OK so I know that you have to have a dirt leg on gas lines. I found gas heater today where the dirt leg is in the unit just in front of the gas valve. Never seen this setup.
any thoughts????? sorry no photo |
|
#2
|
||||
|
||||
|
Drip leg.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
what's a dirt leg. i think i missed "it" again. maybe it's me.??
|
|
#4
|
|||
|
|||
|
I call it a dirt leg.
|
|
#5
|
||||
|
||||
|
Dirt legs are not required in any jurisdiction that I know of. Drip legs, however, are required by utility companies when the moisture content is high in the fuel they provide.
I think I may have seen one in four years. . . IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
When I right it up it is a "drip leg", but every plumber I have talked to calls it a "dirt" leg.
|
|
#7
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
|||
|
|||
|
Quote:
|
|
#9
|
|||
|
|||
|
Quote:
Hmmmm, I think AZ will be beach front property before long. I hope not. |
|
#10
|
|||
|
|||
|
Quote:
|
|
#11
|
||||
|
||||
|
G2419.2 (408.2) Drips. Where wet gas exists, a drip shall be
provided at any point in the line of pipe where condensate could collect. A drip shall also be provided at the outlet of the meter and shall be installed so as to constitute a trap wherein an accumulation of condensate will shut off the flow of gas before the condensate will run back into the meter. G2419.3 (408.3) Location of drips. Drips shall be provided with ready access to permit cleaning or emptying. A drip shall not be located where the condensate is subject to freezing. G2419.4 (408.4) Sediment trap. Where a sediment trap is not incorporated as part of the gas utilization equipment, a sediment trap shall be installed downstream of the equipment shutoff valve as close to the inlet of the equipment as practical. The sediment trap shall be either a tee fitting with a capped nipple in the bottom opening of the run of the tee or other device approved as an effective sediment trap. Illuminating appliances, ranges, clothes dryers and outdoor grills need not be so equipped. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#12
|
|||
|
|||
|
Worked for a mech. cont. for 16yrs, always been called a dirt leg
|
|
#13
|
||||
|
||||
|
Mandatory in the Chicago area by gas companies. Called "drip legs"...
"Dirt legs" are for our politicians... |
|
#14
|
||||
|
||||
|
To answer your original question Bruce, it really doesn't matter where the drip leg is located, but it should be accessible.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#15
|
|||
|
|||
|
Thanks JP just never seen one in the unit.
|
![]() |