Default Confused by air intake and flue setup

Sears Comfortmaker
cat 1
Direct vent
Has induced vent in Unit
also has a damper at base of B vent
also has additional power type vent installed in line
approx 15 foot run
goes out side wall in basement

What gives as far as why additional power venting and can this be an issue?
also the air intake is like a cat 4
never seen this on the 11 year old Unit before.
confused-air-intake-and-flue-setup-cat1.jpgconfused-air-intake-and-flue-setup-cat2.jpgconfused-air-intake-and-flue-setup-cat3.jpgconfused-air-intake-and-flue-setup-cat4.jpg

Last edited by relliott; 8/6/09 at 4:08 PM..
Reply With Quote
Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America)
  #2  
Old 8/6/09, 2:14 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

confused-air-intake-and-flue-setup-dsc01965-medium-.jpg.JPG
Views:	60
Size:	84.5 KB
ID:	30650confused-air-intake-and-flue-setup-air-intake-medium-.jpg.JPG
Views:	65
Size:	83.2 KB
ID:	30648confused-air-intake-and-flue-setup-dsc02095.jpgMore pics

Last edited by relliott; 8/6/09 at 3:16 PM..
Reply With Quote
  #3  
Old 8/6/09, 4:33 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Confused by air intake and flue setup

Is required when: "line approx 15 foot run,goes out side wall in basement"



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #4  
Old 8/6/09, 4:52 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

Quote:
Originally Posted by dandersen View Post
Is required when: "line approx 15 foot run,goes out side wall in basement"
What is required David ?

It has a draft inducer built in to the Unit .
Are you saying additional fan is required?

also what about that air intake?
should it be piped at least to outside of the Unit ?
Reply With Quote
  #5  
Old 8/6/09, 5:14 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

Quote:
Originally Posted by relliott View Post
What gives as far as why additional power venting and can this be an issue?
I think he means that...
Quote:
Originally Posted by relliott View Post

Has induced vent in Unit
also has a damper at base of B vent
also has additional power type vent installed in line
Quote:
Originally Posted by dandersen View Post
Is required when: "line approx 15 foot run,goes out side wall in basement"
HTH
Reply With Quote
  #6  
Old 8/6/09, 5:15 PM
Jeff Merritt Jeff Merritt is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Chicago, IL
Posts: 1,103
Default Re: Confused by air intake and flue setup

Bob, A cat I with draft inducer can only push 15 -20 feet tops, depending on the angle how many elbows, the additional blower assembly at the end of the run finished getting the burned fuel out of the FAU/building, some require a damper, You should have just called.
Reply With Quote
  #7  
Old 8/6/09, 5:20 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

Quote:
Originally Posted by jmerritt1 View Post
Bob, A cat I with draft inducer can only push 15 -20 feet tops, depending on the angle how many elbows, the additional blower assembly at the end of the run finished getting the burned fuel out of the FAU/building, some require a damper, You should have just called.
Got any links to info.

Called who?

I still need to call it out as it does have a slightly dropped elbow besides the hole.
confused-air-intake-and-flue-setup-elbow.jpg

What about that air intake.
It almost looks like a cat 4.
Reply With Quote
  #8  
Old 8/6/09, 7:11 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Confused by air intake and flue setup

Bob,

Sorry I'm flooded with calls...

The local codes interpret sidewall venting as needing an induced draft.

You have long distance and a side wall application.

Whether it's right ,wrong or necessary, they may have required it.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #9  
Old 8/6/09, 7:27 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

There is information on Field Controls web site http://www.fieldcontrols.com/venting.php
and Tjernlund's web site http://www.tjernlund.com/gassidewall.htm

These are the systems installed to replace the recalled HTPV High Temperature Plastic Vent systems. And is also to be used where sidewall venting is the only option and is not for use with condensing furnaces.
Reply With Quote
  #10  
Old 8/6/09, 7:45 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

Quote:
Originally Posted by Gary Reecher View Post
There is information on Field Controls web site http://www.fieldcontrols.com/venting.php
and Tjernlund's web site http://www.tjernlund.com/gassidewall.htm

These are the systems installed to replace the recalled HTPV High Temperature Plastic Vent systems. And is also to be used where sidewall venting is the only option and is not for use with condensing furnaces.
Thanks for the links but what about that air intake?
I know it is ok mto be drawing inside air but this is drawing inside the cabinet Unit air. (no pipe)
Reply With Quote
  #11  
Old 8/6/09, 8:51 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

The installation instructions will have to be checked. Normally not an issue unless lack of combustion air is an issue. Which can be verified by a combustion test of flue gases and draft measurement. There are air louvers on the front of the furnace and that is where combustion air is drawn into the furnace from the mechanical room. If combustion air is adequate in the mechanical room combustion test should be good.
Reply With Quote
  #12  
Old 8/6/09, 8:59 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

Quote:
Originally Posted by Gary Reecher View Post
The installation instructions will have to be checked. Normally not an issue unless lack of combustion air is an issue. Which can be verified by a combustion test of flue gases and draft measurement. There are air louvers on the front of the furnace and that is where combustion air is drawn into the furnace from the mechanical room. If combustion air is adequate in the mechanical room combustion test should be good.
Yes I know that but issue is if it can be drawn from inside the cabinet .
There is not even a short section of sch 40 .(see pic)
Reply With Quote
  #13  
Old 8/6/09, 11:14 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

My first sentence. The manufacturers installation instruction must be checked.
Reply With Quote
Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America)
  #14  
Old 8/6/09, 11:17 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

Quote:
Originally Posted by Gary Reecher View Post
My first sentence. The manufacturers installation instruction must be checked.
Difficult to obtain at 11 years old.
I tried.
Reply With Quote
  #15  
Old 8/6/09, 11:54 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Confused by air intake and flue setup

What is the manufacturer and model number?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cracked flue tile bknowlton Inspecting HVAC Systems 6 2/2/07 12:37 AM


All times are GMT -4. The time now is 12:52 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts