Default Condenser placement

What do you folks think of the placement of the condensers on this 600k new home? The buyer called the builder after receiving my report and the builder assured them it would be o.k. One of the reasons the buyer purchased a new home was that they couldn't keep their old home at 80 degrees when it was 110 outside.
Attached Images
File Type: jpg Condensers.jpg (91.0 KB, 61 views)
Reply With Quote
  #2  
Old 4/19/07, 9:06 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,526
Brian E. Kelly .
Default Re: Condenser placement

These guidelines say their unit only needs 10" of clearance Gary, as I believe the send the hot air up and away.

http://www.thermopride.com/pdfs/PremiereACISManual.pdf





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #3  
Old 4/20/07, 12:01 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Condenser placement

Quote:
Originally Posted by gheller
What do you folks think of the placement of the condensers on this 600k new home? The buyer called the builder after receiving my report and the builder assured them it would be o.k. One of the reasons the buyer purchased a new home was that they couldn't keep their old home at 80 degrees when it was 110 outside.
Those units will run like any other setting where they are but you will be decreasing the life expectancy considerable as there are no prevailing winds to carry the heat away operating those unit in that box is not the smartest thing to do. Heat is what kills the largest % of A/C units and those two unit will be operating at a higher head pressure when it really gets hot. Just the reflection of the sun off of the two structures will be tremendous. I see folks build fences, plant all kinds of crazy bushes around the units because they think they are not pretty. They are just shooting themselves in the foot. My personal opinion about the location bad choice.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #4  
Old 4/20/07, 12:31 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,426
Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information
Default Re: Condenser placement

Charley, I agree BUT many manufacturers only recommend 12" clearance or less. So at that point it is just our opinion.
Reply With Quote
  #5  
Old 4/20/07, 3:52 AM
Rick McCullough Rick McCullough is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Arvada, CO
Posts: 238
Rick McCullough has had a little positive feedback
Default Re: Condenser placement

Quote:
Originally Posted by dbowers
Charley, I agree BUT many manufacturers only recommend 12" clearance or less. So at that point it is just our opinion.
And what do you offer if NOT your Opinion?
Reply With Quote
  #6  
Old 4/20/07, 10:08 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Condenser placement

Quote:
Originally Posted by dbowers
Charley, I agree BUT many manufacturers only recommend 12" clearance or less. So at that point it is just our opinion.
Dan; There is just not much thought put into what some folks do when installing equipment yes there is not anything that can generally be done about things such as this one. I would of just made a comment on it and moved on.

I have a infamous saying about proper cooling of these units. I look the owner in the eye and ask. If you owned a new Caddy would you place a piece of cardboard in front of the radiator in July and make a long drive. I just get this glazed over look and usually no comment.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #7  
Old 4/20/07, 8:48 PM
bbenjamin bbenjamin is offline
New User
 
Join Date: Feb 2007
Location: Round O, SC
Posts: 45
bbenjamin hasn't had much positive or negative feedback
Please Note: bbenjamin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Condenser placement

I said it once I will say it again, "You can get anyone to do your air conditioning/heating/gas work that doesn't mean it will be done correctly and in accordance to code."

Their should be enough space for the serviceman/woman to be able to work on the unit. This is why I would have failed it. Honestly how many small service techs have you seen. Seriously split system condensers are designed to take in outside air and also be cooled by that same outside air. In this particular set-up neither of which is at its optimum effeciency.
Reply With Quote
  #8  
Old 4/20/07, 11:52 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Condenser placement

Quote:
Originally Posted by bbenjamin
I said it once I will say it again, "You can get anyone to do your air conditioning/heating/gas work that doesn't mean it will be done correctly and in accordance to code."

Their should be enough space for the serviceman/woman to be able to work on the unit. This is why I would have failed it. Honestly how many small service techs have you seen. Seriously split system condensers are designed to take in outside air and also be cooled by that same outside air. In this particular set-up neither of which is at its optimum effeciency.
Bruce how could you fail it. I operate on the theory does the unit perform its intended function at the time of inspection.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #9  
Old 4/21/07, 2:47 AM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 6,480
Robert E. Elliott .
Default Re: Condenser placement

Hi ...Bob Elliott here and my first time posting on the NACHI board.Just a quick intro.If you fall in love you can check me out at one of my sites (lol)
It's getting to be around 12:30am here in Chicago.I am a local NACHI chicago member,and since we had an HVAC expert at the meeting last night just thought I would check out the board.
Can not resist commenting that you guys are disagreeing as you agree at the same time.
If you want to get sued or bad rapped go ahead and fail the thing ,but the obvious answer would come in the way of FACT<OPINION >GUIDANCE.
Fact:The unit meets manufacturers specs
Opinion:I feel that there is a chance the unit may not run up to specs due to the fact that even though the manufacture has determined 10"to be enough clearance they may be refering only to a minimum standard reguarding one side and not two so I recommend you have a qualified mechanical contractor certifiy it"s placement.You said your piece and covered your ***.Said and done.
Reply With Quote
  #10  
Old 4/21/07, 3:03 AM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 6,480
Robert E. Elliott .
Default Re: Condenser placement

Regarding the above message I am a member so do not believe everything the software tells you.
Reply With Quote
  #11  
Old 4/21/07, 11:25 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,332
William E. Siegel is often very helpful William E. Siegel is often very helpful
Default Re: Condenser placement

From what I can see looking at that picture, it looks like it meets the manufacturer installation recommdations. Do you have the measurments on both sides of the units.

"One of the reasons the buyer purchased a new home was that they couldn't keep their old home at 80 degrees when it was 110 outside." Must have been an awful strange home or a bad AC. It think there were other reasons they were moving.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
HVAC condenser clearances cfolsom HVAC 7 11/22/07 4:03 PM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 8 9/9/07 8:02 PM
oily reside on condenser valve Mel Olinsky HVAC 2 7/13/07 8:01 PM
Moisture on pad at heat pump condenser lfoster HVAC 3 5/2/07 6:38 PM
Discoloration on condenser fins ? lfoster HVAC 5 5/2/07 9:17 AM


All times are GMT -4. The time now is 7:39 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics