Default Direct Vent Pellet Stove Help

I don't run across many of these situations around here. The vent pipe is about 7 feet off the sidewalk. Then neighboring home is over 20 feet away. The home is clad in vinyl siding. There is no manual available and was curious if there is a problem with this. To me, it's a DLR (Doesn't look right). Who would be the licensee for refrerral A Chimney Sweep??

Thanks in advance for your help!
Attached Thumbnails
direct-vent-pellet-stove-help-woodstoveinteriorjpg.jpg   direct-vent-pellet-stove-help-woodstoveexterior.jpg   direct-vent-pellet-stove-help-woodstoveexterior1.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America)
  #2  
Old 5/1/09, 5:44 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Direct Vent Pellet Stove Help

It DLR to me either but I would defer in any case.

Do you have a make and model for the stove?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #3  
Old 5/1/09, 10:42 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,776
Default Re: Direct Vent Pellet Stove Help

Greg,

The installation looks OK to me but the siding will discolour from soot and draft may be minimal at times...



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #4  
Old 5/2/09, 12:49 AM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 1,246
Default Re: Direct Vent Pellet Stove Help

So what keeps the exhaust from blowing back into the window? (Humor me, I know the window would probably be closed when the burner is being used)



Bobby Hamilton
Bloodhound Home Inspection Services
Youngstown Home Inspection
Austintown Ohio Home Inspection


Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
  #5  
Old 5/2/09, 2:17 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Direct Vent Pellet Stove Help

Quote:
Originally Posted by mlarson View Post
It DLR to me either but I would defer in any case.

Do you have a make and model for the stove?
Sure Mike,

Make: Harman Stove
Model: Accentra

From what I could find the 7' requirement works. The nearby window was fixed. Just one of those things that dlr. Thanks for asking.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #6  
Old 5/2/09, 6:30 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Direct Vent Pellet Stove Help

Here is the manual.

http://www.harmanstoves.com/doc/accentram.pdf

It indicates 48" to operable window and 7 ft. above walk and 3 ft. to all combustibles.

Smaller clearances if optional outside air vent is installed.

The clearance diagram is on page 19.

Read it carefully and I am not sure about the vent termination in your pic.

DLR because if has no downturn to prevent rain infiltration.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #7  
Old 5/3/09, 9:22 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,776
Default Re: Direct Vent Pellet Stove Help

Quote:
Originally Posted by bhamilton View Post
So what keeps the exhaust from blowing back into the window? (Humor me, I know the window would probably be closed when the burner is being used)
Below copied from page 19 of the installation manual:

B. The clearance to a window or door that may be opened must be a minimum of 48" to the side and 48" below the window/door, and 12" above the window/door. 1
With outside air installed, the clearances are 18" to the side and below and 9" above.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #8  
Old 5/3/09, 10:45 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Direct Vent Pellet Stove Help

Quote:
Originally Posted by mlarson View Post
Here is the manual.

http://www.harmanstoves.com/doc/accentram.pdf

It indicates 48" to operable window and 7 ft. above walk and 3 ft. to all combustibles.

Smaller clearances if optional outside air vent is installed.

The clearance diagram is on page 19.

Read it carefully and I am not sure about the vent termination in your pic.

DLR because if has no downturn to prevent rain infiltration.
Thanks,
I mentioned in the report that they should refer to the manufacturer's reccomendations but there was no manual present. I forwarded the link to the manual to our client. So now they have the reference. I had a brain fahrt not to look that up. There were many other discussions that had me a little distracted.

The clients are from Florida and did not have any experince with Furnaces, Humidifiers, Attics, Basements and this home had all AND the home was built in 1885 with K&T and 2-prong receptacles, sagging floors....



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet Stove venting jcampbell Inspecting HVAC Systems 9 1/24/09 9:14 PM
Variable speed direct vent blower motor csteele Inspecting HVAC Systems 6 5/5/08 8:41 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM
Direct vent WH with draft hood dpeterson Plumbing Inspections 9 12/30/06 3:35 PM


All times are GMT -4. The time now is 6:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts