InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > HVAC

Notices

HVAC Topics include heating, venting, and air conditioning.

Reply
 
LinkBack Thread Tools
  #1  
Old 10/28/08, 1:01 PM
Mark Nicholet's Avatar
Mark Nicholet Mark Nicholet is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 439
Default Direct vent close to combustible(s)

I talked to a builder yesterday about this direct vent for a 20,000 BTU nat. gas fireplace. The vent is stamped keep clear 2ft. The builder said it is not a problem and he has other houses with this install. My concern was the wood member directly above the vent. I thought it could be flashed on the top side. What is your opinions? Thanks.
Attached Thumbnails
direct-vent-close-combustible-s-dsc06098-medium-.jpg.JPG
Views:	33
Size:	45.8 KB
ID:	24891   direct-vent-close-combustible-s-ir_0094-medium-.jpg.jpg
Views:	20
Size:	31.3 KB
ID:	24892  




Mark Nicholet
Apple Home Inspections LTD
My Blog

InterNACHI member
Infrared-Certified
CAHPI(BC) member
BC Licence # 47592
Reply With Quote
  #2  
Old 10/28/08, 1:20 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: FL panhandle
Posts: 3,734
Default Re: Direct vent close to combustible(s)

If you know the manufacture, go find the installation instructions / procedures (almost always online at the website), and if it backs up your concerns (download for future reference), refer to them when you voice your concerns and move on. If the customer still wants to buy the home you have done your job and there is little else you can do. It will not pay off in the long run for you to get into a pissing match with the builder (that is the buyer's job). Make sure you know what you are talking about before you do anything though. Back it up with documentation. State the facts, let the facts speak for themselves, keep your emotions out of it. Remember, you are the "disinterested" third party.



Doug Edwards, CMI








Last edited by dedwards; 10/28/08 at 1:25 PM..
Reply With Quote
  #3  
Old 10/28/08, 1:22 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,347
Default Re: Direct vent close to combustible(s)

If it were me I would obtain the manufacturer's installation manual to determine proper clearances. For instance, Lennox direct vent installations allow 2.5" projections of combustible material within 3" of the vent. Anything over 2.5" must be 24" away.

See fig 5 but again this is for a Lennox product only:
Lennox fp.pdf



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Variable speed direct vent blower motor csteele HVAC 6 5/5/08 8:41 AM
MEMCO Direct Vent jcampbell HVAC 2 3/3/08 8:42 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Misc. Discussion 8 1/25/07 5:22 PM
Direct vent WH with draft hood dpeterson Plumbing 9 12/30/06 3:35 PM


All times are GMT -4. The time now is 2:56 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts