Any special requirements regarding foundation vents for supplying a medium efficiency gas furnace in an under floor area, e.g., not less than 2x the required openings?
|
|
#2
|
|||
|
|||
|
Al,
The minimum combustion air requirement for the furnace can be found in the installation manual. If the crawl space does not have enough vents to meet this, they can always add a combustion air pipe from the exterior. Best regards, Russell G. Cloyd Intra-Spec Home Inspections & Code Consulting, LLC 859-586-4591 www.intra-spechomeinspections.com |
|
#3
|
||||
|
||||
|
Don't forget to add in the combustion air for the water heater or any other gas fired appliance.
Henry Valenzano CMI (Hank) Double Check Home Inspection LLC. www.DCHI.com Hank@DCHI.com 719-635-6425 Colorado Arms Repair : Gunsmith www.ArmsRepair.com Henry@ArmsRepair.com |
|
#4
|
||||
|
||||
|
CodeCheck has the current model requirements for combustion air which can be used as a guideline, absent specific local provisions to use as a guide if known ... JMO
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#5
|
||||
|
||||
|
Quote:
</IMG> Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#6
|
||||
|
||||
|
Hey Crarlie, been pretty busy lately so I have been mostly lurking in the educational and structural related areas ... but I try to check in on the HVAC topics occasionally since it is one of my specialty areas.
Concerning the equipment in a crawl space, the area should be vented for moisture escape anyway (unless conditioned), which can provide the required combustion air. For C.A. from an outdoor source a general rule of thumb is to look for vents up high with about 1.0 sq. inch per 3,000 BTU's of equipment rating. So if the equipment is rated at say 120,000 BTU's, then there would need to be 40 sq. inches of intake vents. Even a crawl with a good floor vapor retarder (e.g. rat slab) requires air vents with 144 sq. inches per 1,500 s.f of area. JMO Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Return air from crawl space | WHI | Inspecting HVAC Systems | 11 | 1/9/12 7:43 PM |
| Gas flex line in crawl space | Richard Seay | Plumbing Inspections | 19 | 8/12/08 8:12 PM |
| Crawl space in under house | dnasser | Structural Inspections | 15 | 2/27/07 7:12 PM |
| Manufactured home crawl space | sstanczyk | Structural Inspections | 2 | 2/19/06 4:23 PM |