Default Constant blower

Unit is BDP (Carrier) model 394GAW060125 furnace and when I raised thermostat, the blower immediately came on and continued to run without delay for heat exchanger to heat up. Can it be thermostat problem or deeper?



STATEN ISLAND HOME INSPECTIONS
WWW.SIHOMEINSPECT.COM
LIC.#16000002260
718-987-1759
917-797-3917
SERVING DOWNSTATE NEW YORK

Last edited by lcannizzaro; 10/20/08 at 7:35 PM..
Reply With Quote
  #2  
Old 10/21/08, 12:35 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: Constant blower

Quote:
Originally Posted by lcannizzaro View Post
Unit is BDP (Carrier) model 394GAW060125 furnace and when I raised thermostat, the blower immediately came on and continued to run without delay for heat exchanger to heat up. Can it be thermostat problem or deeper?
No help for you yet so I will take a shot in the dark is this a new install first time for the furnace use. If so most of the newer units have DIP switches on the control panel that have to be set for proper operation. If it is not a new install yes it could be as simple as a stat problem but most likely would be in the control board itself.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 10/21/08, 6:55 AM
Louis Cannizzaro Louis Cannizzaro is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Staten Island, NY
Posts: 127
Default Re: Constant blower

Thanks, this is my own unit and want to try with replacing the furnace control circuit board first because stat worked fine when switched to a/c.



STATEN ISLAND HOME INSPECTIONS
WWW.SIHOMEINSPECT.COM
LIC.#16000002260
718-987-1759
917-797-3917
SERVING DOWNSTATE NEW YORK
Reply With Quote
  #4  
Old 10/21/08, 8:28 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Constant blower

Charley...how about a defective (shorted) Klixon? Unusual but not impossible, right?



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #5  
Old 10/21/08, 10:07 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: Constant blower

Quote:
Originally Posted by mboyett View Post
Charley...how about a defective (shorted) Klixon? Unusual but not impossible, right?
Mike I doubt it not going to be a standard Klixon that brings the blower on and or off on a newer furnace



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 10/21/08, 12:26 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Constant blower

I have a relatively new York furnace that does that. The blower kicks on to ensure that there is a proper draft prior to ignition (not sure how that works). If the blower fails for some reason, then the gas won't kick on and ignite. I was "educated" by my HVAC tech when he installed it, and warned about that ahead of time. It's a little bit annoying because when it kicks on, it does blow cold air until the burner starts. But hey...what is, is. And if it is somehow safer, then so be it.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #7  
Old 10/21/08, 2:46 PM
Matt Berman Matt Berman is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 107
Wink Re: Constant blower

like Charley says its more than likley the control board ,the blower is controled by the board .
Reply With Quote
  #8  
Old 10/21/08, 3:25 PM
rramsey rramsey is offline
New User
 
Join Date: Jan 2007
Location: Bertram, Tx
Posts: 46
Please Note: rramsey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Constant blower

New control systems bring on blower and/or combustion fan blower for 45-90 seconds to clear any conbustible gases from unit prior to firing burners
Reply With Quote
  #9  
Old 10/21/08, 9:24 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Constant blower

Quote:
Originally Posted by rramsey View Post
New control systems bring on blower and/or combustion fan blower for 45-90 seconds to clear any conbustible gases from unit prior to firing burners
That sounds familiar.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #10  
Old 10/22/08, 4:58 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 549
Default Re: Constant blower

Quote:
Originally Posted by lcannizzaro View Post
Unit is BDP (Carrier) model 394GAW060125 furnace and when I raised thermostat, the blower immediately came on and continued to run without delay for heat exchanger to heat up. Can it be thermostat problem or deeper?
Louis
When you say the blower comes on almost immediately, do you mean the induced draft blower or the air handler blower. The induced draft blower comes on almost immediately to clear fumes. The air handler blower doesn't normally come on till the H/E warms up.
Reply With Quote
  #11  
Old 10/23/08, 9:18 PM
Louis Cannizzaro Louis Cannizzaro is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Staten Island, NY
Posts: 127
Default Re: Constant blower

The blower in question is the air handler but after spraying the circuit board with an electrical contact cleaner. The unit is now functioning as it should. I guess that the contacts that were not in use for over 6 months had a residue that prevented the furnace sequence from working properly. Thanks to all for the input.



STATEN ISLAND HOME INSPECTIONS
WWW.SIHOMEINSPECT.COM
LIC.#16000002260
718-987-1759
917-797-3917
SERVING DOWNSTATE NEW YORK
Reply With Quote
  #12  
Old 10/24/08, 8:58 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: Constant blower

Quote:
Originally Posted by lcannizzaro View Post
The blower in question is the air handler but after spraying the circuit board with an electrical contact cleaner. The unit is now functioning as it should. I guess that the contacts that were not in use for over 6 months had a residue that prevented the furnace sequence from working properly. Thanks to all for the input.
Louis Change your filter more often don't let your board lint over cleanlyness is next to Godlyness have a good one.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 10/26/08, 10:24 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Constant blower

If it is an electronic thermostat some have a set up switch for gas or electric furnace. The switch or programming may be set for electric. In this mode the main blower will come on immediately.
Reply With Quote
  #14  
Old 10/30/08, 11:19 AM
Louis Cannizzaro Louis Cannizzaro is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Staten Island, NY
Posts: 127
Default Re: Constant blower

Unit is short cycling now. I'm starting to believe that control board needs replacement. Thats probably what the HVAC tech will suggest.



STATEN ISLAND HOME INSPECTIONS
WWW.SIHOMEINSPECT.COM
LIC.#16000002260
718-987-1759
917-797-3917
SERVING DOWNSTATE NEW YORK
Reply With Quote
  #15  
Old 10/30/08, 12:23 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Constant blower

Quote:
Originally Posted by lcannizzaro View Post
Unit is short cycling now. I'm starting to believe that control board needs replacement. Thats probably what the HVAC tech will suggest.
What are the fan "on-off" settings? Standard setting are usually "on" at 150F and "off" at 120F. Some furnaces I see have them set at 120/90 for energy savings purposes. In many instances, this will cause the blower to short cycle at the end of the heating cycle.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Blower Door rdunbar Canadian Inspectors 3 9/1/08 6:22 PM
Variable speed direct vent blower motor csteele Inspecting HVAC Systems 6 5/5/08 9:41 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
Basic Electrical Theory Questions- EASY pabernathy Electrical Inspections 41 7/7/06 11:53 AM


All times are GMT -4. The time now is 4:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts