Default Damper in ductwork

This is the ductwork from a oil fired furnace to the chimney. unit instaled in 03. Never have seen it before. Seems to be sucking air in to assist in the draft, but wanted to make sure it was not dangerous. 1st time posting. Hope the picture is attached.
Attached Thumbnails
damper-ductwork-dsc00616.jpg  
Reply With Quote
  #2  
Old 4/10/07, 12:34 PM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Damper in ductwork

Quote:
Originally Posted by jsigns
This is the ductwork from a oil fired furnace to the chimney. unit instaled in 03. Never have seen it before. Seems to be sucking air in to assist in the draft, but wanted to make sure it was not dangerous. 1st time posting. Hope the picture is attached.
That is normal in oil fired furnaces. It is a barometric damper

Last edited by Jason1; 4/10/07 at 12:40 PM..
Reply With Quote
  #3  
Old 4/10/07, 12:37 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Damper in ductwork

Before you start determining the installation of HVAC equipment, I would recommend you take some courses and only report on what you know is not right.

IAW SOP you are only required to run the HVAC from the T-Stat. No further evaluation is required or expected.

If you don't know what you are looking at, I would recommend that you do not get involved, as this is not a requirement of HI's.

You will find this damper in oil fired boilers/furnaces. It has a purpose. Just because you have not see it before, does not mean there is a problem with it.
Reply With Quote
  #4  
Old 4/10/07, 12:38 PM
jsigns jsigns is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Swarthmore, PA
Posts: 4
Default Re: Damper in ductwork

I've seen other oil fired furnacces without this. Is there a reson it would be in some but not all? Thanks, John
Reply With Quote
  #5  
Old 4/10/07, 12:42 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Damper in ductwork

Barometric Draft: The swing damper on the vent connector controls the draft up the chimney. If the draft is too high, the hot flue gases will pass through the heat exchanger too quickly, sending the heat up the chimney. Draft should be a set a 0.02"W.C.- 0.03" W.C. with a draft gauge. This very small amount of pressure is the equal to a velocity 566FPM - 694 FPM (Feet Per Minute) If the barometric damper door is sticking or does not open at all, it will not control the draft properly. Draft can reach 0.08 W.C. or 1133 FPM. As the velocity of the flue gas increases less heat is absorbed into the supply air to heat the house and more heat goes up the chimney.
Reply With Quote
  #6  
Old 4/10/07, 12:44 PM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Damper in ductwork

A barometric damper isolates the burner in the furnace from changes in pressure at the chimney exit.Whenever the chimney suction is greater than the furnace’s needs, the flap rotates open and lets room air into the chimney.

Proper adjustment of the barometric damper is important. While it is a signifi cant part of the heating system, it is also a huge leak in the system. The damper can allow combustion gases to leak into the house, especially when
large exhaust devices, such as a dryer or a range hood, are operating. Also, if the damper is improperly adjusted, it can waste much of the heat produced by the furnace.
Reply With Quote
  #7  
Old 4/10/07, 12:50 PM
jsigns jsigns is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Swarthmore, PA
Posts: 4
Default Re: Damper in ductwork

Thanks for all of your help. I was asking to better educate myself and I was concerned about the safety issue of carbon monoxide.
Reply With Quote
  #8  
Old 4/10/07, 12:53 PM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Damper in ductwork

Quote:
Originally Posted by mlarson

Draft should be a set a 0.02"W.C.- 0.03" W.C. with a draft gauge.
What kind of tools do you carry around?
Reply With Quote
  #9  
Old 4/10/07, 12:55 PM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Damper in ductwork

Quote:
Originally Posted by jsigns
Thanks for all of your help. I was asking to better educate myself .
Good job, I would recommend you take an HVAC inspection course.
Reply With Quote
  #10  
Old 4/10/07, 1:25 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Damper in ductwork

Quote:
Originally Posted by Jason1
What kind of tools do you carry around?
Little beyond the scope of a home inspection eh?

I use to have easy access to a draft gauge.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas log insert damper lbrown2 Inspecting HVAC Systems 11 9/18/08 7:07 AM
Soot from Barometric Draft Damper (posted by Ted Hull) AskNACHI.org AskNACHI.org Inspection Questions Forum 3 5/11/07 7:49 AM
Barometric damper sstanczyk Inspecting HVAC Systems 9 3/9/06 2:13 PM


All times are GMT -4. The time now is 6:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts