Default Re: dirt leg

Attachment 2543

Last edited by dvalley; 10/7/07 at 5:41 PM..
Reply With Quote
  #17  
Old 4/1/06, 4:23 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: dirt leg

Drip legs here are installed about 50% of the time. I called the gas company and they said it isn't a significant defect in residential construction (commercial is a different story). I also called building inspector and they don't inforce it. I quit referencing it in my reports because of that.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #18  
Old 4/1/06, 4:49 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: dirt leg

Quote:
Originally Posted by pbolliger
Mandatory in the Chicago area by gas companies. Called "drip legs"...

"Dirt legs" are for our politicians...
I think you meant "Dirt Bags"
Reply With Quote
  #19  
Old 4/1/06, 6:11 PM
dspencer's Avatar
dspencer dspencer is offline
Active Poster
 
Join Date: Dec 2004
Location: Marengo, Oh
Posts: 178
Please Note: dspencer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: dirt leg

Quote:
Originally Posted by tallen
When I right it up it is a "drip leg", but every plumber I have talked to calls it a "dirt" leg.
Ditto
Reply With Quote
  #20  
Old 4/1/06, 8:15 PM
msaxton msaxton is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Duluth, MN
Posts: 285
Default Re: dirt leg

I do beleive they are required here, havnt seen any without one around here



"If God was one of us, would he recommend a detailed analysis by a structural engineer for the world?"

Michael S. Saxton
http://www.duluthhomeinspections.com
Reply With Quote
  #21  
Old 4/1/06, 8:58 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: dirt leg

I did a few inspections for a client about a year ago.

He was purchasing a home and was specifically looking for an All Electric House.

Heat Pump or Baseboard. No Natural Gas, Propane and/or Oil Heating was acceptable.

The requirement was due to the fact that He and his Family survived a Natural gas explosion in their home.

Cause of explosion was attributed to the lack of a sediment leg at the Laundry Dryer. Sediment lodged in the gas valve of the Laundry dryer allowing natural gas to leak at the completion of the Dryer Cycle. Leakage was ignited by the Water Heater.

Home exploded and was a total loss.

Client, Wife and 2 children survived.

He believed that Lightening could strike twice. He was not taking any chances.

Since then, I observe and report every instance where a Gas Sediment (Drip and/or Dirt) leg is not present.

Your mileage may vary.....



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #22  
Old 4/1/06, 9:49 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: dirt leg

I think he's calling a sediment trap a dirt leg, which sound's reasonable. Trouble is I don't know what a sediment trap is. (See G2419.4 (408.4))



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #23  
Old 4/2/06, 5:21 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: dirt leg

Quote:
Originally Posted by jpope
I think I may have seen one in four years. . .
Well, if we were playing golf, I'd have you beat. Can one have a hole-in-zero in golf?



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #24  
Old 4/2/06, 8:01 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: dirt leg

Drip legs are for wet piping applications and Dirt legs are commonly referred to with Gas piping applications. Both however serve the same purpose.

In Massachusetts, Drip legs, Dirt pockets, Dirt legs (whichever you prefer to call it) are required when connecting to an appliance if the connection is made with black pipe. If the appliance is connected with soft copper, I look for a loop.

This leg serves as a collection point for moisture, and foreign particles (i.e. copper sulfide) that may be in the gas.

If there's no leg present on a gas supply line serving an appliance, I write it up. Period.
Reply With Quote
  #25  
Old 4/2/06, 1:35 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: dirt leg

Technically a "drip leg" is different from a "dirt leg".

A "drip leg" is intended to catch moisture in gas, and is installed at all low points in a gas piping system for wet gas (IRC G2419.2).

A "dirt leg" (or more correctly a "sediment trap") is installed at an appliance to catch tar, rust, scale, pipe dope, dust, debris, and other sediments. It is installed between the shutoff valve and control valve of a gas appliance, and is required by manufacturers and model codes for All gas fired water heaters, boilers, and furnaces (IRC G2419.4).

The terms "drip leg" and "dirt leg" are often interchanged, even by plumbers, but most of the time what you see at an appliance is the required "sediment trap" which is usually a "tee fitting with a capped nipple in the bottom opening of the run of the tee" (per IRC G2419.4).

Attached is a Press Release from the Gas Appliance Manufacturers Association (GAMA) concerning the often missed requirement for installing sediment traps.

JMO & 2 nickels ...
Attached Files
File Type: pdf Sediment Traps - GAMA.pdf (26.4 KB, 572 views)



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #26  
Old 4/2/06, 5:56 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: dirt leg

Quote:
Originally Posted by bgraham
OK so I know that you have to have a dirt leg on gas lines. I found gas heater today where the dirt leg is in the unit just in front of the gas valve. Never seen this setup ... any thoughts?????
To answer your original question, that seems okay as long as the dirt leg (aka "sediment trap") is between the shutoff valve and the appliance control valve. Fouling of the control valve from sediment, and possible resulting gas leaks, is one of biggest reasons for the dirt leg being required for all gas fired water heaters, boilers, and furnaces.

Attached are photos of a typical gas fired water heater, with the dirt leg installed just before the control valve (and after the shutoff valve). If it's not present, it gets a red flag every time for a plumber to come and install one ... even though there are no problems with wet gas in my area.

The point of contention about dirt legs is usually not if they are required (they always are), but how long the leg below the tee needs to be. Some say 1" and some say 3" ... I go with 1" minimum, and 3" desirable.

JMO and 2-nickels ...
Attached Thumbnails
dirt-leg-img_0228-small.jpg   dirt-leg-img_0227-small.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #27  
Old 4/5/06, 3:39 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: dirt leg

Quote:
Originally Posted by roconnor
To answer your original question, that seems okay as long as the dirt leg (aka "sediment trap") is between the shutoff valve and the appliance control valve. Fouling of the control valve from sediment, and possible resulting gas leaks, is one of biggest reasons for the dirt leg being required for all gas fired water heaters, boilers, and furnaces.

Attached are photos of a typical gas fired water heater, with the dirt leg installed just before the control valve (and after the shutoff valve). If it's not present, it gets a red flag every time for a plumber to come and install one ... even though there are no problems with wet gas in my area.

The point of contention about dirt legs is usually not if they are required (they always are), but how long the leg below the tee needs to be. Some say 1" and some say 3" ... I go with 1" minimum, and 3" desirable.

JMO and 2-nickels ...
Speaking as a HVAC Service Tech for once I would love to see that sorry plumbers water heater buried behind the furnace in a closet.
Reply With Quote
  #28  
Old 4/5/06, 4:41 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: dirt leg

Quote:
Originally Posted by roconnor
Attached are photos of a typical gas fired water heater, with the dirt leg installed just before the control valve (and after the shutoff valve).
Quote:
Originally Posted by Gary Reecher
Speaking as a HVAC Service Tech for once I would love to see that sorry plumbers water heater buried behind the furnace in a closet.
I hear ya , as I actually occasionally still work for my family HVAC company helping with installs and service. I have actually worked on servicing that furnace, and a little extra room would have been helpful. But the install essentially meets the minimum install requirements and it could be serviced ... servicing was possible without too much trouble. But extra room would have been helpful.

Hence the common difference between what meets the code minimums and what is considered good practice.

JMO and 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Does it need a Dirt Leg? (condensate trap) mgault Plumbing Inspections 8 7/20/07 8:52 AM
Tee Vent connection & dirt leg. dmacy Inspecting HVAC Systems 4 6/13/06 12:12 PM


All times are GMT -4. The time now is 9:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts