Default condensation issue at TEV

I've come across this problem a few times recently. Ceiling mounted air handler with dripping of condensation from the refregertant line fittings onto the insulation of the coverpanel. What can be done to limit the condensation without affecting the effiency of the unit.

www.mauihomeinspections.com
Attached Thumbnails
condensation-issue-tev-ceiling1715.jpg   condensation-issue-tev-ceiling1714.jpg  
Reply With Quote
  #2  
Old 9/23/08, 7:46 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: condensation issue at TEV

Insulate it with closed cell foam tape designed for the purpose.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 9/23/08, 10:50 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: condensation issue at TEV

Cork press tape is better the foam pops loose over time



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 9/24/08, 2:01 AM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: condensation issue at TEV

Thanks

www.mauihomeinspections.com
Reply With Quote
  #5  
Old 9/24/08, 12:40 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: condensation issue at TEV

That black sticky stuff for reefers is best, but is hell to get off over time.

Just don't seal off the nut at the bottom of the valve.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 9/24/08, 2:03 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: condensation issue at TEV

This seems to be a design or install defect as I never see any insulation wrapped around these areas and every one I inspect is dripping. My concern is these units are installed in 150-200 unit condo projects. Where would I find install instructions that spell out how to handle this issue.

www.mauihomeinspections.com
Reply With Quote
  #7  
Old 9/24/08, 2:58 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: condensation issue at TEV

Copeland Blue Book.

Any TXV Mfg, Sporland etc...

The problem is the air passing by the valve is excessively humid. It is right next to the fans!

It just needs some thermal tape installed.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Building Science- research from respected sources Brian A. MacNeish Ancillary Inspection Services & Additional Topics 17 7/12/11 6:31 AM
Moisture Management mcyr Exterior Inspections 15 9/8/08 12:11 PM
Cutler-Hammer CH breaker issue Marc D. Shunk Electrical Inspections 4 5/27/07 2:04 PM


All times are GMT -4. The time now is 11:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts