Got a question about the vent off the condensation "T" while running the Central Air. How much air should be coming out of this?
Got a friend that says his blows quite of bit? New house.
Thanks
Andy B
Reply With Quote
  #2  
Old 8/3/06, 12:27 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: Condensation drain vent

Thats probably not a vent on the condensate drain line, and there shouldn't be much air coming out. Should be a tee after a trap (as long as it's not tied into a stack vent ... which shouldn't be done anyway) with a short open vert pipe that comes up above the primary drain pan level as a cleanout. They may have put the cleanout tee before the trap without a loose cap, or not enough condensate is being generated to seal the air flow.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #3  
Old 8/3/06, 3:20 PM
Andy T. Bishop Andy T. Bishop is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Allegan, MI
Posts: 311
Default Re: Condensation drain vent

It is the small 1/2 pvc line that comes out the furnace, tees up and down. Down to drain the condensate and up to vent.
So what you are saying is it doesn't condensate enough? How do you get it to condensate more? Burner/gas setting?
Thanks!
Reply With Quote
  #4  
Old 8/3/06, 3:21 PM
Andy T. Bishop Andy T. Bishop is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Allegan, MI
Posts: 311
Default Re: Condensation drain vent

I will try and get a pic.
Reply With Quote
  #5  
Old 8/3/06, 4:57 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,753
Default Re: Condensation drain vent

Robert is most likely correct, a picture would help



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #6  
Old 8/3/06, 8:36 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Condensation drain vent

Are all the vents open?

I agree with Bob.
Reply With Quote
  #7  
Old 8/3/06, 10:18 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: Condensation drain vent

A pic would be helpful. And are you talking about the condensate drain line for a central air conditioner (my initial reaction) or a high efficiency forced air furnace?

In any event condensate is usually piped to daylight or a plumbing fixture tailpiece (before the fixture trap so sewer gas doesn't come out of the condensate lines ... any why you shouldn't just tap a condensate line directly into a sewer waste sack or vent stack like in an attic). To keep air from blowing out of the condensate lines there is usually a trap in the line. It's not required to vent this trap like you would plumbing fixture waste line traps ... since there shouldn't be the risk of sewer gas backing up through the lines, and there generally isn't enough flow/pressure to suck the condensate trap dry.

Although it's not required, many consider it good practice to install an open or removable section of pipe that comes up from the condensate line in order to clean out the lines if they appear to be clogged (aka condensate "cleanout"). This can be an open section of pipe after the condensate trap, or a removable capped section of pipe if it's before the trap. That way conditioned air will not blow out of the condensate cleanout.

So what I think you are describing is actually a cleanout for the condensate lines, and not a vent. And it shouldn't be blowing any air at all with a trap in the line and a correctly installed condensate cleanout.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #8  
Old 8/4/06, 11:55 AM
Andy T. Bishop Andy T. Bishop is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Allegan, MI
Posts: 311
Default Re: Condensation drain vent

Here is the pic. It is blowing quite a bit.
Thanks
Attached Thumbnails
condensation-drain-vent-img_1354.jpg  
Reply With Quote
  #9  
Old 8/4/06, 2:07 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 836
Send a message via Skype™ to pbolliger
Default Re: Condensation drain vent

"Houston we have a problem"

What you got there is a sealed burner "Condensing" Category 4 FAU ... I see a "tee" at the bottom of the "exhaust" that is connected directly into a condensation drain line... Hmmm Think about this .. That pressure is coming from the blower motor out through the "tee" fitting at the top. Why is it done that way???...

This is a case of MFG installation instructions review and possible incorrect installation practice..
I have never seen such a large direct connection from the exhaust to the conensate drain line like that... maybe a small drain tube but never that Huge "tee"...

Anyone.
Reply With Quote
  #10  
Old 8/4/06, 2:59 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 836
Send a message via Skype™ to pbolliger
Default Re: Condensation drain vent

Check this out:
Attached Thumbnails
condensation-drain-vent-furnacventrs.gif  
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Capped drain line vent rdawes HVAC 3 4/21/07 8:00 PM
Air admittance valves everywhere apfaff Plumbing 13 4/16/07 10:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Misc. Discussion 8 1/25/07 6:22 PM


All times are GMT -4. The time now is 3:40 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts