Default Copper tubing

This is a high efficiency furnace. The home has an air conditioner. Question is, should this copper tube be plugged? It has some conditioned air coming out of it. Could someone tell me what its purpose is?

Thanks,

Tech 9 Home Inspections
Attached Thumbnails
copper-tubing-dsc01595.jpg  
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/22/11, 1:13 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Copper tubing

That is a messy leak getting ready to happen someone had no clue what they were doing.
The primary drain has been reduced in size should have stayed 3/4 inch. The copper tube to the right is a poor excuse for a secondary drain, not the proper diameter and not routed to a visible location. Appears to be non-professional installation



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 12/22/11, 3:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Copper tubing

Quote:
Originally Posted by cbottger View Post
That is a messy leak getting ready to happen someone had no clue what they were doing.
You mean, bubble gum is not an acceptable sealant?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 12/22/11, 10:30 PM
Jarrod M. Northage's Avatar
Jarrod M. Northage Jarrod M. Northage is offline
InterNACHI Member
 
Join Date: Nov 2010
Location: Winnipeg, Manitoba, Canada
Posts: 44
Default Re: Copper tubing

The condensate drain line is working properly, so is the pump. I was there when it filled up and the pump started. My original question was should/could this 2nd copper line be plugged? There is no condensate coming from it, and there is no evidence of it ever leaking from this tube. Conditioned air is coming out of it. So is it safe to assume that it can be capped?

Thanks.
Reply With Quote
  #5  
Old 12/23/11, 12:34 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Copper tubing

Quote:
Originally Posted by jnorthage View Post
The condensate drain line is working properly, so is the pump. I was there when it filled up and the pump started. My original question was should/could this 2nd copper line be plugged? There is no condensate coming from it, and there is no evidence of it ever leaking from this tube. Conditioned air is coming out of it. So is it safe to assume that it can be capped?

Thanks.
Why would you cap it ?
Charlie says it is a drain line and he certainly seems to know HVAC.
A secondary drain line is usually higher than the primary and only gets used if the primary plugs up so basically it needs to be routed.
Reply With Quote
  #6  
Old 12/23/11, 1:02 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Copper tubing

Lets start this over the primary drain line has been reduced it should not be as it will be prone to blockage from cold water slime as they all do. The secondary drain is the short copper stub out and no it is not suppose to be blocked or capped off, it should be routed to an appropriate drain in case the primary becomes blocked. The pic indicates the secondary drain will make a mess when the primary becomes blocked.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 12/27/11, 7:47 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Copper tubing

Hi Jarrod
I guess it depends where you are.
In Ontario, the high level (secondary) drain is typically capped. If the primary drain becomes blocked you know it because of the water all over the furnace room floor.
Only in Canada eh.
Attached Thumbnails
copper-tubing-img_1266.jpg  
Reply With Quote
  #8  
Old 12/27/11, 9:19 PM
Jarrod M. Northage's Avatar
Jarrod M. Northage Jarrod M. Northage is offline
InterNACHI Member
 
Join Date: Nov 2010
Location: Winnipeg, Manitoba, Canada
Posts: 44
Default Re: Copper tubing

Thanks for your replies.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Light Switch Near Shower vsantos Electrical Inspections 204 3/19/12 9:58 AM
Total galvanic reaction? jtribuzio Plumbing Inspections 19 4/3/10 2:18 AM
copper tubing for gas lines asargisian Inspecting HVAC Systems 8 11/29/07 10:47 PM
Flexible copper tubing carrying propane at interior, OK? kshepard Plumbing Inspections 1 3/3/07 1:24 AM
Looking for comment by Caoimhín P. Connell phinsperger Ancillary Inspection Services & Additional Topics 2 2/18/06 11:22 AM


All times are GMT -4. The time now is 11:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts