  #1  
Old 6/4/10, 12:21 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Cracked Air Exch?

HVAC specialist question:

During fire up and prior to blower, flue gases measured 9.0 Oxygen, and 75.6 XAir. After blower, O2 went up to 9.6 and XAir to 85.0.

Is this enough of a change to indicate a cracked air exchange? Is there an acceptable range published somewhere?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/4/10, 10:57 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cracked Air Exch?

Quote:
Originally Posted by jbushart View Post
HVAC specialist question:

During fire up and prior to blower, flue gases measured 9.0 Oxygen, and 75.6 XAir. After blower, O2 went up to 9.6 and XAir to 85.0.

Is this enough of a change to indicate a cracked air exchange? Is there an acceptable range published somewhere?
Definitely communication from the pressurized house air side of the heat exchanger to the combustion gas side. May be cracked exchanger or bad gasket, if any installed. IMO, should be called.
Reply With Quote
  #3  
Old 6/6/10, 11:54 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cracked Air Exch?

Bacharach in their literature calls out any change in oxygen +/- .5 percent when blower comes on may indicate a heat exchanger leak.
Reply With Quote
  #4  
Old 6/6/10, 12:58 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Cracked Air Exch?

Im just curious as to where you are taking these flue gas readings?

Additionally, here are some videos of heat exchanger cracks. YouTube...who knew.

http://www.youtube.com/watch?v=8e9hP...eature=related

http://www.youtube.com/watch?v=xIKvP...eature=related



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #5  
Old 6/6/10, 6:54 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cracked Air Exch?

Quote:
Originally Posted by dedwards View Post
Im just curious as to where you are taking these flue gas readings?

Additionally, here are some videos of heat exchanger cracks. YouTube...who knew.

http://www.youtube.com/watch?v=8e9hP...eature=related

http://www.youtube.com/watch?v=xIKvP...eature=related

The undiluted flue gases. Vent pipe on 80% and 90% furnaces. Up through draft diverter into each cell exhaust.
Reply With Quote
  #6  
Old 6/21/10, 12:11 PM
Darin Redding's Avatar
Darin Redding Darin Redding is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: Cracked Air Exch?

I'm looking for a recommendation on a combustion gas detector. What devices/brands do you use?



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #7  
Old 6/21/10, 4:19 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cracked Air Exch?

Quote:
Originally Posted by dredding View Post
I'm looking for a recommendation on a combustion gas detector. What devices/brands do you use?
I like the Bacharach 2 225
Reply With Quote
  #8  
Old 6/21/10, 4:34 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Cracked Air Exch?

This is what I use.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #9  
Old 6/21/10, 7:30 PM
Darin Redding's Avatar
Darin Redding Darin Redding is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: Cracked Air Exch?

Spendy little devices. Wow. And you use them primarily to check o2 and co2 levels at the registers?

I guess my new concern is not discovering a cracked heat exchanger.



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #10  
Old 6/21/10, 7:53 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Cracked Air Exch?

Quote:
Originally Posted by dredding View Post
I'm looking for a recommendation on a combustion gas detector. What devices/brands do you use?
Don't get one.....
Reply With Quote
  #11  
Old 6/21/10, 7:57 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cracked Air Exch?

Quote:
Originally Posted by dredding View Post
Spendy little devices. Wow. And you use them primarily to check o2 and co2 levels at the registers?

I guess my new concern is not discovering a cracked heat exchanger.
A good days' energy audits will pay for the device. I have 3 on hand.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cracked wall / slab foundation question hmiles Interior Inspections 4 9/2/09 11:17 AM
Cracked flue tile bknowlton Inspecting HVAC Systems 6 2/1/07 11:37 PM
Cracked Heat Exchanger jallingham Inspecting HVAC Systems 26 5/11/06 10:12 PM


All times are GMT -4. The time now is 11:33 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts