International Association of Certified Home Inspectors
|
|||||||
| HVAC Topics include heating, venting, and air conditioning. |
![]() |
|
|
LinkBack | Thread Tools | Display Modes |
|
#1
|
|||
|
|||
|
Please Note:
Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
I've come across this problem a few times recently. Ceiling mounted air handler with dripping of condensation from the refregertant line fittings onto the insulation of the coverpanel. What can be done to limit the condensation without affecting the effiency of the unit.
www.mauihomeinspections.com |
| Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Insulate it with closed cell foam tape designed for the purpose.
Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Certified Infrared Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#3
|
||||
|
||||
|
Cork press tape is better the foam pops loose over time
Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#4
|
|||
|
|||
|
Please Note:
Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#5
|
||||
|
||||
|
That black sticky stuff for reefers is best, but is hell to get off over time.
Just don't seal off the nut at the bottom of the valve. Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Certified Infrared Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#6
|
|||
|
|||
|
Please Note:
Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
This seems to be a design or install defect as I never see any insulation wrapped around these areas and every one I inspect is dripping. My concern is these units are installed in 150-200 unit condo projects. Where would I find install instructions that spell out how to handle this issue.
www.mauihomeinspections.com |
|
#7
|
||||
|
||||
|
Copeland Blue Book.
Any TXV Mfg, Sporland etc... The problem is the air passing by the valve is excessively humid. It is right next to the fans! It just needs some thermal tape installed. Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Certified Infrared Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
![]() |
| Thread Tools | |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Moisture Management | mcyr | Exterior | 15 | 9/8/08 1:11 PM |
| Building Science- research from respected sources | Brian A. MacNeish | Ancillary Services & Additional Topics | 12 | 2/13/08 12:33 PM |
| Cutler-Hammer CH breaker issue | Marc D. Shunk | Electrical | 4 | 5/27/07 3:04 PM |