  #1  
Old 10/20/08, 6:04 PM
Louis Cannizzaro Louis Cannizzaro is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Staten Island, NY
Posts: 97
Louis Cannizzaro hasn't had much positive or negative feedback
Default Constant blower

Unit is BDP (Carrier) model 394GAW060125 furnace and when I raised thermostat, the blower immediately came on and continued to run without delay for heat exchanger to heat up. Can it be thermostat problem or deeper?



STATEN ISLAND HOME INSPECTIONS
LIC.#16000002260
(71 987-1759
SERVING DOWNSTATE NEW YORK

Last edited by lcannizzaro; 10/20/08 at 7:35 PM.
Reply With Quote
  #2  
Old 10/21/08, 12:35 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Constant blower

Quote:
Originally Posted by lcannizzaro View Post
Unit is BDP (Carrier) model 394GAW060125 furnace and when I raised thermostat, the blower immediately came on and continued to run without delay for heat exchanger to heat up. Can it be thermostat problem or deeper?
No help for you yet so I will take a shot in the dark is this a new install first time for the furnace use. If so most of the newer units have DIP switches on the control panel that have to be set for proper operation. If it is not a new install yes it could be as simple as a stat problem but most likely would be in the control board itself.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #3  
Old 10/21/08, 6:55 AM
Louis Cannizzaro Louis Cannizzaro is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Staten Island, NY
Posts: 97
Louis Cannizzaro hasn't had much positive or negative feedback
Default Re: Constant blower

Thanks, this is my own unit and want to try with replacing the furnace control circuit board first because stat worked fine when switched to a/c.



STATEN ISLAND HOME INSPECTIONS
LIC.#16000002260
(71 987-1759
SERVING DOWNSTATE NEW YORK
Reply With Quote
  #4  
Old 10/21/08, 8:28 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 3,174
Michael R. Boyett .
Default Re: Constant blower

Charley...how about a defective (shorted) Klixon? Unusual but not impossible, right?



Reputation? We don't need no stinking reputation!
Mike Boyett, TREC #7290
Capital City Inspections
Austin, Texas
Reply With Quote
  #5  
Old 10/21/08, 10:07 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Constant blower

Quote:
Originally Posted by mboyett View Post
Charley...how about a defective (shorted) Klixon? Unusual but not impossible, right?
Mike I doubt it not going to be a standard Klixon that brings the blower on and or off on a newer furnace



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #6  
Old 10/21/08, 12:26 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: St. Peters, MO
Posts: 2,192
Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information
Default Re: Constant blower

I have a relatively new York furnace that does that. The blower kicks on to ensure that there is a proper draft prior to ignition (not sure how that works). If the blower fails for some reason, then the gas won't kick on and ignite. I was "educated" by my HVAC tech when he installed it, and warned about that ahead of time. It's a little bit annoying because when it kicks on, it does blow cold air until the burner starts. But hey...what is, is. And if it is somehow safer, then so be it.
Reply With Quote
  #7  
Old 10/21/08, 2:46 PM
Matthew M. Berman Matthew M. Berman is offline
New User
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 68
Matthew M. Berman hasn't had much positive or negative feedback
Wink Re: Constant blower

like Charley says its more than likley the control board ,the blower is controled by the board .
Reply With Quote
  #8  
Old 10/21/08, 3:25 PM
Ralph W. Ramsey Ralph W. Ramsey is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Bertram, Tx
Posts: 45
Ralph W. Ramsey hasn't had much positive or negative feedback
Default Re: Constant blower

New control systems bring on blower and/or combustion fan blower for 45-90 seconds to clear any conbustible gases from unit prior to firing burners
Reply With Quote
  #9  
Old 10/21/08, 9:24 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: St. Peters, MO
Posts: 2,192
Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information
Default Re: Constant blower

Quote:
Originally Posted by rramsey View Post
New control systems bring on blower and/or combustion fan blower for 45-90 seconds to clear any conbustible gases from unit prior to firing burners
That sounds familiar.
Reply With Quote
  #10  
Old 10/22/08, 4:58 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 286
John Allingham is generally well trusted John Allingham is generally well trusted
Default Re: Constant blower

Quote:
Originally Posted by lcannizzaro View Post
Unit is BDP (Carrier) model 394GAW060125 furnace and when I raised thermostat, the blower immediately came on and continued to run without delay for heat exchanger to heat up. Can it be thermostat problem or deeper?
Louis
When you say the blower comes on almost immediately, do you mean the induced draft blower or the air handler blower. The induced draft blower comes on almost immediately to clear fumes. The air handler blower doesn't normally come on till the H/E warms up.
Reply With Quote
  #11  
Old 10/23/08, 9:18 PM
Louis Cannizzaro Louis Cannizzaro is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Staten Island, NY
Posts: 97
Louis Cannizzaro hasn't had much positive or negative feedback
Default Re: Constant blower

The blower in question is the air handler but after spraying the circuit board with an electrical contact cleaner. The unit is now functioning as it should. I guess that the contacts that were not in use for over 6 months had a residue that prevented the furnace sequence from working properly. Thanks to all for the input.



STATEN ISLAND HOME INSPECTIONS
LIC.#16000002260
(71 987-1759
SERVING DOWNSTATE NEW YORK
Reply With Quote
  #12  
Old 10/24/08, 8:58 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Constant blower

Quote:
Originally Posted by lcannizzaro View Post
The blower in question is the air handler but after spraying the circuit board with an electrical contact cleaner. The unit is now functioning as it should. I guess that the contacts that were not in use for over 6 months had a residue that prevented the furnace sequence from working properly. Thanks to all for the input.
Louis Change your filter more often don't let your board lint over cleanlyness is next to Godlyness have a good one.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #13  
Old 10/26/08, 10:24 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 156
Gary Reecher hasn't had much positive or negative feedback
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Constant blower

If it is an electronic thermostat some have a set up switch for gas or electric furnace. The switch or programming may be set for electric. In this mode the main blower will come on immediately.
Reply With Quote
  #14  
Old 10/30/08, 11:19 AM
Louis Cannizzaro Louis Cannizzaro is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Staten Island, NY
Posts: 97
Louis Cannizzaro hasn't had much positive or negative feedback
Default Re: Constant blower

Unit is short cycling now. I'm starting to believe that control board needs replacement. Thats probably what the HVAC tech will suggest.



STATEN ISLAND HOME INSPECTIONS
LIC.#16000002260
(71 987-1759
SERVING DOWNSTATE NEW YORK
Reply With Quote
  #15  
Old 10/30/08, 12:23 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,248
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Constant blower

Quote:
Originally Posted by lcannizzaro View Post
Unit is short cycling now. I'm starting to believe that control board needs replacement. Thats probably what the HVAC tech will suggest.
What are the fan "on-off" settings? Standard setting are usually "on" at 150F and "off" at 120F. Some furnaces I see have them set at 120/90 for energy savings purposes. In many instances, this will cause the blower to short cycle at the end of the heating cycle.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Blower Door rdunbar Canadian Inspectors 3 9/1/08 6:22 PM
Variable speed direct vent blower motor csteele HVAC 6 5/5/08 9:41 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Basic Electrical Theory Questions- EASY pabernathy Electrical 41 7/7/06 11:53 AM


All times are GMT -4. The time now is 4:42 PM.