Default CSST Class Action

http://www.pddocs.com/csst/faq.aspx

What is the Class Action about?

The lawsuit claims that CSST poses an unreasonable risk of fire due to lightning strikes. Plaintiffs allege that the CSST tubing is not thick enough to prevent damage to the CSST in the event of a lightning strike and that Defendants failed to warn consumers about these alleged dangers.
The Settling Defendants deny these allegations and assert that their CSST is safe if properly installed in accordance with local codes and the manufacturers’ instructions.




Is there more than one brand of CSST involved?

Yes. The CSST installed on your property may have been manufactured by Titeflex, Ward, OmegaFlex, or Parker Hannifin.

Titeflex's CSST is stamped with the mark “GASTITE.”

Ward's CSST is stamped with the mark “WARDFLEX.”

OmegaFlex's CSST is stamped with the marks “TRACPIPE” or “COUNTERSTRIKE.”

Parker Hannifin's CSST is stamped with the mark “PARFLEX.”



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #2  
Old 11/2/06, 8:38 AM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 427
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CSST Class Action

Thanks for that link. Interesting.
Reply With Quote
  #3  
Old 11/2/06, 10:00 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: CSST Class Action

Thanks Joe,

I wonder how many instances there are of this tubing being affected by lightening?

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #4  
Old 11/2/06, 10:32 AM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CSST Class Action

That was ... en-lightning
Reply With Quote
  #5  
Old 11/2/06, 11:06 AM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: CSST Class Action

Thank you Mr. Hagarty. I appreciate you taking the time to post this info.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #6  
Old 11/2/06, 11:53 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: CSST Class Action

Interesting indeed. It appears the real issue is with the installation methods. Proper bonding of the system is the apparent remedy.

In my area (Los Angeles County), based on our LDZ, consumers will be allotted $200 (for a home less than 3000 sq ft) toward the purchase and installation of a lightning protection system.

I will be preparing a new narrative for my report system to include this information. Thanks Joe.

FWIW - CSST has not been approved for use in CA although many local jurisdictions are allowing it by "special permission."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 11/25/06, 1:56 AM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: CSST Class Action

I just inspected a home today that was LOADED with this Gastite yellow hose...



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #8  
Old 11/25/06, 10:38 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: CSST Class Action

Quote:
Originally Posted by bsumpter
I just inspected a home today that was LOADED with this Gastite yellow hose...
I see the 'yellow hose' every week.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 11/25/06, 11:00 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: CSST Class Action

Comments on this proposed narrative?

"A gas piping system called CSST is present in this home. CSST is used to transmit gas in residential, commercial and industrial structures. CSST consists of a continuous, flexible, stainless steel pipe, and typically is covered with a yellow exterior plastic coating. In the case of one of the products manufactured by OmegaFlex, called "COUNTERSTRIKE," the product is covered with a black exterior coating with yellow lettering. CSST typically is routed beneath, through and alongside floor joists, inside interior wall cavities and on top of ceiling joists in attic space from a gas source to an appliance. CSST does not include gas-appliance connectors (e.g., a connector that runs from a gas outlet to an appliance). Titeflex's CSST product is known as "GASTITE," Ward's CSST product is known as "WARDFLEX," OmegaFlex’s CSST is known as "TRACPIPE" or "COUNTERSTRIKE," and Parker Hannifin’s CSST product is known as "PARFLEX." Typically, these products may be visible along floor joists, above basements, in attic spaces, or connected to exposed appliances such as water heaters. The piping should be stamped with a manufacturer’s mark. We may not attempt to identify the type of CSST present and more than one brand may be involved."

"A lawsuit claims that CSST poses an unreasonable risk of fire due to lightning strikes. The plaintiffs allege that the CSST tubing is not thick enough to prevent damage to the CSST in the event of a lightning strike and that manufacturers failed to warn consumers about these alleged dangers. The manufacturers deny these allegations and assert that their CSST is safe if properly installed in accordance with local codes and the manufacturers’ instructions. Nevertheless, the lawsuit was settled and affects any and all persons and/or entities who own structures in the United States in which CSST manufactured by the Settling Defendants was installed as of September 5, 2006. We take no position on the lawsuit and may not determine whether the CSST observed in this residence is covered by the lawsuit. You should trace the CSST in this home and determine the manufacturer for yourself. We recommend that you read the details of the lawsuit and settlement, which can be viewed at: http://www.pddocs.com/csst/faq.aspx#"



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 11/25/06 at 11:17 AM..
Reply With Quote
  #10  
Old 11/25/06, 11:44 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: CSST Class Action

Let me ask a some general questions here.

Can we possibly be aware of all the potential recalls and lawsuits against products that may be in our clients homes?

While I believe we should limit our liablility by careful and informed report writing, just how far should we go?

Any and all comments and discussion welcome.
Inquiring minds want to know.
Reply With Quote
  #11  
Old 11/25/06, 12:25 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,843
Default Re: CSST Class Action

Here's an old article on this topic in a suburb of Dallas, TX

http://www.selectinspect.com/pdf/FRI...pipe%20ban.pdf

I was in contact with Gastite and Frisco Building Dept. during these investigations.

It was found in all cases the cause was improper bonding and lightning protection.

Once this was and is accomplished there have been no further incidences documented in Frisco and CSST systems are being installed today, in my market anyway.

JDF,

You may need to revise your statement not all are covered please read the bold:

Who is covered by the Proposed Settlement?

The Settlement Class consists of any and all persons and/or entities who own structures in the United States in which CSST manufactured by Settling Defendants was installed as of September 5, 2006 (“Settlement Class Members”).

The following persons are excluded from the Settlement Class: a) persons and/or entities who timely opt-out of this proceeding following the directions for opting-out established by the Court; b) any and all federal, state, and/or local governments, including, but not limited to, their departments, agencies, divisions, bureaus, boards, sections, groups, counsels and/or subdivisions; c) any currently sitting Arkansas state court judges and/or justices and/or any persons within the third degree of consanguinity (blood relationship) to such judges and/or justices; d) Settling Defendants; e) Plaintiffs’ Counsel and their immediate families; and f) any person or entity who as of September 5, 2006, has an individual personal injury, product liability or subrogation lawsuit pending against any of the Settling Defendants in which injury or damage is alleged to have occurred as a result of a failure of CSST resulting from an actual or near lightning strike.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 11/25/06 at 12:32 PM.. Reason: could
Reply With Quote
  #12  
Old 11/25/06, 12:27 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: CSST Class Action

Quote:
Originally Posted by badair

Here's an old article on this topic in a suburb of Dallas, TX

http://www.selectinspect.com/pdf/FRI...pipe%20ban.pdf

Dead Link.

You do not have permission to access http://www.selectinspect.com/pdf/FRI...pipe%20ban.pdf



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #13  
Old 11/25/06, 12:39 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: CSST Class Action

Quote:
Originally Posted by jhagarty
Dead Link.

You do not have permission to access http://www.selectinspect.com/pdf/FRI...pipe%20ban.pdf
Worked OK for me as a right click -save target as- but here it is anyway.

FRISCO Gas pipe ban.pdf
Reply With Quote
  #14  
Old 11/25/06, 1:20 PM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: CSST Class Action

Here is my version of the narrative:

Quote:
A gas piping system called CSST is present in this home. CSST is used to transmit gas in residential, commercial and industrial structures.

CSST consists of a continuous, flexible, stainless steel pipe, and typically is covered with a yellow exterior plastic coating. In the case of one of the products manufactured by OmegaFlex, called "COUNTERSTRIKE," the product is covered with a black exterior coating with yellow lettering. CSST typically is routed beneath, through and alongside floor joists, inside interior wall cavities and on top of ceiling joists in attic space from a gas source to an appliance. CSST does not include gas-appliance connectors (e.g., a connector that runs from a gas outlet to an appliance). Titeflex's CSST product is known as "GASTITE," Ward's CSST product is known as "WARDFLEX," OmegaFlex’s CSST is known as "TRACPIPE" or "COUNTERSTRIKE," and Parker Hannifin’s CSST product is known as "PARFLEX." Typically, these products may be visible along floor joists, above basements, in attic spaces, or connected to exposed appliances such as water heaters. The piping should be stamped with a manufacturer’s mark. We may not attempt to identify the type of CSST present and more than one brand may be involved

A lawsuit claims that CSST poses an unreasonable risk of fire due to lightning strikes. The plaintiffs allege that the CSST tubing is not thick enough to prevent damage to the CSST in the event of a lightning strike and that manufacturers failed to warn consumers about these alleged dangers. The manufacturers deny these allegations and assert that their CSST is safe if properly installed in accordance with local codes and the manufacturers’ instructions. Nevertheless, the lawsuit was settled and affects any and all persons and/or entities who own structures in the United States in which CSST manufactured by the Settling Defendants was installed as of September 5, 2006.

We take no position on the lawsuit and may not determine whether the CSST observed in this residence is covered by the lawsuit. You should consider further evaluation by a specialist to trace the CSST in this home and determine the manufacturer and installation procedures used.

For more information regarding the proposed class action settlement call: 1-800-420-2916 or visit http:// www.csstsettlement.com

We recommend that you read the details of the lawsuit and settlement, which can be viewed at: http://www.pddocs.com/csst/faq.aspx and consider further evaluation by a specialist regarding this product and its installation
.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #15  
Old 11/25/06, 3:17 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: CSST Class Action

I like it Brian.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Proposed Class Action Settlement "Sears" Anti-tip Device mcyr General Inspection Discussion 3 11/8/07 7:18 AM
MAR is Publicly Backing Away from HI Licensing Bill jbushart Legislation, Licensing & Legal Issues for Inspectors 18 4/6/07 12:40 AM