit: Here is a link to a pump. It looks like the overflow switch is an option.
http://www.fieldcontrols.com/pdfs/CONDENpump.PDF



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr
"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold

Last edited by rbrady; 9/15/08 at 12:09 PM. Reason: More information
Reply With Quote
  #3  
Old 9/15/08, 11:55 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,653
David A. Andersen .
Default Re: Condensate pump in the attic

Hello Joe,
Condensate pumps on the upper floors pumping "downward" is a waste of resources.

The location of the pump (which is susceptible to failure) is a consideration when located above the finished space.

The condensate pump shut off control should be employed to shut down the HVAC system "when" failure occurs.

One thing you didn't mention was if there was a safety switch on the drip pan. There should also be a switch located here (wired in series). Condensate pump failure is not the only cause of condensate flooding.

I don't necessarily agree with calling for further evaluation (as this condition is no more catastrophic than any other configuration without a specific code requirement). I would recommend "monitoring the condition". If the client is concerned, they can change it. You're covering all the bases, I just report things a little differently.





David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #4  
Old 9/15/08, 12:04 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,135
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: Condensate pump in the attic

Quote:
Originally Posted by jfunderburk View Post
First time I've seen this in 4 years. Last week I saw it twice. HVAC condensate pumps in the attic. Neither had the pump in a drip pan. Bad idea? Poor design? What are your thoughts?

This is what I said about it:

"Condensation from the attic unit evaporator coil is pumped to the exterior. Although this may be permissible, we consider it to be a poor design. It is highly unusual and rarely seen. This mechanical pump will eventually fail and when that happens the reservoir may overflow and may damage the ceilings below, particularly if the pump is not in the drip pan or wired to shut down the HVAC system. We recommend that this installation be evaluated by a licensed and competent HVAC contractor and replaced with a conventional gravity flow condensate drain if practical."
Was the pump in the attic alongside the air handler? If so, I don't see an issue with this set-up. I look for a pump, a secondary pan with a hard-wired flood stop device (there are many) which is designed to detect water in the secondary pan and will automatically shut down the air handler if it senses water in the secondary pan.

Last edited by dvalley; 9/15/08 at 12:08 PM.
Reply With Quote
  #5  
Old 9/15/08, 12:07 PM
Joe D. Funderburk's Avatar
Joe D. Funderburk Joe D. Funderburk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Rock Hill, SC
Posts: 1,940
Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information
Send a message via Yahoo to jfunderburk
Default Re: Condensate pump in the attic

Quote:
Originally Posted by dandersen View Post
[size=2]One thing you didn't mention was if there was a safety switch on the drip pan.

You mean this pan?

091008 122.JPG 091008 121.JPG



Joe Funderburk
Alpha & Omega Home Inspections, LLC
Hickory Grove, SC
NACHI ID: NACHI05120170
www.aohomeinspection.com
Reply With Quote
  #6  
Old 9/15/08, 12:15 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,135
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: Condensate pump in the attic

Quote:
Originally Posted by jfunderburk View Post
I can see that the flood stop device is wired (second pic) but seeing that the secondary pan drain hole will allow all condensate to drain onto the ceiling below. This simply needs a drainage pipe installed which will run out into the soffit area.
Reply With Quote
  #7  
Old 9/15/08, 12:19 PM
Joe D. Funderburk's Avatar
Joe D. Funderburk Joe D. Funderburk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Rock Hill, SC
Posts: 1,940
Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information
Send a message via Yahoo to jfunderburk
Default Re: Condensate pump in the attic

David, thanks for all your help. Shouldn't the pan be moved over a tad? Seems like it's right even with the evaporator coil seam.



Joe Funderburk
Alpha & Omega Home Inspections, LLC
Hickory Grove, SC
NACHI ID: NACHI05120170
www.aohomeinspection.com
Reply With Quote
  #8  
Old 9/15/08, 12:26 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,135
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: Condensate pump in the attic

Quote:
Originally Posted by jfunderburk View Post
David, thanks for all your help. Shouldn't the pan be moved over a tad? Seems like it's right even with the evaporator coil seam.
Joe,

If the secondary pan is smaller than the unit itself, the pan should be upgraded to be the same size or a tad larger than the unit that it is under.

I'd rather see the pan sized accordingly rather than moving it and taking chances on the drip location. Condensate will drip at all locations (from the primary pan area) and having the secondary pan sized accordingly will alleviate unexpected drips onto the ceiling below.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Condensate pump instead of drain piping lfoster HVAC 7 6/22/08 4:16 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Building Science- research from respected sources Brian A. MacNeish Ancillary Services & Additional Topics 12 2/13/08 12:33 PM


All times are GMT -4. The time now is 5:41 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics